Tekmar 356 question

Options
GM_73
GM_73 Member Posts: 6

Tekmar 356 is showing the mix demand icon in lower right screen. It however doesn't show any pump percentage in the bar graph. Is this normal?

Comments

  • hot_rod
    hot_rod Member Posts: 26,843

    Scroll through all the parameters, with the item button I believe, what is the supply temperature. Is the system heating? Supply to the system warm?

    Screenshot 2026-01-09 at 12.11.34 PM.png Screenshot 2026-01-09 at 12.12.23 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • GM_73
    GM_73 Member Posts: 6

    Customer is stating floors aren't as hot as they used to be. We replaced the Tekmar about 3 weeks ago because the screen was blank and the inject ion pump wasn't working. Customer sent screen shot of display, will be going there Monday.

    Mix temp- 113

    Boiler supply 183

    Outdoor ambient 52 (Chicago in January)!

    Thank you

  • 109A_5
    109A_5 Member Posts: 3,590

    I believe just because there is mixing demand that does not guarantee injection pump activity if the Mix Target has been satisfied. There may be more influences than just Mixing Demand for injection pump activity. Some settings may have to be changed for their comfort at the expense of best efficiency. Maybe it is just the weather, not enough heat loss since it is unusually warm out.

    image.png image.png image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    Ironman
  • GM_73
    GM_73 Member Posts: 6

    Thank you for the responses thus far, really appreciated! Went to customer today, Jan. 13. Still not heating enough. Since installing the control, have yet to ever see the pump running. Test button does actuate pump. Jumpered the injection pump and manifolds warm nicely, supply and return which tells me IF the injection pump runs, they will have heat. I have set this up as a reset control. Couple of points I'd like to note.

    1-Set outdoor Design to 0 degrees- Chicago. Room temp to 75

    2- Looking at the manual one would believe that jumpering terminals 7 and 9 would actuate pump. However I now realize that other criteria must be met for that to happen (supply temp and boiler return temp).

    3-As a test I'm considering changing terminal unit setting to fin tube or cast iron radiator, see if the inject ion pump runs (briefly).

    4-Supply sensor reads 113 degrees tho a thermometer reads supply as 89-90. Possible incorrect placement of sensor? System has worked perfect ly past 22 years however…

    Sorry for the rambling, frustrated.

  • 109A_5
    109A_5 Member Posts: 3,590
    edited 8:01AM

    Your Item " 4-Supply sensor reads 113 degrees " This does not agree with previously posted information.

    If there is demand and the boiler is running what is controlling the boiler's circulator ? If the boiler is running and the boiler's circulator is running, 113 degrees (Supply sensor) seems low and 89-90 would be even worse.

    What is the Target Mixed supply set for ?

    Maybe the sensor is bad.

    Another thread (link below), long read, but may help you.

    Claimed it worked for 21 years, and then something changed, it was resolved (long story short), the boiler pump was not wired into the system correctly. In this case when the Tekmar 356 sensed the boiler was hot enough it would end the call to the boiler and that would turn off the boiler's circulator. So no more heat to the system until the Boiler Supply sensor cooled enough. Tekmar's note below warns about that situation. In that case the system's drawings helped a lot.

    https://forum.heatinghelp.com/discussion/comment/1869060

    image.png image.png

    Is this set correctly ?

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Member Posts: 3,590

    Looks like the Boiler Supply / Boiler Return, Mixing and the Outdoor Reset Sensors have the same resistance properties.

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System