Converting 2 pipe Bundy radiator to 1 pipe system
Comments
-
What size are the pipe connection tappings?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
-
I'm not at all sure they will. Why? Because it does not appear that they are connected across the tops of the columns — and that means that normal one pipe steam radiator venting, with a vent on the last section and air and steam moving across the top to reach that vent, won't happen.
But maybe… @Steamhead ?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
There is a bushing on the inlet end but it's hard to tell its actual size.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
There is a bushing on the inlet end but I can't tell what size it is.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thank you Steamhead, I noticed that too. Hopefully it’s 1 1/4” but I think more than likely 1” since that was standard. I just read that 1 “ supports 25-30 EDR if this style does actually work. Jamie that is a great observation. I was hoping
that the steam would push the air out through the columns in a up/down and repeat manner but I’m not so sure about that.
0 -
I made the Large Bundy in my Parlor two-pipe (The only one in my house). Its been 25 years, but I believe its 1" Supply. Ill look behind the couch tonight. Mad Dog
1 -
I have a round one and piped it just like Mad Dog did his on single pipe steam.
If it's going on the first floor you can use both pipes and put an inverted loop on the return into the bottom of the supply runout.
13 Loops, 36" high, 1-1/4 inlet, 1" outlet. The steam distributes up and down the loops just fine. Put a vent in the last loop if you need it.
2 -
Mad Dog/ Long Beach Ed could you please share a picture of the piping when you get a chance so I can better visualize/understand what I can do? I’m not exactly following your description. Thank you.
0 -
-
-
1" inlet on right. 3/4" outlet on left. No trap. Loop seal is in basement closet below. Mad Dog
1 -
-
Thanks for sharing. I wouldn’t be able to add a loop downstairs. Could something like this work for a larger radiator?
0 -
Lose the trap. You don't need it.
The check valve would have to have a very lightweight flapper so the weight of the water would open it. And the rad would need a vent.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements