What are the thoughts on using kraft faced vs. unfaced fiberglass insulation to insulate the bottom side of under floor radiant heating? The trade-offs I can think of are that there would be less air infiltration and possibly easier installation with the craft faced, but it would come at a higher cost. I spent about an hour looking for old posts, but but didn't see in any of the discussions on insualtion where faced and unfaced were compared.

The living portion of the house is on a crawl space and I'm installaing radiant under-floor using .016" X 4" omega heat transfer plates in about 75% of the house and .022" X 6" omega plates in the rest, which has a greater heating load. Joist spacing is 16" in about half of the house and 24" in the other half. Pex spacing is/will be 8" in most of the house and 12" in some areas with lower heat loss.

The garage and shop non-living areas portion are on a concrete slab. The garage (about half the space on a slab) has pex in the concrete and the other half uses a radiant heated wall. This section has been in use for about a year with the current boiler via a mixing valve.

Current heating source is a 25-year-old cast iron boiler with baseboard. The replacement is a Lochinvar Noble. DHW is via an indirect water heater. When I cut over to the under-floor radiant, everything will be low temperature except for the water heater.

The crawl space is conditioned. There is blue board insulation on the inside and outside of the foundation with an R value 8. It's higher at the rim joist. I plan to keep its temperature relatively close to the living space.

Design temperature is -15f.

Before I take the insurance off of my truck for the winter I want to lay in a supply of insulation I will need before next spring.

Comments

  • HydronicMike
    HydronicMike Posts: 471

    The usual adage is “No face, no space”.

  • hot_rod
    hot_rod Posts: 28,704

    I think you are talking brown kraft paper, not the foil faced stuff? Seems the Kraft would keep any crawl space moisture out of the batts?

    Screenshot 2026-08-30 at 7.23.29 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • DCContrarian
    DCContrarian Posts: 1,588

    If the crawl space is conditioned it shouldn't matter. There's no vapor drive between two conditioned spaces.

  • AlaskaDick
    AlaskaDick Posts: 54

    Kraft, no foil. The outside walls of the house have poly sheet and the blue board against the inside of foundation serves as a vapor barrier there. The ground is also lined with poly. The rim joist is insulated with eps and xps insulation and sealed with canned spray foam so the ends of the fiberglass won't be against a cold face. Also, we are not in a high humidity area and the poly on the floor does a good job of blocking any water vapor coming from in the ground. I also have an HRV for the house.

    My thoughts go along with those of DCContrarian, the temperatures will be relatively close. I'm not attempting to keep the crawl space cold, I just don't want it to be warmer than the house.

    My experience with kraft faced is that it's less effective as a vapor barrier compared with poly and that unfaced is subject to air infiltration. Infilitration may not be an issue in this application since the bottom of the plywood floors and joists would prevent most air movement if there is no air space above the fiberglass.

    Thanks for the inputs to help me think this though.

  • HomerJSmith
    HomerJSmith Posts: 2,837
    edited August 31

    Using heat transfer plates, no face, no space is fine. Without heat transfer plates you get banding, not an efficient transfer of heat energy. I like two runs of pex per bay, but may necessitate shorter circuits.

    Sounds like you have this all figured out. Use the new insulation that doesn't itch or your wife wont let you near her for a month.

    HydronicMike
  • Is there any fire hazard / danger in putting the paper face insulation with the paper in direct contact with the aluminum plate ?

  • pecmsg
    pecmsg Posts: 7,634

    how hot are you running the floor heat?

  • hot_rod
    hot_rod Posts: 28,704

    Ignition point is probably 450°F or so. Rarely do you need to run over 130, 140F max. on any plate system. 115- 120 is a design temperature example.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Ignition of kraft paper faced fiberglass, styrene foam insulation, or the wooden structure isn't an issue with the temperatures used for hydronic heating. However, expanded or extruded polystyrene isn't suitable above about 165 f. The hydronic heat won't ignite it, but it softens and causes it to lose the properties that make it suitable for insualation. If the temperature exceeds the design limit, polyiso insulation or fiberglass should be used. When I was designing my system I found that polyiso (more expensive and not as readily avaiable) was frequently recommended for use in radiant walls, but I didn't plan for the water temperature to ever exceed styrene's limits. The higher heat used for baseboard could easily exceed that limit if the pipe/tubing is close to the styrene.

    In some places building codes require that flamable insulation be covered with a flame resistant coating such as drywall or plywood, but that's to protect it from an external ignition source, not from the heat from the hydronic system.

  • skyking1
    skyking1 Posts: 164

    mine is no face no space as mentioned above over heat transfer plates. Less costly and gets the job done.