I’m having issues with one of my downspouts. The downspout goes into the ground and goes across my patio underneath a brick patio — so I can’t actually see what’s going on under there.

I ran water into the downspout for about 5 minutes. It didn’t back up at all, but I also noticed that nothing came out of the exit where the pipe is supposed to discharge.

So now I’m trying to figure out what that means. My only guess is that there’s a break or separation somewhere underground, and the water is leaking into the soil or foundation (I see moisture intrusion in my tile and hardwood in the room next to that downspout, which is what prompted me to go investigating in the first place). I don't think it's clogged because if it were, then I should surely see water backup at the entrance of the downspout

I’m considering running a camera or snake through it, but open to ideas. I'll either have to buy a borescope to do this or call in a power rodding plumber on monday...

Edit: Here's a pic of the relevant area of my property:

the red star on the far right is the discharge location

the yellow arrow points to another downspout where I ran water but was able to observe

the red arrow points to the downspout in question where I ran water but was not able to observe water existing at the discharge (red star).

before anyone asks, I don't think there's any other possible above ground discharge point for this downspout. idk if it's possible for me to be connected to the underground sewer directly though...

Upvote1Downvote1Go to commentsShare

«1

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    I would also suspect a break underground. I think you're on the right track with the borescope

    Big Ed_4
  • mattmia2
    mattmia2 Posts: 18,399

    you could shove a sewer rod or cable in it and see what happens too, if it comes out the other end or if it stops somewhere or if a lot goes somewhere else.

    if you have well draining soil the hose may not be enough water to saturate wherever the leak is and come out the other end. depending on where the leak ism that may or may not be a problem.

    it may connect in to the drain tile around the foundation.

  • hot_rod
    hot_rod Posts: 28,705

    4" pipe? How long of a run. A few years back we strapped a phone in video mode on an RC model and ran it up some irrigation piping. I think it was 10" diameter however.

    Most all sewer cleaners have sewer cameras these days.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,399

    i bought like a $30 night vision security camera from harbor freight that came with like a 50' cable and duct taped it to a sewer rod.

  • Mad Dog_2
    Mad Dog_2 Posts: 8,755

    I could go to a hidden drywell too. Camera'ing it is a good idea. Mad Dog

  • leonz
    leonz Posts: 1,994

    If your basement walls are cinder block they will leak water and really make things messy. Have a sewer cleaner come in and send their camera down the pipe to see what is going on as it will become very, very, very expensive repair project if there is no sump pump as the water will percolate through a cinder block wall.

    SuperTech
  • Intplm.
    Intplm. Posts: 3,162

    The one on the left (red arrow) may be piped to a dry well and not piped to the drain on the right (yellow arrow)

    For your own peace of mind, using a camera is a good idea.

  • If the camera doesn’t help, they also make non toxic tracer dye. Municipal sewer might give you some.

  • orioncyg
    orioncyg Posts: 65
    edited October 2025

    Thanks for all the comments guys.

    I got this borescope https://www.amazon.com/dp/B0BS1CFFH8?ref=ppx_yo2ov_dt_b_fed_asin_title today but haven't had the time to use it yet. Hopefully it'll work.

    I wanted to add a few other details. So when I blasted water into the downspout on the left side (the red arrow one), I had my friend put his ears on the downspout on the right one (the yellow one) and he could hear water flowing. This seems to suggest that the 2 downspouts are connected on the same network (as expected), so I think that might rule out the dry well idea? If they weren't connected on the same network, then I don't think he'd be able to hear anything.

    Another clarification is that part of the house between the red and yellow downspouts is the sunroom. It's an addition built in 1986. It was built on top of a concrete slab so there's no basement underneath. I'm seeing some water intrusion in that room unfortunately that appears to be coming from the ground. That's what sent me on this scooby doo mission in the first place… Below's a pic of water damage in that room and also another angle of the downspout (in this pic, the downspout marked with the red arrow is the one on the right):

  • leonz
    leonz Posts: 1,994
    edited October 2025

    Do you have willow trees near the home? They may have broken through the pipe joints or perforations.

    With the exposed damage you may very well end up removing the bricks to find it if the pavers were not mudded in place.

