Spray Foam and Steam riser
I am renting an apartment and I noticed the steam radiator risers at the ceiling are plugged with what I think is great stuff expanding foam. I looked it up and saw that this foam is only rated for up to 240F and says not to use with radiators . I heard that steam risers can get to around 220 if working normally. Is this rating for when the foam starts to degrade or does it literally combust at that temperature. I want to know if this is an urgent fire risk I need to worry about or not. Thanks for any help
Comments
-
How long has it been there ?
Here is the MSDS or SDS. Not sure if it is current. It appears it is referring to the uncured state.
Not sure if radiator pipes require a fire block caulk, or if the gap size is an issue (building codes).
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Is there a customer service number on any of the information you have on Great Stuff? That is the number to call for that information?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
From what I remember about Great Stuff and other polyurethane insulation is that it is combustible and will melt if it catches on fire and supports flame spread. The operating temperature range should not exceed extended 200° exposure. Since Steam will be near and above that temperature on a regular basis It is not recommended for insulating stream pipes.
You probably will not experience spontaneous combustion at 200° to 220°, however the product will dry out, you may experience off gassing, and it will start to turn a darker color.
The product will ignite if exposed to 700°F to 800°F however so will the rest of the building's combustible components.
You may be looking at a product that is known as Fire Block which is designed to seal up openings in floors and walls to prevent air movement within a structure. That product is rated at a slightly higher temperature however it is not designed to insulate pipes. It is designed to fill gaps. Best practice would be to use fiberglass pipe insulation designed for steam pipes and then use the spray foam so it fills the gap between the fire rated floor or wall and comes in contact with the insulation NOT THE STEAM PIPE ITSELF.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
I had considered using spray foam around my steam piping, but I didn't want a disgusting stinky sticky mess, so I didn't.
I doubt it would burn, but it'll smell and probably offgas and dry out as Ed said.
Spray foam is excellent has it's places, but this isn't one of them.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
That would look great too @ChrisJ
look closely at this section… Could there be a Wye Strainer that will never get cleaned?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
4 -
It's too early for that stuff Ed.
Ugh.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
@timbeans78, I've merged your duplicate discussions into one here to prevent confusion. Thanks.
Forum Moderator
0 -
Those are testable backflow preventers! I would love to be called out to test those. That wye strainer is a check valve that is (no longer) repairable.
0 -
they definitely bought the box for that.
0 -
All that piping and fittings must be the most expensive equipment for water in the whole building.
And they cover it with foam?!?
It hopefully passes only cold water and may sweat.
Pre-slit foam or 1/2" FG could not cost that much considering what the BFP set up cost.
0 -
Perhaps it's AI and not real.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Could be, but that picture was here on the wall maybe 2 years ago.
0
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 429 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 119 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 50 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements