aksvks
aksvks Member Posts: 4
edited 7:05PM in Oil Heating

Hi, New home owner , oil boiler, baseboard water heating + hot water tank, 2500sqft, Boston., Looking to replace our leaking 40 year old burnham v7, here are some of the options got from installers. Please help to decide.

Weil McLain gold S4

Burnham 206en-to

+3K

Williamson OWB-4

purepro P5

Buderus G115

+8K

Energy Kinetics System 2000 Model EK-1

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 26,410

    Is this steam or hot water? And — most important — have you checked to ensure that the possible replacement boiler is the correct size for your house and your system? It's a simple check — for steam, what is the power capacity (EDR) of the installed radiation; for a house a simple heat loss calculation.

    Don't assume that the existing boiler is the right size…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • aksvks
    aksvks Member Posts: 4

    hot water, going to ask the installer to check a heat loss calc. thanks

  • Robertw
    Robertw Member Posts: 63

    If i might add the Ek-1 frontier can be fired at 4 different firing rates. Great option if you're planning on renovating or adding square footage. Also, the savings in the long run can't be beat. Especially if your making hot water with our storage tank and plate heat exchanger.

    If you want to message me i can possibly help with the sizing.

    My 2 cents.

    Robert W.

    Energy Kinetics

  • HVACNUT
    HVACNUT Member Posts: 7,021

    EK-1 Frontier no question. That's not a Buderus model. G115 or G215 (you don't need a G215).

  • hot_rod
    hot_rod Member Posts: 25,721

    gas or oil?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream