My rental condo unit's master bathroom is getting very little cold water and then no cold water at all in the mornings (6-7am). So basically hot water coming out of the fixtures even when turned cold. This happens at all 4 fixtures. 2 sinks, a shower and a bathtub. It's been happening for a month.

The condo manager is hiring a plumber to inspect (shower body, faucets). He said he will bill me back if the issue is specific to my apartment. (He has a track record of pushing building problems back onto owners.)

1. Boiler was replaced end of October 2025. We have oldish supply pipe. Copper sweat. ~50 years old.

2. We recently got some additional common charges for pressure work b/w 5th and 6th floor. My unit is on the 5th floor.

3. And charges for a leak b/w 5th and 4th floor. (Adjacent to my unit) - not sure if DWV or Copper pipe.

4. 6th floor unit above me has low hot water pressure after a recent shutdown (Early April)

5. Another 6th floor unit (adjacent to unit above me) has very little hot water during the same time my tenants have an issue.

6. There have been recent renovations in nearby apartments.

7. My bathroom's risers come up and feed the vanity sinks, then supply the toilet. And then the shower. And then a separate bathtub. It is possible the shower catridge mixing components are damaged and allowing hot water to cross over to the cold line. This only happens in the morning. I think people are using more hot water (showers) in the morning than cold water (toilet). So the pressure on the hot side has to be so much higher than the cold side to over come the cold supply pressure so as to force hot water all the way back to the vanities. We're talking about a 10'x6' bathroom. So a lot of pipe distance and hence water volume. But I guess this is possible.

8. If the hot water pressure is that high, why is one unit on the 6th floor not getting enough hot pressure. And another unit is getting too little hot water. He ends up taking cold showers.

9. My tenants turn off the water and go to the 4th floor bathroom to get ready. (It's a duplex). No problem in that bathroom.

10. Lets go back to the new boiler. ITs a boiler not a hot water tank supplying hot water. So there is a master mixing valve. It takes 180F water and mixes it with cold to achieve ~120F. There could be some failure at the mixing valve.

11. There is also a recirculation pump. Keeps hot water available so you don't have to wait for it on the higher floors. 6 story building.

My guess is when balancing the pressure on the recirculation pump, something went wrong. Too much pressure on the 5th floor and too little pressure on the 6th floor.

What do you guys think?

Comments

  • Mad Dog_2
    Mad Dog_2 Posts: 8,758

    Oh boy...that's going to take some time physically on the job. That sounds like a real one-sided situation there. Mad Dog

  • Larry Weingarten
    Larry Weingarten Posts: 4,212

    Hi, the first thing I'd check for is crossover… water leaking from hot to cold in this case. Create the problem and then "look" at the plumbing with an IR camera. With a little luck, it will lead you to the problem or problems.

    Yours, Larry

    branimal
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,025

    I believe that supplying water at temperatures that could cause scalding from a common water heater system may be a code violation that the building owner is responsible for addressing, without passing the cost on to you.

    Does the local Department of Health or the Authority Having Jurisdiction (AHJ) know that your landlord is supplying excessively hot water to your apartment? I would recommend documenting this as soon as possible so you have clear proof of the issue.

    If your landlord later attempts to charge you for the repair by claiming the problem is specific to your unit, you will have documentation. At that point, you can involve the AHJ and request a written response confirming that maintaining code compliance is the responsibility of the property owner—not the tenant.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    branimalLarry WeingartenMad Dog_2
  • hot_rod
    hot_rod Posts: 28,776

    a failed check valve could be allowing the recirc hot water to push into the cold side

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Larry Weingartenbranimal
  • branimal
    branimal Posts: 304

    I think I figured out what's going on..... lmk if i'm off base. (I own Apt 501)

    Facts first / then an opinion.

    • Apt 602 – when he has water temperature issues, it’s because there isn’t enough hot water to mix with the cold. This happens in the mornings. This is the inverse of the issue Apt 501 is experiencing. (Too much hot water in the mornings). Perhaps hot water is getting diverted before it reaches 602's pipes.
    • Apt 601 – has been experiencing significantly less hot water pressure in the kitchen since a recent water shutoff
    • XYZ Plumbing has recently done work to address water pressure issues on the 6th & 5th floors.
    • XYZ Plumbing has recently done work to repair a pipe leak from 502 to 402.
    • New Boiler installed (~October 2025). New boilers exert higher effective pressure on the pipes than our decommissioned boiler. I would guess the majority of our riser and branch lines are from the mid-1980s.
    • Apt 501 – Very limited cold water in the mornings (~615a – 715a). After a few minutes the water is unusable at the shower and two sinks. This is the exact time slot that 602 is experiencing “not enough hot water”. Because 501 operates perfectly outside of this window, the internal hardware (shower cartridges/faucets) is clearly functional.
    • Apt 501’s shower, vanity sink 1 and vanity sink 2 are getting hot water when turned to the cold position during morning rush hours. What are the chances that all three cartridges are damaged at the same time? And then start working outside of the stated early morning hours.

    • It could be a pressure balancing issue at peak load time. There is high hot and cold water demand in the morning. (Showers/Toilets). Hot water is pressurized by a recirculating pump/ variable speed pump (new boiler). Cold water relies on street pressure. So hot water pressure becomes higher than cold water pressure and pushes into the cold lines. When water demand drops (after peak morning hours), the hot water recirculation pump reduces pressure. Hot water pressure and cold water pressure get closer to equilibrium and there is no crossover from hot to cold. This would explain the phenomena we are witnessing in the morning hours.

    I don't know if we have check valves under our shut off valves. I don't recall seeing one when my bathroom/kitchen was renovated.

  • Jamie Hall
    Jamie Hall Posts: 28,004

    Since all this started, I gather, when the new boiler was installed — along with, I expect, a fair amount of plumbing rearranging in the boiler room — that's where I would go looking. Not in the individual units.

    One thing — it is unlikely (unless something was done incorrectly — that the recirculation pump could add any pressure. At least, it shouldn't. What it can do, however, in the absence of check valves, is take hot water from one set of lines and run it into the cold water lines of another set, when there is demand on those lines and hence lower pressure on those lines. Which it shouldn't be able to do, if there are check valves where needed.

    In any event — back down to the boiler room and figure out how each unit gets its hot an cold water, where each unit's recirculation lines go, and so on. Don't assume that ANYTHING was done right until it is veriried.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Mad Dog_2branimal
  • hot_rod
    hot_rod Posts: 28,776

    Whatpressure is the water coming into the building? How many stories? At 7 storiesn then pressure at the top will be about 30 psi lower than street level.

    601 could be as simple as a plugged screen in the faucet. It sounds like a cross connection somewhere in the building.

    Any janitor mop sinks? They sometimes have Y hoses that cross over. But any single handle mixer is suspect, or electronic faucets with H&C always on.

    This may be a time consuming troubleshoot.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mad Dog_2branimal
  • I'd definitely suggest starting with building-wide scope rather than trying to nail anything down to a specific unit off the bat. What can you tell us about the following?

    How does the building handle cold domestic water? gravity tank, booster, or is city pressure sufficient? the specific scenario your building has can change how things interact, Can you verify city pressure into the building if relying on only city pressure? Old gauges are often frozen or inaccurate, swapping in a new gauge to verify is good practice.

    -hot domestic is usually pressurized through the cold so usually the hot in a building will have slightly less psi than the cold. But sometimes if a building has enough issues they will add a booster pump for additional hot pressure as a band aid fix rather than correcting plumbing issues. Since your building seems to be more on the special side, do they have a separate hot water booster?

    -Verify the operation of the main mixing valve, what is your cold in, hot out, and recirc return temps. Don't just look at the thermometers that might be installed. 80% of the ones I see stopped working correctly decades ago. A thermal camera is very much preferred for this over a laser thermometer.

    branimal
  • branimal
    branimal Posts: 304

    Just to clarify, I'm not the plumber on this job, nor am I a plumber 😂. (I do know some basic plumbing). I'm an owner of a unit (401/501 duplex) in this building.

    (Italics is emails from building manager)

    Yesterday (4/24/2026) the plumber came by. "Plumber checked domestic pump and all check valves in basement. Everything is in order. Plumber checked plumbing in 302 sink and cartridge in 303 shower."

    The plumber will check my unit on Monday morning. I am not sure what he's going to check, but I will be present.

    Here are the facts rehashed:

    1. 501 (my unit) is duplexed with 401. The issue has spread to 401. Sink and shower scalding hot water.
    2. Scalding hot water only happens in the early morning hours 5am-6am ish. And then water temps return to normal behavior
    3. This only happens intermittently - not every morning
    4. Unit 602 has the opposite problem - not enough hot water. In the mornings, but not every morning

    Here's the service work history that I have pieced together:

    1. January 2024 -
      1. "New domestic pump is consistently providing 70 PSI";
      2. "Heat pump controls pressure to apartments";
      3. Street cold water pressure is approx 50-60 psi. Building is 6 stories tall.
    2. September 2024 : Branch line b/w 402 and 502 replace due to leak
    3. May/June 2025 Plumber dealt with pressure issue on 5th and 6th floor
    4. October 2025 : Boiler replaced
    5. After a water/heat shutdown 4/17/2026 - the plumber checked a couple of apartments for pressure and temperature; no issues found. The fact that they are checking tells me they know there's something wrong. Quote from building manager "We are constantly in touch about this issue".

    @hot_rod pressure is 50-60 psi from the street. 6 story building. There is a janitor mop sink from what I recall in the basement. What do you mean by an electronic faucet that is always on?

    @pumpcontrolguy

    • Cold water is city pressure (50-60psi according to google).
    • Building manager mentions both a new domestic pump and a heat pump controlling pressure to apartments. See above.
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,025

    Have you contacted the AHJ on ths problem? Building code enforcement, local department of heath, Maybe even the plumbing inspector? Your municipal website should have information on what municipal departments cover renter's rights in your location. At least file a notice that you have this problem with that department. Even if they don't come and inspect it at 6:00AM. St least there is a record of the complaint on file with them.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    branimal
  • Larry Weingarten
    Larry Weingarten Posts: 4,212

    Hi, I'm always looking for excuses to get tools, and this seems a perfect opportunity for you. I recently got a very inexpensive thermal camera that plugs into my phone. Here are photos of the phone and my cat, who clearly has a cool nose. This tool could really speed up tracing down and finding the plumbing problem/s in your building.

