original circulator sized too small?

2»

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,038
    edited September 18

    That point on the curve. 9.3 Ft head at 14 GPM (based on the max flow thru 1-1/4" pipe copper) still falls just above the 0010 pump curve and below the 0012 pump curve, so I would still use the 0012 pump. If you happen to already own a 0010 then that is a better choice than a 007.

    Screenshot 2025-09-16 at 10.27.58 PM.png

    You already have an oversized boiler for the piping that it is connected to. And you have indicated that you have about 121 Feet of baseboard for the one floor, and perhaps about the same for the second floor. That would indicate you need about 13 GPM for about 133,000 BTUh. That would actually fall directly on the 0010 performance curve. You might be good with that pump and it is less expensive than the 0012 if you need to purchase the correct pump.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • mattmia2
    mattmia2 Member Posts: 14,136

    the 0010 would do it(just a little under but close enough). the 007 should give you 5 gpm which isn't enough to adequately heat the house but should be making part way in to some of the loops pretty quickly.

  • wyatts
    wyatts Member Posts: 16

    that sounds about right. taco 0010 it is. i was also wondering about the expansion tank, if it was undersized. ill have to check the pressure when it gets up to temp. it only has a amtrol model 30 on it. if it was undersized you would think something might of broke at this point possibly

  • wyatts
    wyatts Member Posts: 16

    you could also put two 007 on each zone possibly correct? instead of zone valves

  • mattmia2
    mattmia2 Member Posts: 14,136

    no, the 007 doesn't have enough head for either zone.

    i would get an ecm pump that covers that point on the curve. they can be set to multiple curves and use less power.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,038

    @mattmia2 is correct, If you have a loop that requires 9.3 ft of head and needs less than 5 GPM then a taco 007 would work. I don't believe your longest zone is that small (only 5000 BTUs of baseboard). You need at least one of the pumps to be a 0010. If the other zone is shorter, it will have less resistance to flow, so perhaps a 007 might work on that zone. But you don't need to redesign the system just to save $$ on a circulator pump. Get the 0010 and see how that works. I believe you will be pleased.  

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,533
    edited September 19

    The .04 only works if the pipe size is reasonable for the flow. 17 gpm with 1 1/4 is a little undersized.

    17 gpm on 1 1/4" is 6.29 feet of head/100feet of pipe

    at 154 feet (1.54 x 6.29)=9.435' x 1.5 for fittings=13.6 feet total

    Looks like the 0012 that @EdTheHeaterMan picked is right.

  • wyatts
    wyatts Member Posts: 16
  • wyatts
    wyatts Member Posts: 16

    yeah i have two 007s so i was just wondering. would be pretty quick to sweat em in

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,533

    Every 10,000 btu needs 1 gpm of flow. 168,000/10,000-16.8gpm

  • wyatts
    wyatts Member Posts: 16

    what do you think about the Spiro vents. I was wondering about installing one. i should probably just replace all the corroded old style air vents around the house though

  • mattmia2
    mattmia2 Member Posts: 14,136

    automatic vents will eventually leak, if you can purge to get that part flowing i'd replace them with manual vents. i like the caleffi discal better than the spirovent but both will work if you put them where the temp is the highest and pressure lowest.

    the auto vents are fine by the boiler where you will notice them leaking, out in the system I would try to avoid as much as possible.

  • wyatts
    wyatts Member Posts: 16

    im not sure how i would pipe one in since my circulator is on the return so if you put one on the supply it is hot and it is highest pressure. and my expansion tank isnt under a air scoop. it has its on leg off top of boiler.

    IMG_2056.jpeg
  • hot_rod
    hot_rod Member Posts: 25,650

    If you are at 5000' elevation or higher you derate boiler output also.

    So in Denver that boiler output is more like 157,000 so 15 gpm would be adequate.

    Yes, and air purger, the microbubble type is what you should have for an air, and noise free efficient hydronic system

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • 109A_5
    109A_5 Member Posts: 2,757

    I'd go with the 0012, unless the cost is a show stopper. Why deal with maybe marginal ? So far not seeing a 0012 type with ECM features, just 3 speeds.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • hot_rod
    hot_rod Member Posts: 25,650

    If a repipe is in your future, move the circ to the supply side, just after a Discal with the expansion tank connected.

    Screenshot 2025-09-18 at 7.59.05 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,038

    I would surely go with the Caleffi Discal or SpiroVent to make all those micro bubbles crash into the element inside the vent that causes them to make larger (more buoyant) so the can easily float to the top of the air vent chamber. Then the vent will open to let out that air. Noe your current boiler feed and expansion tank piping needs to be redesigned, you may as well just get new Extrol 60 for your system and make it look like this.

    Screenshot 2025-09-19 at 11.07.14 AM.png

    The new feed line will enter at the same location as the expansion tank so not to have the pressure of the tank and the auto feed working against each other. (see new copper feed). You can just place a set of circulator flanges connected to a 5-1/2" long x 1-1/4" pipe nipple to replace the existing circulator. No repiping needed. Just a set of flanges and a a couple of full face flange gaskets.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    mattmia2
  • mattmia2
    mattmia2 Member Posts: 14,136

    where is the expansion tank and zone valves now? might want to keep the isolation valve for purging and to disconnect things at the boiler without draining the system