Anyone have tips on wall mounting Danfoss RA2000 remote thermostatic operators?

Options
rossn
rossn Posts: 161
edited July 22 in THE MAIN WALL

I have some Danfoss RA2000 remote thermostatic operators (one is 13G8562) that I'd like to cleanly wall mount (no drywall yet). The european mounting holes don't align with a single or double gang US device box, and they are shorter than the boxes. In my case, the longer operators will also be fed through smurf tube, in the event replacement is needed in the future.

Anyone have a trick that works well for mounting these to a box, which can feed the smurf, looks good aesthetically, and meets IRC and fire codes?

Adjacent switch plate covers are lutron, and matching whites is always hard than you'd think. Ideal would be no plate showing, so maybe an adjustable box against the back of the drywall?

image.jpeg

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,328

    All I can think of is maybe a Wiremold or Panduit box extension that you could mount on the wall with a blank cover plate on it. Then you could drill holes in the cover plate to mount the operator. Sensor could maybe come out the side of the box.

    If you want it to surface mount directly on the wall maybe have a sheet metal shop make some mounting plates especially if you have a bunch of them to do.

    Maybe contact Danfoss and see if they have a solution.

    rossn
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,940

    Call a local supply company in the UK

    Plumbsave
    32 Clemens Street
    Leamington Spa, CV31 2DN

    I'm sure that have the proper mounting hardware in stock. See if they ship to the USA.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    rossn
  • mattmia2
    mattmia2 Posts: 18,399

    It seems like if you are doing that much pre-planning that a motorized zone valve and thermostat would have been easier.

    Did you confirm that the cap tube comes off the actuator or control in such a way that you can get it through conduit?

    There is probably a nema to european adapter device strap out there somewhere. Most of the stuff i deal with has brackets with holes for both.

    rossn
  • rossn
    rossn Posts: 161

    @EBEBRATT-Ed - thanks. This is in a nice residential home, so a box that sticks out of the wall wouldn't be ideal. The custom cover plate could work, but I fear the costs will get high with that. I opened a case with Danfoss and see what they have to say.

    @EdTheHeaterMan - Thanks. I dropped Plumbsave an e-mail.

    @mattmia2 - The manifolds are already installed and I already have the operators, so I wouldn't want to switch at this point. Besides, I want the valve actuation that a thermostatic valve offers. Yes, the cap does come off and fits through tubing. Yeah, definitely looking for device strap with cover plate. Biggest issue here being that the device is shorter than a device box. Looking like the eaton. I need to check further to see if a hole in the drywall behind the operator would be allowable, or if it has to be re-mudded… this assumes I abut a box against the back of the drywall and use drywall anchors to physically mount the operator.

  • mattmia2
    mattmia2 Posts: 18,399
    edited July 22

    what about an octagon box or something like that?

    or a 4 square and a round mud ring

  • hot_rod
    hot_rod Posts: 28,699

    I think there is a mounting plate behind the cover. Just put some backing in the wall to fasten it to. I don't think it needs to be in a box, there is no electricity, or code to cover a capillary tube. As far as I know.

    End your fish conduit near the backing blocks.

    I thought I had a sample, but it is MIA

    Screenshot 2026-07-22 at 4.41.04 PM.png Screenshot 2026-07-22 at 4.46.25 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,399

    although you really don't want air blowing through a hole in the wall and affecting the element.

  • Big Ed_4
    Big Ed_4 Posts: 3,585

    I would assume the controller was designed to just be mounted on the wall and the tube is tucked behind .

    There was an error rendering this rich post.

  • Kaos
    Kaos Posts: 1,003

    I've ordered random stuff from the UK site before, shipping is reasonable and if it doesn't have power in it, it doesn't need to be rated.

    https://www.amazon.co.uk/Litt-Single-Pattress-Premium-Quality/dp/B0B75HPXJ2?sr=8-1

  • Steve Minnich
    Steve Minnich Posts: 2,964

    This is the reason i only use the pop on heads

    Steve Minnich
    PC7060