I am renting an apartment and I noticed the steam radiator risers at the ceiling are plugged with what I think is great stuff expanding foam. I looked it up and saw that this foam is only rated for up to 240F and says not to use with radiators . I heard that steam risers can get to around 220 if working normally. Is this rating for when the foam starts to degrade or does it literally combust at that temperature. I want to know if this is an urgent fire risk I need to worry about or not. Thanks for any help

Comments

  • 109A_5
    109A_5 Posts: 4,759
    edited February 18

    How long has it been there ?

    Here is the MSDS or SDS. Not sure if it is current. It appears it is referring to the uncured state.

    https://www.fit.edu/media/site-specific/wwwfitedu/facilities/documents/msds-forms/DOW---Great-Stuff-Window--Door.pdf

    https://www.greatstuff.dupont.com/content/dam/dupont/amer/us/en/greatstuff-renewed/public/documents/en/great-stuff-consumer-safety-information-43-d100729-enna.pdf

    Not sure if radiator pipes require a fire block caulk, or if the gap size is an issue (building codes).

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,946

    Is there a customer service number on any of the information you have on Great Stuff? That is the number to call for that information?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,946

    From what I remember about Great Stuff and other polyurethane insulation is that it is combustible and will melt if it catches on fire and supports flame spread.   The operating temperature range should not exceed extended 200° exposure.  Since Steam will be near and above that temperature on a regular basis It is not recommended for insulating stream pipes.  

    You probably will not experience spontaneous combustion at 200° to 220°, however the product will dry out, you may experience off gassing, and it will start to turn a darker color.  

    The product will ignite if exposed to 700°F to 800°F however so will the rest of the building's combustible components.  

    You may be looking at a product that is known as Fire Block which is designed to seal up openings in floors and walls to prevent air movement within a structure.  That product is rated at a slightly higher temperature however it is not designed to insulate pipes.  It is designed to fill gaps. Best practice would be to use fiberglass pipe insulation designed for steam pipes and then use the spray foam so it fills the gap between the fire rated floor or wall and comes in contact with the insulation NOT THE STEAM PIPE ITSELF.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • ChrisJ
    ChrisJ Posts: 17,763

    I had considered using spray foam around my steam piping, but I didn't want a disgusting stinky sticky mess, so I didn't.

    I doubt it would burn, but it'll smell and probably offgas and dry out as Ed said.


    Spray foam is excellent has it's places, but this isn't one of them.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,946

    That would look great too @ChrisJ

    Untitled Image

    look closely at this section… Could there be a Wye Strainer that will never get cleaned?

    Screenshot 2026-02-17 at 11.43.20 AM.png

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    CLambratio4GenPlumberPeteA
  • ChrisJ
    ChrisJ Posts: 17,763

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • @timbeans78, I've merged your duplicate discussions into one here to prevent confusion. Thanks.

    Forum Moderator

  • Those are testable backflow preventers! I would love to be called out to test those. That wye strainer is a check valve that is (no longer) repairable.

  • JUGHNE
    JUGHNE Posts: 11,653

    All that piping and fittings must be the most expensive equipment for water in the whole building.

    And they cover it with foam?!?

    It hopefully passes only cold water and may sweat.

    Pre-slit foam or 1/2" FG could not cost that much considering what the BFP set up cost.

  • ChrisJ
    ChrisJ Posts: 17,763

    Perhaps it's AI and not real.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • JUGHNE
    JUGHNE Posts: 11,653

    Could be, but that picture was here on the wall maybe 2 years ago.