I have a Utica star fire steam boiler sfh4150st with a tankless coil for domestic hot water and a hot water loop supporting a new addition. My issue is with the loop bubbling & flashing when the boiler builds a head of steam. I’m thinking of adding new aquastat that can control both high and low however I am not aware of a unit that will shut down the circulator at 200 degrees.

Appreciate the guidance

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    Can you post a few picture of the boiler and controls and the hot water loop connected to the boiler?

    You may need a bypass pipe to mix and control the temp of the hot water loop.

  • 109A_5
    109A_5 Posts: 4,759

    https://heatinghelp.com/systems-help-center/how-to-run-a-hot-water-zone-off-a-steam-boiler/

    https://heatinghelp.com/systems-help-center/how-to-run-a-hot-water-zone-off-a-steam-boiler/

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • I understand the best practice when installing a loop on a steam boiler unfortunately I did not

    IMG_1004.jpeg IMG_1005.jpeg IMG_1007.jpeg

    do the initial install. Please note the ball valve that is tied off the loop, not sure if that was a Utica best practice 25 years ago .. I have attached the requested picture

  • HVACNUT
    HVACNUT Posts: 7,784

    Why are there Tee's above and below the circulator? The piping back to (or from) the boiler off the bull of the Tee looks like its above the water line.

  • 109A_5
    109A_5 Posts: 4,759
    edited December 2025

    What model is this aquastat ? It probably has a high limit. You could connect the circulator for your hot water loop to the aquastat's burner terminals. So if the boiler's water temperature is above the high limit the burner and the circulator will both be off. Probably may not even need the aquastat's burner circuit connected to the burner, since the steam zone and the DHW low limit are both active. If you actually want two different high limit temperatures (burner & circulator) you will need another aquastat.

    However in the midst of winter either way may limit the available time for the hot water loop to actively work. Since you will have to wait for the boiler water to cool down enough to activate the circulator and as soon as the Steam zone calls again the water will go over the high limit. You could try it with minimal changes.

    If it does not work well you may need the proper piping for the proper water blend temperature for the hot water loop.

    image.png

    Example Aquastats;

    https://www.supplyhouse.com/Johnson-Controls-A19DAC-1C-Temperature-Control-100-240F

    https://www.supplyhouse.com/Resideo-L4006A2007-High-or-Low-Limit-Aquastat-100-240-DegreeF-range-5-30-DegreeF-Adj-Differential-L4006A2007

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • The aquastat model is a ra89a 1074. Looking at a line drawing it appears this is just a relay. I understand your approach but need to investigate the correct model

  • 109A_5
    109A_5 Posts: 4,759

    Yeah that is just a relay, I was not sure. So you would need an aquastat or change the piping (which would be better). Waiting for the boiler water to cool down may take too long when you need the heat the most.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • leonz
    leonz Posts: 1,994

    Would a boiler mate be a better option???

  • Thank you all for the input!! I will do a quick aquastat swap that will shutdown the circulator at 190. If this fails due to the length of time it takes to cool from the set point I will take the boiler mate option..I would love to better understand how this system performed without issue for 23 years before this flashing/noise problem started about a year ago slowly getting louder.

  • HVACNUT
    HVACNUT Posts: 7,784

    I can't comprehend the piping with the Tee's above and below the circulator if its a simple baseboard loop. And to me, the one pipe looks like its piped at steam level into the boiler. I never piped a hydronic loop off a steam boiler, but I thought supply and return should be down low on the boiler taps. A wye strainer because its piped down low. And no iron body circulator? For some reason I remember hearing that.

    The current aquastat is a Honeywell L4006A, which is "open on temperature increase". I don't think the aquastat is the issue.

    Follow the thermostat wire from the RA89. Does it go directly to the thermostat?

    Again, I don't understand how it ever worked. You say it did. So the question is, did it work fine before the Magic Nest Common Maker?

    Screenshot_20251214_111003_Samsung Internet.jpg
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    Both pipes should be down low. @DanHolohan also shows a method of piping both HW supply and return to a single tapping by using a DT bushing if two tapping's are not available.

    What is that sensor sticking out of the RA 89A. Looks like a temp stat?

    If I am not mistaken a bronze circ is the best but @ethicalpaul is running his system with an iron circ.

    You need a bypass to blend the water temp so it doesn't flash when the boiler is steaming.

  • ethicalpaul
    ethicalpaul Posts: 9,076
    edited December 2025

    Yes I went with cast iron because it cost 1/3 of a bronze circulator and I keep my boiler water clean and at 9-10 ph so corrosion is reduced. My cast iron one has been going for 3-4 years I think, so far

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • 109A_5
    109A_5 Posts: 4,759

    So the new addition is 23 years old ???

    Something changed ? That is new information presented ?

    The BoilerMate seems like the most expensive method possible. What aquastat are you swapping, I don't see one to swap. You could add an aquastat to the RA89A relay circuit.

    I would not mess with the DHW (aquastat) stuff if it works OK.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Posts: 4,759

    "I would love to better understand how this system performed without issue for 23 years before this flashing/noise problem started about a year ago slowly getting louder."

    Has it been verified that all the air has been purged out of the hot water loop ?

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System