Energy Kinetics Resolute owners — looking for real-world feedback

Options
ahchang
ahchang Member Posts: 3

I'm considering replacing my Weil-McLain Gold oil boiler with an Energy Kinetics Resolute. Most reviews I've found are for the EK Frontier, so I'm hoping to hear from actual Resolute owners.

If you've had one installed, I'd appreciate any feedback on:

  1. How long has it been running, and has it failed? If so, what caused it?
  2. Any exhaust odor issues near the house (sidewall vent especially)?
  3. Any siding staining from the vent?
  4. How does actual fuel usage compare to your old boiler (vs. EK's advertised savings)?
  5. Was parts/service support easy to find locally?
  6. Can you share the installers you used if you are in Eastern Massachusetts?

Thanks in advance for sharing your experience!

Comments

  • pecmsg
    pecmsg Member Posts: 7,440
    edited July 24

    as with all equipment like this installing contractor is the biggest factor in how well the equipment works. following manufacturers recommend recommendations and you can get a very long life it cutting corners your guess is as good as mine


    Energy kinetics is a very good system with excellent Tech Support, just ensure the tech doing the work have been trained on it and not justone person at the company

  • ahchang
    ahchang Member Posts: 3
    edited July 26

    Hi @BKfromEK, thank you. I will send you a message.

  • HVACNUT
    HVACNUT Member Posts: 7,611

    @ahchang , are you eliminating the chimney? Why go with a power vent if not needed?

    I also have a WM Gold, and my EK-1 Frontier is in my garage waiting patiently. I originally considered the Resolute for the extra efficiency. I even got a quote pre Covid from my Regional Manager. Life happened so I couldn't do it then. I've got an interior chimney in good shape, so I'll make use of it with the Frontier.

    You'll be happy whichever model you get. I can't wait to not hear my boiler.

  • ahchang
    ahchang Member Posts: 3

    @HVACNUT Thank you for sharing!

    My preference is to keep venting through the chimney, but it needs a stainless steel liner and an all-fuel connector replaced at the base, since the current one is too close to combustibles — about $5K upfront, plus sweeping every 3-5 years. Sidewall venting needs replacement every 7-10 years instead. As long as I can confirm sidewall venting won't cause odor or staining issues, I believe it makes more sense for my situation. Your thoughts?

  • Steamhead
    Steamhead Member Posts: 18,802

    Do the chimney work- you'll only have to do it once if done right. Sidewall venting introduces more moving parts which usually break down in the middle of winter.

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

  • hot_rod
    hot_rod Member Posts: 28,075

    the concerns you have with sidewall venting, staining. smell, noise, would be specific to your job,

    Typical wind direction, proximity to inside corner , etc.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • HVACNUT
    HVACNUT Member Posts: 7,611

    I don't see an awful lot of oil power vent boilers, but the ones I have seen were due to a fault with the PV itself or its operating controls.

    Unlike most retrofit PV applications, you'll have full serviceable access to the PV and the controls with the Resolute.

    Note that with the Resolute, it MUST use outside combustion air.