Weil McLain 1107-1 baseboard hot water wont shut off
Integrated domestic hot water and baseboard hot water. Stopped responding to thermostat. Will only do constant full on baseboard hot water heat, will not cycle off. Replaced thermostat. Checked thermostat connection to furnace. Is next step replacing control board?
Comments
-
Were both the domestic hot water and the baseboard thermostat / aquastat wires disconnected at the boiler ? Does the control board seem like it is actually receiving a call for heat ? What is the actual boiler model ?
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
-
If you have the CGt, the 3 way valve could be bypassing. What model and Series boiler?
0 -
It is the Cgt-5pin. Series 2. Looks like it's from 2014.
0 -
It's only one zone, for one floor, for baseboard hot water, but it also supplies domestic hot water. It is supplying hot water just fine. The problem is that the heat won't turn off in response to the thermostat. It is running heat nonstop.
I read on here someone else with the exact same problem on what sounded like the same unit.
0 -
Somewhere something is telling that boiler to run. You will need to work through the controls to find what controls what… can't tell without being there or having a pretty complete wiring diagram to work from.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
So you'd say I have to do that, before jumping to replacing the control board.
0 -
Post some photos of the boiler and piping .. You may have a dirty flow valve or bad check …
There was an error rendering this rich post.
0 -
" So you'd say I have to do that, before jumping to replacing the control board. "
If you want to replace the control board for $$$, you certainly can. However you run the risk of spending $$$ and replacing the control board may not repair the issue. It is your money and your choice, your gamble.
Typically a Service Tech would want to disconnect the control wiring from the boiler (at the boiler) to prove it is actually the control board that is causing the issue. Usually isolating the control wiring from the boiler is quick and simple.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Looking at the wiring diagram, before I condemned the Control Module, if you have a multi-meter I'd verify there is 24 VAC between the two pins circled in Red below. 24 VAC equals no call for heat. The other way (better than just disconnecting the thermostat wires at the boiler) is unplugging the relay and the connector to the 3-way valve (Orange boxes). The thing is if the relay (pins 4 to 6) or the 3-way valve (pins 1 to 4) has a defect staying closed there could be an erroneous call for heat.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Weil mclain says replace the 3 way valve and the control panel, that they discontinued this model because of these very problems.
0 -
From the other end of a phone line that is an easy recommendation, might as well recommend replacing the whole boiler with one that does not have those issues.
Replacing the 3 way valve and the control panel may resolve 99% of the issues, however other things could be at fault, like the relay and the wiring.
But when the boiler is out of warranty and at the customers expense what do they care ?
Also their experience may have proven that Plumbers and HVAC Technicians are not strong electrical control troubleshooters, as far as issues internal to the boiler and the 'Parts Cannon' or 'Shotgun' repair strategy more often than not works to get the boiler working again.
In my opinion if the control panel is in fact defective the parts to repair it may be under $10 or a bad solder joint just needs repair. If you replace everything it could be you learn nothing unless an analysis is done later.
I like finding the exact issue and just replacing / repairing the defective issue.
You could make the argument that replacing everything freshens things up, however it is at the customer's expense.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Plumber went with a new 3 way valve (says old one was stuck), and a new board (which fortunately he had not opened), and found that the water pressure was low. He took the automatic water feeder out, took it apart to clean it out, put it back in, reset the water pressure, and it started working again. He did not replace the board.
0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 76 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements