Replacing corroded class 250 or 300 black/malleable iron pipe & elbow on WGO-4 series 3

Options
masscat
masscat Member Posts: 12
edited May 6 in Oil Heating

Hi all, I need to replace, what appears to be, a heavily corroded class 250 or 300 malleable iron elbow and section of 4ft, 1-1/4" black pipe near the return of my Weil-McClain P-WGO-4 series 3.

  1. Can I use class 150 fittings/pipe? I can't easily find class 250 or 300. The manual doesn't seem to specify. Looking at an Anvil cut sheet suggests I can go up to a temp of 250F at 225PSI with class 150 fittings. The max temp I've observed on my heat gun exiting the boiler is ~190F, but I know the boiler is firing above 370F.
  2. The manual suggests front section B1 return piping has a 1-1/2" pipe size. My system looks like it immediately reduces to 1-1/4" at the return with a bushing (all the pipes measure 5-3/8" circumference…~1.71" diameter.
  3. I'm getting some used Ridgid tools (die head, ratchet, reamer, 3-wheel cutter, pipe stand). I'll have a retired machinist (dad) who installed/maintained his own boiler helping, but he prefer sawzall and hasn't done this in years.
  4. Any watchouts for draining the system?

See images below.

Corrosion-1.jpg Corrosion-2.jpg Corrosion-3.jpg

Comments

  • pecmsg
    pecmsg Member Posts: 7,142
    edited May 6

    those look like schedule 80 fittings. There used on high pressure systems.
    I don’t think you need something that heavy on a domestic boiler.
    I hope there’s a union nearby!

  • mattmia2
    mattmia2 Member Posts: 17,031

    if this is hot water you can replace it with pretty much any black fittings and pipe or you could also replace it with copper.

  • masscat
    masscat Member Posts: 12

    Baseboard heat. Indirect HW is on the other side.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,302

    You can certainly use 150# malleable or 125# CI fittings. They are the same dimensions as the 250 or 300# fittings.

    As mentioned above copper is a good choice as well

  • hot_rod
    hot_rod Member Posts: 27,613

    a sawzall, handheld power threader, union and some new fittings is the fix.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream