Weil McLain 1107-1 baseboard hot water wont shut off

Options

Integrated domestic hot water and baseboard hot water. Stopped responding to thermostat. Will only do constant full on baseboard hot water heat, will not cycle off. Replaced thermostat. Checked thermostat connection to furnace. Is next step replacing control board?

Comments

  • 109A_5
    109A_5 Posts: 4,761

    Were both the domestic hot water and the baseboard thermostat / aquastat wires disconnected at the boiler ? Does the control board seem like it is actually receiving a call for heat ? What is the actual boiler model ?

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • mattmia2
    mattmia2 Posts: 18,399

    could be a stuck end switch or zone valve too if it is using zone valves.

    109A_5
  • HVACNUT
    HVACNUT Posts: 7,784

    If you have the CGt, the 3 way valve could be bypassing. What model and Series boiler?

  • It is the Cgt-5pin. Series 2. Looks like it's from 2014.

  • It's only one zone, for one floor, for baseboard hot water, but it also supplies domestic hot water. It is supplying hot water just fine. The problem is that the heat won't turn off in response to the thermostat. It is running heat nonstop.

    I read on here someone else with the exact same problem on what sounded like the same unit.

  • Jamie Hall
    Jamie Hall Posts: 27,975

    Somewhere something is telling that boiler to run. You will need to work through the controls to find what controls what… can't tell without being there or having a pretty complete wiring diagram to work from.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • So you'd say I have to do that, before jumping to replacing the control board.

  • Big Ed_4
    Big Ed_4 Posts: 3,585

    Post some photos of the boiler and piping .. You may have a dirty flow valve or bad check …

    There was an error rendering this rich post.

  • 109A_5
    109A_5 Posts: 4,761

    " So you'd say I have to do that, before jumping to replacing the control board. "

    If you want to replace the control board for $$$, you certainly can. However you run the risk of spending $$$ and replacing the control board may not repair the issue. It is your money and your choice, your gamble.

    Typically a Service Tech would want to disconnect the control wiring from the boiler (at the boiler) to prove it is actually the control board that is causing the issue. Usually isolating the control wiring from the boiler is quick and simple.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Posts: 4,761

    Looking at the wiring diagram, before I condemned the Control Module, if you have a multi-meter I'd verify there is 24 VAC between the two pins circled in Red below. 24 VAC equals no call for heat. The other way (better than just disconnecting the thermostat wires at the boiler) is unplugging the relay and the connector to the 3-way valve (Orange boxes). The thing is if the relay (pins 4 to 6) or the 3-way valve (pins 1 to 4) has a defect staying closed there could be an erroneous call for heat.

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Weil mclain says replace the 3 way valve and the control panel, that they discontinued this model because of these very problems.

  • 109A_5
    109A_5 Posts: 4,761

    From the other end of a phone line that is an easy recommendation, might as well recommend replacing the whole boiler with one that does not have those issues.

    Replacing the 3 way valve and the control panel may resolve 99% of the issues, however other things could be at fault, like the relay and the wiring.

    But when the boiler is out of warranty and at the customers expense what do they care ?

    Also their experience may have proven that Plumbers and HVAC Technicians are not strong electrical control troubleshooters, as far as issues internal to the boiler and the 'Parts Cannon' or 'Shotgun' repair strategy more often than not works to get the boiler working again.

    In my opinion if the control panel is in fact defective the parts to repair it may be under $10 or a bad solder joint just needs repair. If you replace everything it could be you learn nothing unless an analysis is done later.

    I like finding the exact issue and just replacing / repairing the defective issue.

    You could make the argument that replacing everything freshens things up, however it is at the customer's expense.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Plumber went with a new 3 way valve (says old one was stuck), and a new board (which fortunately he had not opened), and found that the water pressure was low. He took the automatic water feeder out, took it apart to clean it out, put it back in, reset the water pressure, and it started working again. He did not replace the board.

  • Plumber says circulator pump is running constantly now. Already replaced 3 way valve, relief valve, expansion tank, and water feeder recently. Worked well for a few weeks. Now again, heat running constantly, cannot turn it off, and they still have hot water. Plumber says 3 way pump switched appropriately when we ran hot water. He unplugs it from board, pump stops. He thinks it is the board.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    You probably could buy a boiler with the money you wasted.

    Look, you need someone who can TROUBLESHOOT with test equipment.

    You're going at this like a car that is overheating do you replace the tires?

    Obviously, your plumber doesn't have a clue about electrical.

    Most HVAC service calls are 80% electrical related. You can buy a meter and do some testing yourself. If you can't you need a competent technician who can.

  • 109A_5
    109A_5 Posts: 4,761

    That seems like a new symptom, I did not find that symptom mentioned earlier in the thread. You are referring to the circulator that the boiler's control board has control over. How many circulator are in the system ?

    What LEDs are presently on ?

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System