I have a small 2 story house w Dunkirk boiler situated in center of basement. 1 pipe system. At the end of 1 2.5 inch main, approx 20 feet, it T off to 1 3/4 pipe. About 4 feet from one half of the T are 2 vents stacked/ganged on one vent opening, a Gorton #1 and a MaidOMist 18. Time from furnace to vent opening is 1 minute w vents removed. With vents installed time is 1 min, 47 sec. The Gorton sits on top of the T and heats up first. The MaidOMist is on a 2 inch nipple (off to the side of the T) and take a while longer to heat up.

Does the MaidOMist vent take longer because it is a slower vent or is it because it is not right on the top of the T fitting?

Should I add another vent to the gang/stack/manifold (not sure what term to use) to try to get the time down to 1 minute,as it is w no vents screwed in?

Rad on this end of house are slow to heat.

Comments

  • ethicalpaul
    ethicalpaul Posts: 9,076

    I have to admit I don’t know what a Maid o Mist 18 is but regardless, 1:47 is pretty fast, there’s not much to gain there

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • I added Maid O Mist pic. I dont have others of the setup can but get em

  • Steamhead
    Steamhead Posts: 19,007

    It's a #1, meant to compete with the Gorton #1.

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

  • 109A_5
    109A_5 Posts: 4,759

    Seems like you could do better. The way I see it, the less time you are burning fuel (each cycle) to push air out of the system, the more fuel you will save.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    Intplm.
  • ethicalpaul
    ethicalpaul Posts: 9,076
    edited January 14

    Well you can only vent air as fast as the steam can heat the main so the vent usually isn't even the bottleneck. He's getting 1 minute with an open pipe and 1:47 with his current venting.

    Steamhead Member Posts: 18,267January 13

    It's a #1, meant to compete with the Gorton #1.

    Or the Gorton #1 was meant to compete with the Maid O Mist #1. I've never seen proof of which company set up their designs and numbering first.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Steamhead
    Steamhead Posts: 19,007

    I know Gorton had their #2 in the early 20th century. It was designed as the only vent in a Vapor system. The inside is the same as the smaller vents, only bigger.

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

  • Thanks everyone. Think I will add another Maid O Mist, try to get that time down closer to 1 minutes. From the chart above, looks like it vents a little more and it's cheaper. Can anyone suggest why I should go with the Gorton instead?

  • 109A_5
    109A_5 Posts: 4,759

    Since the orifice is removable, I kind of wonder if the with old Maid O Mist and maybe the new one (although it probably would void the warranty), if the orifice could be drilled out a bit more. To get a bit more air flow through it.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Steamhead
    Steamhead Posts: 19,007

    ISTR the D orifice is the same size as the valve seat, so no, that wouldn't help.

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

    ethicalpaul
  • 109A_5
    109A_5 Posts: 4,759
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • ethicalpaul
    ethicalpaul Posts: 9,076

    Warranty hahaha on a vent. I'm not really laughing at you, but rather at the unpredictable lifetime of any given steam vent

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • 109A_5
    109A_5 Posts: 4,759

    @ethicalpaul I thought you had at least one replaced under warranty, maybe I'm thinking of someone else. However thinking about it, who ever it was, I think the place they purchased it from did not want it back.

    Anyway it does not matter apparently the D orifice is the same as the valve diameter so modifying it is useless.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    ethicalpaul
  • I added another Maid O Mist. Time to heat at the vents went from 1:47 to 1:28.
    Not terribly significant I suppose but a change non the less. Just wanted to provide the update.

  • Steamhead
    Steamhead Posts: 19,007

    Did it even out the heating of the radiators?

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

  • No, it didnt really help any. I have one in particular on the end of that line, 2nd Fl that "works sometimes, sometime no". I am trying to correct things that appear wrong or could be improved upon.

  • Steamhead
    Steamhead Posts: 19,007

    Try a Gorton #2.

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

  • ethicalpaul
    ethicalpaul Posts: 9,076

    spending $150 to try to get the steam to the main vent faster than the 1:28 he currently has seems like a lot to spend for no possible noticeable gain

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • 109A_5
    109A_5 Posts: 4,759

    You could try a valve (inexpensive) and play with the main venting manually. Maybe a pipe plug with a hole drilled in it if you want to play with different orifice sizes.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    jeffatncx
  • Yeah, and as I understand it, with 3 #1 vents I am 3/4 of the way there already. Seems there is something else going on.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    I agree with @ethicalpaul I don't think increasing the vent size will do anything. Your already pretty fast. And you could easily be off 20 seconds or more from the start time as you can't tell exaclly when the water starts boiling.

  • 109A_5
    109A_5 Posts: 4,759

    My main venting timing starts the instant I have to pull my finger off the boiler's supply riser, I think it is fairly consistent.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    jeffatncx
  • ethicalpaul
    ethicalpaul Posts: 9,076

    if the riser is cool enough to hold, then you aren’t measuring the speed of venting, you are measuring the speed of the main getting heated by the steam.

    But either way it’s fine—sitting in a living room you can’t tell the difference as long as some decent venting is happening

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • 109A_5
    109A_5 Posts: 4,759

    You are correct.

    I guess I should add that is from a cooler start but while watching the cooler start and the steam coming up I also can hear the boiling and see the water in the sight glass start to move and the -1 - 0 - 1 water column pressure gauge just start to move. This all seems consistent with a hot start and my mains are insulated and don't cool down too fast.

    The end of my main has two valves, one to open air, and one that shuts off the main vent for testing and/or for maintenance. So I can go from an open 3/4" pipe vent to no main venting at all.

    Obviously a cold main takes longer.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    ethicalpaul
  • ethicalpaul
    ethicalpaul Posts: 9,076

    those valves are great for testing, cool

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • dabrakeman
    dabrakeman Posts: 1,038

    With only 20ft of 2.5" main and a few feet of smaller you have more than enough main venting. The warmer the pipes the more the main venting will come into play as less of the steam being produced is condensed warming the mains. Thus the steam has the potential to advance more quickly and push out air more quickly. By the way, this is one reason why people tend to hear more hissing from their vents in the extreme cold because mains and takeoffs are all warmer when there is less time between boiler cycles.

    ethicalpaul