CROSS OVER STEAM MAIN TO DRY RETURN

Options
simon_skove
simon_skove Posts: 85
edited November 2025 in Strictly Steam

Is this where main steam line is vented to the dry return? After nearly 100 years, should the nipple leg be taken off and let come out what may?

img-5902.jpeg

Comments

  • neilc
    neilc Posts: 3,213

    check my reply in your other thread,

    is that a capped nipple at the bottom of the right 90, or does that go thru the wall as a wet return?

    answer in the other thread,

    known to beat dead horses
  • Jamie Hall
    Jamie Hall Posts: 27,975

    Yes… but. It is very likely that at one time at the top of that arrangement there was a crossover trap — a simple radiator trap, but connected starting at the steam main with a short nipple up, then a 90 and a nipple to the INLET of the trap, with the outlet of the trap going straight down through a nipple to the dry return. Air went through the trap, and condensate went down the water seal loop and made its way back to the dry return..

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Steamhead
    Steamhead Posts: 19,007

    That might be a Tudor system. Go here for some illustrations of how that loop seal fits into the system:

    https://www.heatinghelp.com/systems-help-center/european-heating-systems-circa-1907/

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

  • no evidence of that Jamie.