Is this at risk of freezing?

Options
trivetman
trivetman Member Posts: 262
edited October 2025 in Plumbing

I've been running a recirculating hot water loop using one of those crossover valves which uses the cold line for the return. I am in the process of rebuilding a third floor closet and realize I've got access to a space next to the chimney where I can probably fish a line of pex through to the basement to be a dedicated return line.

Only hesitation is I don't know how cold this space might get. it's a hot water recirculating line, but there's always power outages and other edge cases to consider. My gut tells me it's far enough from the exterior wall not to be a freeze risk (as long as the house heat is working!), but I'm not 100% sure. I'm also realizing we have some existing water lines running from basement to second floor in essentially the same spot two floors down and which have never been a problem, but I didn't put those in so never questioned them. House is a 1900 build without any insulation against the stone exterior.

Here's a top view cross-section of the space Dimensions are approximate. Would you put a water line here for a client? Region is Philadelphia area.

WaterLIneQuestion.jpg

Comments

  • mattmia2
    mattmia2 Member Posts: 17,565
    edited October 2025

    unless there is a significant draft in from the outside(which is certainly a possibility in that chase) that is far enough in to not freeze unless you've lost heat for probably a day or 2 or more

    trivetmanCanucker
  • hot_rod
    hot_rod Member Posts: 27,904

    you will want to insulate the line to limit the heatloss if that is a cold space. Running recirc lines in cold spaces will cost more DHW fuel.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 17,565

    it essentially makes all of the hot water lines in the loop part of the tank

  • Intplm.
    Intplm. Member Posts: 3,088

    You should be fine there. Just insulate the area.

    Grallert
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,541

    I agree with @hot_rod & @mattmia2 sbout adding some pipe insulation. I also want to add

    Screenshot 2025-10-20 at 1.52.49 PM.png

    For the Philadelphia Fans.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    trivetman
  • JAdams
    JAdams Member Posts: 39
    edited October 2025

    Use PEX tubing for the recirc line and insulate it well past the possible freezing point. If you wanted to take added protection, you could also run the insulated recirc pipe through a conduit, but long enough so the cold air can't penetrate through the ends. I live in an area where temps get well below zero and there is always a breeze. Also, remember that Hot water will freeze before cold water, so protecting it from a cool breeze should be taken.

  • 4Johnpipe
    4Johnpipe Member Posts: 491

    I would recommend insulating a hot water return line regardless of location. That said can you access the area above that closet or chase so you can seal off any potential down draft? That would be helpful…

    LANGAN'S PLUMBING & HEATING LLC
    Considerate People, Considerate Service, Consider It Done!
    732-751-1560
    email: langansph@yahoo.com
    www.langansplumbing.com
  • Jack Getkin
    Jack Getkin Member Posts: 12

    I agree the line should be insulated. You should also know factory insulated PEX tubing is available for purchase and use. It is more costly than uninsulated PEX but the insulation will be on the tube as you install it. It's a one and done operation.

  • Alan Welch
    Alan Welch Member Posts: 271

    Isolation valves on both ends just in case.

  • trivetman
    trivetman Member Posts: 262

    Thanks guys. I had to give up on this one. Wasn’t nearly as easy to fish a line through two floors as I had thought it would be.

    For real…hot freezing before cold?? I thought this was just some false myth I had heard back in my college days. Hows that work?

  • gunn308
    gunn308 Member Posts: 18

    Your Zamboni will not make ice with cold water it needs hot water or you're gonna be swimming

  • LMacNevin
    LMacNevin Member Posts: 25

    A Zamboni uses hot water to quickly melt all the snow and ridges on the ice and to leave a smooth surface. If they used cold water, a clumpy mess would be left behind on the rink and in the augers of the Zam itself.

    mattmia2
  • Forever_Student
    Forever_Student Member Posts: 12

    "Hot Water freezes before cold" refers to the "Mpemba effect", and it's not proven science. There have been a lot of experiments and research around it, and it is only partially reproducible. Sometimes experimentation disproves this theory, so it's not a known quantity. In theory, there are a few requirements where it is true, but some of them don't apply to this situation, so I wouldn't say it's true in this instance.

    One reason it may happen is that hot water evaporates more readily than cold, and evaporation causes rapid cooling, so you get a huge cooling boost from a lot of evaporation happening really quickly. But the hot water still has to travel through a cooler temperature before freezing, so it's questionable whether this really causes it to freeze faster. However, if you throw a bucket of hot water out into very cold air, you maximize its surface area, which allows for more evaporation, condensation, and crystallization, so you can make snow and ice faster with hot water here than cold water. But you won't really have evaporation inside your pex, so this won't really affect it.

    Another theory is that hot water creates higher temperature differentials and temperature gradients between hot and cold, which allows more internal convection, which accelerates heat transfer. This actually could apply to your pipe.

    Last one I'll mention is that heating water to or near its boiling point decreases gas solubility, so you lose dissolved gases from the water. Those dissolved gases slightly lower the freezing point, so your heated water might freeze at 32F, where your never-heated water might freeze at 31F or 31.5F. However, this mostly applies when comparing water that has been heated to water that has not been heated. If you're comparing water that has been heated to other water that has been heated, this shouldn't impact results.

    There are a couple more theoretical drivers, but that's enough nerdy science rambling for today. The overall summary is that the statement "Hot water freezes faster than cold" should be taken as an unproven theory, not a law or a fact. It might be true, but it's not indisputably true.

  • trivetman
    trivetman Member Posts: 262

    can of worms……opened!!

    mattmia2
  • mattmia2
    mattmia2 Member Posts: 17,565

    please use the thread from a couple years ago with like 5 pages to further discuss…