Very Old Two Pipe Radiator

Long Beach Ed
Long Beach Ed Member Posts: 1,806
edited October 19 in Strictly Steam

Anyone know how the base of this radiator is internally arranged and how the steam circulates through it? We'd like to use this as a single pipe radiator, with the return plugged. That's an 1-1/4" supply and 1" return.

It may be a pre-1890 Bundy; where later ones just had a single internal baffle.

The heating load is minimal, so condensate load should be less than its design. If it doesn't work out, we'd add a return with a condensate loop…

One section was tapped in later years for a vent. Check out the original vent standpipe on the end. Thanks for all your help!

a1.jpg a1.jpg

Comments

  • Steamhead
    Steamhead Member Posts: 18,050

    Is there a name on the base? If it's a Bundy, it would be "A.A. Griffing".

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Mad Dog_2
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,806
    edited October 19

    Nope. No "AA Griffing" or anything anywhere.

  • Jamie Hall
    Jamie Hall Member Posts: 26,515

    No particular reason why that won't work, at least after a fashion, as a single pipe radiator. However, it will probably work better — indeed remarkably well! — if you pipe it as though it were a two pipe radiator. Inlet on one side and a return on the other. With a twist. Is there any way at your proposed location that you can create a water seal on the "outlet" side? If so, and you put an air vent on that outlet pipe, it will function exactly as a two pipe would…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Steamhead
    Steamhead Member Posts: 18,050
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    HeatingHelp.com
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,336

    Ed...I have two I installed in my house. The long one in the parlor is piped, Two-pipe. The smaller of the two is in the kitchen and works great on one-pipe. Mad Dog

  • Long Beach Ed
    Long Beach Ed Member Posts: 1,806

    Thank you Gentlemen.