  • Toothed
    Toothed Member Posts: 13

    UPDATE: All is working as it should. Transformer fuse seemed to have been the issue. I am thinking I blew the fuse as I was replacing one of the zone valve heads, or when fixing some loose wiring on the control board. Initially I think It may have a been one bad coil and as I was replacing it I may have blown the fuse, which then lead to the all zones failed open scenario. That relay was not receiving power, which then made the DHW tank thermostat not be operational.

    Thanks so much for all the input, I very much appreciate it and it has helped get a better understanding of this system.

  • mattmia2
    mattmia2 Member Posts: 16,267

    my guess is a wire touched somewhere and blew the fuse, that stuff isn't dressed very well

    Toothed
  • Toothed
    Toothed Member Posts: 13

    Agreed. I redid the wiring with new connectors on the relay. I plan to redo the wiring on the main board this summer. Thanks again!