When to let water out of boiler drain. Burnham Gas Steam
Hi, I am confused , just had new Burnham steam master max installed in 2 floor townhouse in Brooklyn. Every plumber I have talked to says ' Yea u should open the drain and drain a a gallon or two every week. maintenance, moreso if it comes out brownish to start' But on Page 3 of their manual it states DO NOT CONTINUALLY ADD FRESH WATER YOU WILL SEVERELY DAMAGE BOILER. I understand draining water means replacing water, so what is going on with this? Thanks for any help.
Comments
-
DO NOT drain any water, especially weekly.
If it was a float type LWCO, you should be dumping that weekly with the burner on, but I assume this new install has a probe type LWCO. Pictures would help us.
You may want to have the system flushed out every few years but other than that, no, no draining.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
-
That instruction of draining water weekly comes from an old style LWCO control that requires that procedure. They actually have the necessary valve as part of the control.
Unless you have one of the float type LWCO controls that instruction is not for you. Most new boilers are equipped with a probe type electronic LWCO control. They only require annual maintenance. Do not open any water drain valves during the heating season to let water out of the boiler unless it is required for servicing some other part of the system. You want to keep from adding fresh water on a regular basis.
That water in your boiler is actually equivalent to distilled water after several weeks of operation because it will all have been boiled off at some point to make steam then returned to the boiler as condensed water. That is the process for distilled water, boiling off the water and condensing it back into water. That way all the contaminants are left behind. That is what you don't want in your boiler or float type LWCO so you flush them out. But the new water added will contain more contaminants.
So if you don't have a float type LWCO, don’t add new water every week. Wait for the entire year of operation then you can flush out any muck that forms inside the boiler from that entire year of operation all at once. Make sense?
Hope this answers your query.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
once a month Max to check your LWCO. What company from Brooklyn said this out of curiosity cause that’s horrible advice. Even if you had an Older style 67, just enough to check proper function, not gallons. Do you have a picture of the install??
0 -
-
No I know but generally you open it 2-3x even four times testing it and you’re getting enough out to accomplish both. Certainly don’t need gallons of water, at least in my opinion. But I’d also be very shocked if he had a 67
0 -
So, I was talking to a Burnham rep that told me they have a water quality issue that the chlorides stay dissolved and get to a higher concentration because of the location of the flue. Apparently they have a tendency to rot the return nipple so draining the steam max is actually a good idea. Could have been BS but it sounded like logic unless the water was treated.
1 -
The return nipple mostly sees condensate so I'm not sure how draining the boiler would assist with that. And in any case I would much rather replace a return nipple than a boiler. If I owned it I wouldn't be draining it more than once per year for no more than a gallon.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 118 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 57 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements