Steam radiator valve and convector valve difference

Options
anatori25
anatori25 Member Posts: 21
edited 7:16PM in Strictly Steam

Hello,

When installing steel convector, I used steam radiator angle valve 1 1/4 from Home Depot. I bought convector element from OCS Industries. I didn't pay attention that they have 1 1/4 convector valves. I have problems with my setup (clicking noise, etc.). Can it be because I used wrong valve? BTW what is the difference between these two valves?

Thank you in advance,

Comments

  • mattmia2
    mattmia2 Member Posts: 16,886
    edited 7:11PM

    pictures?

    it could be, water trapped in the convector because of the valve geometry or it could be just the convector expanding, depends on the noise.

  • anatori25
    anatori25 Member Posts: 21

    @mattmia2

    Here are the pictures…

    20260324_162059.jpg 20260324_162014.jpg
  • anatori25
    anatori25 Member Posts: 21

    Clicking noise… It can be much louder early in the morning, when the building steam system is on for the first time.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,265

    Are your valves fully open? A convector valve is ofter a globe style valve as is the steam valve you show in the photos.

    this is an excerpt from a book on steam heating systems:" On a one pipe steam system, valves should be operated fully open or fully closed never left partially open, as that can trap condensate and cause banging/noise.

    The convector valve is often a smaller, more compact globe or ball-style valve, sometimes with a screwdriver-operated stem. Depending on the convector valve you purchase, it may be either a ball valve or a globe valve, and it may be configured as an angle valve or a straight valve. In either case, that valve also needs to be fully open on a one-pipe steam system.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,601

    This is a typical convector shutoff valve. The orientation is convenient, when installing sunrads.

  • ethicalpaul
    ethicalpaul Member Posts: 8,850

    That's one of the nicest convector installations I have ever seen in my non-career. Although I'm a little concerned about how you got that large angle…see below (I hope it didn't cause the issue I describe there)

    But having said that, that sound is water hammer and according to your description of it being more prominent after a long off-time it is no doubt due to some condensate lying in a pipe somewhere.

    I would bet it is below your valve somewhere…a horizontal section that has become less than horizontal.

    I have heard contractors say it can be cured with insulation, but that is false. You have to find the sloped pipe that is acting like a trap and fix the slope so it doesn't capture water.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    EdTheHeaterManSTEAM DOCTOR
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,265
    edited 8:59PM

    This might have been a better choice with a strait valve under the convector element. that way you can fill the space with convector and not have that mush empty space on the right end of the opening. But i agree with @ethicalpaul on the job. nice work!

    image.png

    See the strait valve on the right opening? and again it must be fully open.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • mattmia2
    mattmia2 Member Posts: 16,886

    you might try raising the valve end some to see if it pulls up the riser and takes the sag out of something below the floor.

    ethicalpaulEdTheHeaterMan
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,601

    Or just eliminate the valve entirely

  • ethicalpaul
    ethicalpaul Member Posts: 8,850

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    STEAM DOCTOR
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,601

    Agreed. My intention was, instead of busting your chops tried to figure out which valve to use, just eliminate the valve entirely. It has no real function, at least the residential settings. And even in apartment buildings, get a valve on the air vent side.

    ethicalpaul