  • I don't think I have any willow trees, but I have LOTS of trees as you can see in your pic.
    Are willow trees particularly distructive? Just curious why you mentioned willow trees in particular

    I actually took some pavers in the area off and it looks like it's just sitting on earth. I don't see any mortar underneath

  • leonz
    leonz Posts: 1,994

    Willows are the masters of pipe and foundation destruction where water is concerned, I have 12 foot diameter willow trees that have damaged my sand filter septic system and I have to spend $5,000.00 to get rid of them.

    Both Hardwood and softwood trees will seek water and can have surface roots. That is a reason you see a great deal of sidewalk damage as the roots are reaching for the rain gutters.

    When arborists plant hardwood trees instead of slow growing Blue Phitzer Junipers or Yews that can be shaped in raised beds you see a great deal of sidewalk damage.

  • Ah I see, thanks for explaining. I know I have some pine trees in the yard. There are some other trees and idk the name of them.

    Unfortunately, I have a couple trees growing right next to the property (one of them is right by that french door to the left of the pic in the OP. that particular tree is literally within a foot of the foundation)…I was considering getting them removed but some people told me that whatever damage they've caused to the foundation has already been done and removing them might actually make things worse

  • I had my masonary guy come take a look and he said he wouldn't be surprised if the pipe under the patio broke given it's one of those corrugated perforated drainage pipes. He recommended replacing it with PVC if I do find it's defective.

    I'm planning on using my borescope this afternoon to see what's happening.

  • leonz
    leonz Posts: 1,994

    Cut the trees down and burn out the stumps with a big bag of matchlight charcoal if you cannot remove them with a stump grinder or excavator. You will not know if the basement wall is damaged unless you have a wall failure.

  • orioncyg
    orioncyg Posts: 65
    edited October 2025

    Ok some other updates from today:

    1. I used the endoscope/borescope I got from Amazon (this one https://www.amazon.com/dp/B0BS1CFFH8?ref=ppx_yo2ov_dt_b_fed_asin_title&th=1 )

      I couldn't thread through much. Maybe got 3'-4' and couldn't get it to move forward, so not much to learn there
    2. My masonry guy from earlier today suggested blasting water for a good 30min (a few days ago, I only did it for 5min or so) to see if I start seeing water at the discharge, and indeed I did after probably 15-20min. This probably raises more questions than it resolved however… e.g., how in the world does it take that long for the water to reach the discharge?? fwiw when I ran water in to the downspout on the right side (the yellow one), it took less than 30 seconds for me to start seeing water coming out of the discharge.

    the straight line distance between the red and yellow marked down spouts is about 15' and presumably it's a pretty straight section of pipe connecting the 2 downspouts below ground, so I don't know how in the world it takes so much longer for the water in the red downspout to reach that discharge….. i suppose there could be a clog, but then again, it should probably take 5-10min to fill that entire network of pipes with water, not 15-20min. i still thinks there's probably a leak somewhere underground.

    Lyle {pheloa} Carter
  • hot_rod
    hot_rod Posts: 28,705

    A sewer cleaner with a jetter is another option. They have reverse heads that blast water back out as it runs in

    If you have access to a pressure washer get a head like this, and run it in

    IMG_1272.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,399

    you might need to attach some sort of almost ball shaped guide an inch or 2 in diameter just behind the camera on that borescope to let it ride over the corrugations instead of jam and wedge in to them.

  • I actually bought this pressure washer on sale last week: https://www.bestbuy.com/product/greenworks-pro-electric-pressure-washer-up-to-2300-psi-at-1-2-gpm-green/BL6VJXCP3C

    I've never used one before and haven't opened it yet. I was going to return it because I read bad things about green works after buying it. Maybe I'll keep it and try it on the downspout. But how does the water jet navigate turns though?

  • I did think of something along those lines, like drilling a hole in a tennis ball and attaching the camera through it. Is there a specific tool for this purpose? I tried googling what you suggested and didn't see anything that I'd think would work.


    Ultimately, I still have a hard time seeing how this thing is going to manage to turn corners.

    Also, I mispoke in last night's comment. I scoped from the floor drain actually (the one next to the downspout and right in front of the door). I haven't tried any of the 2 labeled downspouts but I imagine I will have the same issue trying to turn corners, especailly when it hits the ground. My scope kept getting stuck. I imagine specialized plumbers will have much more expensive equipment that can navigate corners or a maze-like network with ease?

    In the afternoon/evening, I'm going to try blasting water again and see if it gets to the discharge faster than yesterday. If it does, then I think the network is less blocked than it was yesterday. At this point, I think it's likely there there's a leak AND a (partial) blockage.

  • leonz
    leonz Posts: 1,994

    You obviously have root damage from ingress if you cannot pass the borescope through it.

    Before you go any further you should invest in a good sewer tape from a plumbing supply company and zipo tie the end of the sewer tape behind the camera head and every 5 feet after that and then pass it through the piping if possible as the sewer tape will provide you with the fulcrum/stiffness needed to push the camera cable through it UNLESS and only unless the drain pipe is totally blocked like mine were.

  • The interior of the pipe is perforated. That's the main reason why it's getting stuck unfortunately.

    But I probably do have root damage somewhere and that's probably what's causing a leak.

    Will the method you suggested also work for navigating corners? I have a hard time seeing how this thing is going to be able to turn corners. One of the reasons why I decided to go from the floor drain instead of the downspout is so that I don't have to turn the 90 degree corner one it goes into the ground.

  • leonz
    leonz Posts: 1,994

    It will navigate the corners it just takes patience to push it through by using the sewer tape attached to it as the sewer tape is stiffer than the fiber optic cable. You just have to be sure that you have a zip tie every five feet to assure it stays rigid.

  • hot_rod
    hot_rod Posts: 28,705

    Are you sure there are fittings in the line? Sometimes that corrugated pipe bends enough that ells are not needed

    They have jetters that fit in 1-1/2” pipe and turn around fittings.

    My wife is in the the sewer and drain business, I read these industry magazines to see all the unique tools available

    They have cameras and jetters on tracks, like a micro bulldozer, those probably walk over corrugations. Maybe not around tight bends

    IMG_1275.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Got it, thanks. I will give this a try. I'm not entirely sure how this works but probably because I haven't used sewer tape before, but why do you need zip ties if the sewer tape is going to make the camera cord rigid?

  • Idk if there are fittings. There are junctions though, probably y-shaped, and something must be there to connect them together?

  • orioncyg
    orioncyg Posts: 65
    edited October 2025

    Wait, is this the sewer tape? https://www.homedepot.com/p/RIDGID-3-4-in-x-100-ft-E-2731-Drain-Cleaning-Exposed-Sewer-Rod-Flat-Sewer-Tape-w-4-Sided-Spear-Tip-Carrier-62565/202826662


    I probably don't need much but still 100 ft for almost $200 seems really expensive. I thought they'd be priced like regular tape lol

  • leonz
    leonz Posts: 1,994

    You want to make the cable and camera stiffer to assure it does not try to make a U turn in the pipe.

  • leonz
    leonz Posts: 1,994

    If you have a real mess of roots and do not want to rip the patio up the next option is to invest in enough ROOTX to kill the roots and dissolve them in the pipe by pouring the powder down the floor drain and pouting 10 gallons of water in after the powder to make the root killing foam and do this every year.

  • Thanks. Do you have any suggestions on where to get sewer tape? I'm not sure if I'm looking at the right thing? At $200, I feel like I should probably just get a specialized plumber to come in and do this work for me, but I could invest in stuff for future yearly maintenance.

    If there is root damage, then that means getting of the roots will reveal holes in the pipe which will probably need to be replaced…. my masonry guy told me that I should just go with pvc in the future if we do have to tear up that part of the patio to replace the pipe

  • hot_rod
    hot_rod Posts: 28,705

    A sewer tap, even a cable will not do much for roots, just push through.

    It needs to have a spinning root cutter head on a sewer cable.

    RootX will kill off the roots, but you still need to flush the ball out.

    Personally I would get a pro that can identify, fix and offer mitigation options. It needs to be cleaned first, then send a camera in to pinpoint the breaks or other issues.

    The can put liners in broken or separated lines now. To avoid any disruption of slabs or buildings.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • leonz
    leonz Posts: 1,994

    Any large plumbing supply house will have the sewer tape you need.

    Hiring a sewer cleaner to come and scope the piping in the down spouts and the floor drains will be definitive for you to make a decision as to whether the patio has to be ripped out or you can safely use ROOTX.

    If your down spouts have a clear end discharge point to a drainage ditch all the better as they can be jet rodded or snaked from the open end but if they are laid in a bed of stone for drainage that is another matter as another decision will have to be made.

    The decision being whether a combined sump pit black plastic basin with a sump pump to a ditch is needed to eliminate using the perforated piping entirely but the patio would have to be ripped up to some extent to combine the drain spouts using solid pipe to the solid plastic sump basin with the discharge below the frost line to an open drainage ditch point.

    If you have a foundation drain surrounding your home with a clear line of sight drainage point that drains well you can tie in the down spouts in those two drain pipe sections but you will need a backhoe to do the excavation and make it larger enough to allow the work to be done safely using plywood and lumber for shoring but it would be faster to just rip put the patio pavers and then replace it as the dirt would have to be pulled away from the foundation and dumped away from the hole.

  • mattmia2
    mattmia2 Posts: 18,399

    look on ebay for sewer rod/tape and filter for under $75 or so. like 20 years ago I paid like $50 for a 100' 3/4" general homeowner grade rod but the cost of steel and antitrust activity in retail sales has driven the cost of new name brand way up.

    also if you want to do digging, you can probably find it for much less used on ebay from people that don't know what it is so it won't say "sewer" or "tape" or "rod" in the listing so you will have to be creative.

  • mattmia2
    mattmia2 Posts: 18,399

    real sewer cameras have a bulbous head on them that will turn the somewhat gradual corners that sewers should have.

    image.png
  • orioncyg
    orioncyg Posts: 65
    edited October 2025

    I think I'm going to get a specialized plumber to come in for this as this sounds too complicated for me.

    I already have a specialized plumber coming in to clean my main sewer line (access point is in my main basement). They recommended yearly cleaning. Perhaps I can us rootX for this in the future? (this is a separate topic from the outside downspout network)

    I'm planning on having this same plumber look at the downspouts during the same appointment.

    I took some other pics and videos for clarity:

    discharge exit:

    the yellow labeled downspout on the right side:

    the red labeled downspout on left side:

    another angle of the red labeled downspout and also shows 2 floor drains, 1 in front of door, and another on the right where the hole is:

    close up of drain in front of door:

    another downspout to the left of the red labeled downspout:



    here's a video where I walk from the discharge point across the patio:

  • ok another update. I just blasted water again into that floor drain and it took < 3min for me to see water at the discharge location today. recall yestedray it took like 15-20min -- just a ballpark since I didn't actaully time it. i think this means i cleared some blockage yesterday and/or whatever location is holding the water below ground is still full from yesterday's flushing

  • mattmia2
    mattmia2 Posts: 18,399

    Or the ground is still saturated. There may be no blockage and just water leaking out between the joints or they may have used perforated pipe for part of it.

  • leonz
    leonz Posts: 1,994

    You probably mouse/chipmunk nests in the pipe.

  • leonz
    leonz Posts: 1,994
    edited October 2025

    If you have someone come by to clean the lines with a jet rodder its best that its done from each down spout and the floor drains by the door and the rock and Be Doubly sure to cover the end of the ABS pipe with a length of perforated sewer pipe and an end screen that you can remove later to clear an pine needles and pine cones.

    I lined all my Alaska rain gutters with section of 4 inch gutter brush as my IROBOT gutter cleaning robot no longer works as I am unable to buy replacement batteries for it.

    The Gutter Brush prevents debris from clogging the gutters and anything stuck on the brushes just rots away and is flushed to the down spouts.

    It is a one and done affair and if you rent 2 sections of scaffold with wheels and staging or have 2 by 12 by 10 planks for the floor of the scaffold you can have all the gutter brush sections right there as you use them up. The only other tool you need is a small bolt cutter to cut the woven wire brush to length if you end up with an uneven length of gutter.

    Putting a 10 foot length of PVC perforated septic pipe slid over the abs plastic pipe and using a PVC slotted end screen cap will prevent a lot of problems for you. Investing in the gutter brush will eliminate all your issues with pinecones, pine needles, squirrels and birds in the gutters.

    www.gutterbrush.com

  • hot_rod
    hot_rod Posts: 28,705

    it is not too hard to pull up and reset pavers if they are not cemented to a slab, if it comes to that.