    Yours, Larry

    Qi heat.jpeg IMG_6106.jpeg IMG_6107.jpeg
    branimal
  • branimal
    branimal Posts: 304

    The building plumber came by this morning. Multiple apartments have been having issues as well. "Cold water is warm" seems to be the theme. As well as low pressure.

    The plumber checked things in the basement (idk exactly what he checked).

    He thinks one or more shower cartridges have gone bad in the building. I have two bathrooms in a duplex apartment (401 & 501). He shut off the cold water shutoff. Turned my shower's thermostatic valve to cold. And turned on the shower. And there was a slow drip of warm water. He says it's my bad cartridges that's causing the problem. I am not sure how a bad cartridge on the 4th floor bathroom can propagate to the 5th floor bathroom. We did the same check on the 5th floor and there was no issue.

    I guess my next step is to replace the cartridge.

    IMG_6410 2.JPG IMG_6412 2.JPG
  • pedmec
    pedmec Posts: 1,488

    The shower valve should be pressure balancing so to have a small drip is ok. Its suppose to shut the flow down with a loss of pressure on either side of the valve. the valve is doing its job. Unless there is something specific with the shower valve that test don't prove anything .

    Larry Weingartenbranimal
  • gotcha, so Booster pump just does a tiny little bit of pressure, which means when he's talking about a heat pump, he's probably just talking about a circulator to keep the lines hot, not to actually pressurize anything. If you had a large pressure differential between hot and cold pressures, that can throw cartridge balance off and cause poor behavior, but I doubt that's the issue here.

    I also agree that it's too early to pin everyone's issues on your shower cartridge.

    Any chance you have isolation valves for just your shower body and you can shut it off for a period of time to see if the problem goes away when you do?

  • branimal
    branimal Posts: 304

    There is a shutoff for both hot and cold in this bathroom. No shutoff for just the shower. So shutdown would impact, sink, toilet and shower. This is a secondary bathroom for the tenants, so maybe they can shut it off for a few hours.

  • That's really useful then. Id do whatever you can to have them do that to see if you can confirm if it still happens or not with that bathroom isolated. A mild inconvenience to perhaps prove that it's a building problem and not a unit problem.

    branimal
  • branimal
    branimal Posts: 304

    Follow up on this post:

    1. I got my monthly common charge with an additional plumbing charge - notes from the plumber:
      1. "Responded to a call for a hot water bypass on the 01-line of apartments. Traced for cause. Tested the plumbing fixtures on the 01-line as well as the boiler room and risers. Found a shower body cartridge in apartment 401 (my apartment) causing the bypass and in need of replacement. Informed the owner. Owner to complete the repair with others."
    2. I never replaced the shower cartridge b/c I never got a follow up from the plumber or building management that my shower cartridge was the cause of the water temperature issues.
    3. Contacted my tenants regarding the issue today. They haven't had issues since the plumber was there in late April.

    So it wasn't my shower cartridge, but the building is trying to charge me for it. The charge is for 2.5 hours of the plumbers time. A lot in NYC. I want to respond and tell them to kick rocks. But I'm going to be civil and point out the obvious sequence of events.

  • pumpcontrolguy
    pumpcontrolguy Posts: 82
    edited June 24

    So they said the cartridge was bad, never replaced it, but the problem is also now resolved?

    If your building is like most single boiler buildings, it's on summer mode right now and firing only as needed to just keep domestic the right temp. I'm thinking your problem might return again next fall/winter when it's cold out again and the boiler begins running for actual heating again.

    You might not have much pushback right now, but if the issue returns next heating season, you have a great argument to credit you for the plumbing charge.

    edit: It could still be an issue with your shower cartridge, but if the main mixing valve is also not quite right, both things could have been contributing to the problem which is why it might be "fixed" now.

  • branimal
    branimal Posts: 304

    I don't plan to pay the plumbers bill. The plumbing repair occured in late April. Water service has been working perfectly since according to my tenants.

    I will ask the condo board what the plumber repaired to get the water service functioning properly. My guess is they won't give me a straight answer. They have a history of socializing building wide issues to unit owners.

    Since I never replaced my shower cartridge, I would guess the problem was not related to the cartridge. Just to rehash the issue with my cartridge : "He thinks one or more shower cartridges have gone bad in the building. I have two bathrooms in a duplex apartment (401 & 501). He shut off the cold water shutoff. Turned my shower's thermostatic valve to cold. And turned on the shower. And there was a slow drip of warm water. He says it's my bad cartridges that's causing the problem. I am not sure how a bad cartridge on the 4th floor bathroom can propagate to the 5th floor bathroom. We did the same check on the 5th floor and there was no issue."