New fire tube boiler installed January 13 shaking pipes, unacceptable noise levels
Old house ( built 1935, 3 floors + basement), 9 radiators, circulating hot water. When the unit is running the copper pipes connecting the unit to the plumbing vibrate strongly. The result is that every pipe in the house (that carries hot water to the radiators) is vibrating. So the vibration is transmitted to support beams, floors and walls. The noise throughout the house is unbelievable. When it is running the vibrations are strong enough that the new copper piping can be observed to vibrate. And also felt. There is no way the force causing the vibration can be "contained". The previous unit was silent. Couldn't even hear the Taco circulation pumps. I think the source of the vibration must be the fan that pulls combustion air into the unit and propels the products of combustion out of the house.
Does anyone have any idea what needs to be done? If I can't make it quiet I'll have to rip it out and replace it. The previous unit was silent. It never occurred to me that I would need to specify "a quiet furnace".
Comments
-
It sounds like you're the homeowner and you just had this new boiler installed, yes? Did the installer do a combustion analysis on the exhaust gas and verify the exhaust gas composition was within range as required by the mfr for new installs? Have you contacted the installer and asked them to troubleshoot? What did they do/say?
If you search this website you'll find a number of noise complaints for Lochinvar Nobles. Unfortunately there can be several different causes. But there's no way every pipe in the house should be vibrating. With a vibration that bad, it could well be an unbalanced blower. If the installer can't figure it out, he needs to call Lochinvar tech support.
5 -
While there could be something wrong with the boiler… The pipe all needs to be supported properly so it doesn't shake like crazy and what you have there for support is basically nothing, it's not adequate enough. If the unit itself is shaking, like coming off the wall etc, you need to first start with a combustion analyses and tuning, gas pressure checks, check the venting etc. but that pipe will also need supporting.
4 -
-
not to be funny or make fun of a problem ,but maybe some flexible joints were good between boiler and the rest of pipes.
like in a car exhaust.
since it works there too.
other possible causes are every rotating thing like centrifugal fan, water pump(s).
The burner can't possibly be "that temperamental" or potent...
or maybe it's the date 13...
🙄
Bad to the Bone
Song by George Thorogood & The Destroyers ‧ 1982
0 -
-
The piping matters also. In some cases that boiler can be direct piped if you can assure adequate flow. Without adequate flow they can make some rumbling noises, maybe enough to rattle pipes. In some cases they need to be piped primary secondary.
Someone needs to be there and eliminates the variables until the noise stops.
It could be air, lack of adequate flow, out of balance fan, broken impeller vane in pump, combustion noise.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 116 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements