CI Boiler-Return line temperature gage??

Cyclist77
Cyclist77 Member Posts: 197

As our install crawls along I was thinking about the above. I like info!!

Thoughts.

Comments

  • pecmsg
    pecmsg Member Posts: 6,580

    As long as it doesent have to be that accurate………………….

    5240748 - Mr. PEX 5240748 - Strap-On Pipe Thermometer for 3/8"-1.5" Pipe, 0-248F (Pack of 2)

  • Cyclist77
    Cyclist77 Member Posts: 197

    SSince I am still doing piping my idea was to install another "tee" and put a proper one in. Hey in for a penny in for a pound!

  • mattmia2
    mattmia2 Member Posts: 14,599
    edited October 23

    just need a stem type thermometer. set up the fittings so the stem is near/in the flow but clears the other side of the pipe. You can get them with different length stems.

  • hot_rod
    hot_rod Member Posts: 25,918

    PT "Petes" plugs are super handy, easy to use, inexpensive, unbreakable. Use pressure or temperature gauges in them, of whatever quality you want.

    You use the same gauge for all the readings so gauge to gauge accuracy is not an issue.

    Very common on balance valves and any engineered system. Balancing contractors and engineers like them for adjusting, checking and troubleshooting systems.

    Shove this needle adapter in like inflating a basketball. 1/4" fip for a gauge

    Screenshot 2025-10-23 at 1.02.16 PM.png

    Screenshot 2025-10-23 at 12.55.07 PM.png Screenshot 2025-10-23 at 12.54.11 PM.png Screenshot 2025-10-23 at 12.57.10 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream