Main vent failure?

Options
Aack08
Aack08 Member Posts: 16
edited January 7 in Strictly Steam

Hi everyone, we replaced our two mains last year that had failed with Gorton No. 2s and our system has been working well, mostly quiet, well balanced, etc. Within the last few days our upstairs radiators are venting a lot more loudly and are now leaking water from the stem valves. This has happened to us before and it resolved when we made a change to a downstairs vent and replaced the mains. I'm having a hard time telling if one of our mains has failed; it makes a slight gurgling sound so my guess is yes but it's less than a year old so I'm stuck between paying $___ (edited to remove specific pricing) for a new one and being wrong about it failing or paying $____ for the steam specialists nearest us to come back up and tell me the problem.

Any advice is much appreciated, thank you so much! (I tried to attach a video for reference of the sound before I realized that's not an option).

Comments

  • dabrakeman
    dabrakeman Member Posts: 1,017

    We need to find out why you are getting water up into your main which is likely the cause of your vent failure, that or too much pressure. Start by taking some photos of your boiler from distance at multiple angles. Also include a photo of your pressuretrol and your main vent placement.

  • Aack08
    Aack08 Member Posts: 16
    edited January 4

    Thank you, here are a few, if different angles will be better I will be happy to re-take these (the pressuretrol and PSI pictures were taken while the system was running).

    Also for context I forgot to mention our boiler is brand-new as of March 2024 if that helps at all.

  • dabrakeman
    dabrakeman Member Posts: 1,017

    Piping actually looks good.

    Do you see any surging in the site glass when the boiler is steaming, more than a half inch or so? How much skimming do you recall doing or having done when the boiler was installed?

  • 109A_5
    109A_5 Member Posts: 4,067

    What is this valve for ? Is it closed ? I probably would have put the main vents up a bit vertically.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • ethicalpaul
    ethicalpaul Member Posts: 8,850

    Skim tapping. Closed and capped.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • 109A_5
    109A_5 Member Posts: 4,067

    @ethicalpaul Ah yes, thanks, its an oil burner. Camera angle got me, when I first saw it I thought it was Teed into the wet return.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    ethicalpaul
  • Aack08
    Aack08 Member Posts: 16

    Thank you all for looking at this!

    We do skim the boiler about once a week and we try to flush it every few weeks, we do get a lot of gunk through the system but when we got the new boiler they also replaced a lot of the basement pipes which has helped a little bit.

    For the sight glass, I haven't noticed much, if any surging, but to be honest I didn't check this specifically yesterday so I will need to confirm that when I get home from work.

  • Aack08
    Aack08 Member Posts: 16

    My husband just went down to skim the boiler again to see if it would help since it's pushing pretty strong in our upstairs radiators, says the sight glass water is moving right around the half inch mark or so

  • ethicalpaul
    ethicalpaul Member Posts: 8,850

    half inch from the bottom? Or it's moving about 1/2 inch? The former is bad, the latter is good.

    You don't need to skim regularly, in fact it will decrease the life of your boiler.

    Same for flushing, quit doing that.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Aack08
    Aack08 Member Posts: 16
    edited January 7

    Oops, moving about 1/2 inch, we make sure water stays between the min/max lines on our sight-glass so not 1/2 inch from the bottom. And thank you for the advice on how much I'm skimming/flushing, we never used to skim our old boiler, we just thought now with the new one that was supposed to be a regular thing so this is helpful. I thought flushing the built up gunk out of the bottom regularly was supposed to help with properly heating the boiler water so we'll make sure to adjust our practices here.

    ethicalpaul
  • 109A_5
    109A_5 Member Posts: 4,067

    Skimming is only to remove the manufacturing oil (boiler and piping) from the boiler, once that is complete (oils completely removed) you may never have to skim again. Flushing maybe 1 or 2 times a year, once the contamination is minimized from the new boiler install.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    ethicalpaul
  • Aack08
    Aack08 Member Posts: 16

    Thanks, all!

    Good news: we think we've solved the problem. I had assumed that based on the symptoms we were having (louder/more forceful venting upstairs, water/condensation escaping from at least one of the upstairs radiator nut/union elbow (? not sure if I have the proper terminology here), sometimes two of them, I thought we had had an issue related to a vent but it turns out the nut on the radiator that was leaking the most just needed tightening.

    I put all this here in case anyone seeks help like this for their own similar problems in the future. My best advice is try the possible solutions that are free first :) (we learned this the hard way!)


    Thanks again to everyone who jumped in on this thread, I learned a lot about properly skimming/flushing the boiler (or in our case, to not do it!)

  • 109A_5
    109A_5 Member Posts: 4,067

    Water / condensate / steam leaking from any of the piping, valves, radiators and vents is bad and needs repair. Some vents seem to leak a bit of water in some systems, which is not really good.

    Sound like you have it under control.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Aack08
    Aack08 Member Posts: 16

    Thank you, yes I was ready to pull the plug and call someone to come take a look if we hadn't figured it out by last night but now that that nut is tightened and no longer leaking all of the other valve stems are also no longer hissing, all of the vents sound like they're venting normally again, and the heat is seeming to be regulated again in each of the radiators, so we're very pleased :)