how much does size matter in feet?
PSI and Fahrenheit not working on my furnace gauge. the only needle that moves right now is marked Ft. Now I am trying to find a new gauge but can someone please explain the whole feet thing to me. its been about 30 years since i went to vocation school for hydronics so the details have been forgotten
Comments
-
Feet x .433 = psi
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
OK. I did come across that information but how is that useful info to me?
0 -
What feet is the needle pointing to? Multiply that number of feet by .433 to arrive at pressure.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
it is measuring pressure in feet water column instead of pounds per square inch. it was mainly used to tell when the system was filled up to an open expansion tank.
0 -
Right now it says 20.
0 -
8.6 psig
0 -
An easy rule of thumb that you can always remember (although not perfectly accurate but usually close enough is) 2'=1psi
so your 20' simplified is 10psi
The correct way is .433 x20=8.66 psi
or 2.31feet/psi=20/2.31=8.65psi
0 -
Ok. The strange thing is i do have a open expansion tank that is mounted in the ceiling above the furnace. My guess is about eight feet from the floor to the tank. 8 times .433 = 3.464. The gauge reads 20.
0 -
open tank or a sealed compression tank with no diaphragm but closed? i don't see how an open tank can be below the emitters.
0 -
Expansion tanks - Structure Tech Home Inspections
I have the old school style open tank. Its not a open air style. Open air type must be above the emitters. The link above gives more detail on that.
0 -
we're missing something here because if an open expansion tank is below the emitters the water would run out of the tank.
0 -
No. The drain valve on the tank stays closed. Read this link…………
0 -
it showed all 3 styles of expansion tanks, open tanks, compression tanks, and bladder tanks.
0 -
How are you sure that it's an open tank, @scatgo ? I sounds to me like a regular steel compression tank.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
It is not an open tank it is a bare steel compression tank
0 -
Bingo! My bad. Sorry people total brain fart on my part.
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 134 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements