Remodeling a 100-year-old house and dry-fitting Slant/Fin baseboard. I have a 55" run in a bathroom where half the room has wood base (fin tube + enclosure installed), and the other half is fully tiled.

In the tiled section (tight clearance next to a toilet), I’m planning to run exposed supply/return only—no enclosure. Pipe penetrates the wall at ~9" above tiled finished floor

due to plumbing/electrical conflicts; fin tube elsewhere is at ~3" AFF. Considering offsetting with 45s to hug the corner, or running low and sweeping up (45/90) into the wall.

Suggestions support a ~55" horizontal run of exposed pipe without penetrating tile. Options I’ve considered: standoff/cradle supports, surface-placed raceway/soffit (which is the wood piece in the picture, adhesive-mounted clips, or leave it bare and hung close to the corner/wall.

Comments

  • pecmsg
    pecmsg Member Posts: 7,083

    Get a "Plastic" slant fin enclosure to hide it.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,271
    edited April 13

    I might get a tubing bender from one of your ACR friends that work with line sets for refrigeration and do a custom bend.

    Screenshot 2026-04-13 at 10.57.19 AM.png

    if you want to get really fancy, send the piece out to a shop to have it chrome or brass plated to match the bathroom fixtures.

    image.png

    Then you just epoxy the split ring hanger flange to the floor. …and Bob's your Uncle!

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • hot_rod
    hot_rod Member Posts: 27,501

    anything metallic near a toilet can be a corrosion problem

    Slantfin had a painted stainless version for bathroom use

    Pex with composite fittings ?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 16,890

    it technically only needs support every 10'. you can use plastic anchors in the grout lines of the tile and have it be repairable.

    RJG
  • HydronicMike
    HydronicMike Member Posts: 351

    Should've been addressed before you tiled. Anything you do may be undesirable, and you risk someone stepping on the pipe.
    Any chance you can come out of the wall, go up, and use a flat panel, low profile radiator?
    Or, it looks like it's going to be behind the toilet. I'd drill a hole, and go below the floor, and box it out in the back corner.
    Or get to the pipe on the other side of the tiled wall, re-route.

  • You could also delete the BB and install a towel warmer next to the toilet. Accessories include a toilet paper warmer.

    0-14.jpg
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    RJGEdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,271

    I like the toilet paper warmer idea. LOL

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?