Webster Vent Trap??

Options
Paul S_3
Paul S_3 Member Posts: 1,297

Hey guys. Hope all is well. A friend of mine is on a job and he is asking me if I know what this is. is this just an air eliminator or a vent trap. Steam is leaking out the top. It doesn’t look like a boiler return trap. Also what can be done to replace this because it’s not a threaded port on top.

IMG_1623.png
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company

Comments

  • Steamhead
    Steamhead Member Posts: 18,532

    It's a vent trap which is the same as air eliminator. Not sure what brand.

    He needs to look for the bad trap that's letting steam into the dry returns that the vent trap is connected to. Just follow the steam-hot return to whichever rad return runout(s) are steam-hot.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Paul S_3
  • Paul S_3
    Paul S_3 Member Posts: 1,297
    edited 1:12AM

    thanks @Steamhead so it has to be a bad trap or traps at the radiators. Even If the boiler pressure got too high from a clogged pigtail and backed water up into that vent trap the vent trap float would close the vent and air lock the system? Is that how these work?

    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Jamie Hall
    Jamie Hall Member Posts: 27,401

    More or less. The key is the comment "steam is leaking out the top". On two pipe steam systems, steam should neveer get into the returns (well, hardly ever — but that's another matter). If it does, some steam trap somewhere has failed — and you need to find it.

    The float should close the trap outlet if the pressure gets too high — but there are a host of other problems high pressure will cause, most of them non-obivious, so get the pressure under control as well.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Paul S_3
    Paul S_3 Member Posts: 1,297

    can this be replaced with a return venting manifold as long that the boiler pressure is maintained low ?