We have a customer with an early 2000s boiler. It’s been going in and out, every time we go the system is running. Or they cancel the call. They want a price for a new system.

I get there yesterday, they asked me about replacement: why it’s necessary. I say it’s not necessary, if the boiler is not leaking, we can keep on repairing it

I walk up to the boiler, no hot water in the indirect. No codes on the integrated control board. I jump the TT at the boiler, it fires.

I trace it back to a loose connection at the Taco; the wire itself is dropping in and out. I thought I’ll be the hero and get them going, even though my role was sales/estimating at that moment.

The low-voltage line gets away from me, drops right into the line voltage term—-Bang

The transformer hisses like I’ve never seen, like there was a serpent in there. I replaced the transformer, flip the tripped breaker back on, and another pop. The integrated control board gets hammered.

Great, I’m trying to help these people and I just throttled myself into the ground.

Thankfully, I’ve got an old friend/customer that knows circuitry very well. I call him up at quarter after five, he says come on by. He looks at it and says it’s gonna take me a couple hours, “I’ll call you when it’s done”

I go over there around 8 o’clock. Pick up the board. He says “I can’t guarantee it’s gonna work but give it a try”

Today I pop it in, it lights up like a champ.

Does anybody else have any “good deeds getting punished” stories?

I can’t believe I’ve been doing it this long and I’ve never gotten in trouble with a low-voltage to line voltage short. Lesson learned.

IMG_9909.jpeg IMG_9907.jpeg
Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com
Mad Dog_2

Comments

  • Mad Dog_2
    Mad Dog_2 Posts: 8,755

    I've got one too many "no good deed goes unpunished" stories. Guys like us always do the right thing and eat the cost. What I have learned to do in these situations is not touch ANYTHING until you are 100% clear with them, maybe in writing, that you are doing them a favor, but not responsible for any parts or labor incurred.

    Don't beat yourself up Gary, we work in cramped conditions and its very easy to cause a dead short. Burned out plenty of transformer learning...Mad Dog

    GrallertGW
  • GW
    GW Posts: 5,259

    Ed yes, I’m moving faster than I should at times.

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    EdTheHeaterMan
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    I rather like working on things live myself.

    GW109A_5EdTheHeaterManPC7060
  • GW
    GW Posts: 5,259

    yes, it was a fluke,

    I can’t quite tell if Ed was being sarcastic. He went on and on about how to shut a switch off. Fantastic advice though

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,948
    edited September 2025

    Sometimes a picture is worth a thousand words and I often try to use the most basic terms and use the original artwork to illustrate my point. Being that Gary has at times asked some questions herein, that require a detailed explanation, like how to design a bathroom, I didn't want to leave any room for doubt as to my instructions.

    Yes I was being sarcastic 🤣.

    I have often worked on live wires. it is so much faster that looking for the circuit breaker.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • 109A_5
    109A_5 Posts: 4,759

    Troubleshooting live circuits you will learn more faster, but there are risks.

    The "no good deed goes unpunished" is minimized by shutting the power off as Ed states. It is a good practice adhere to.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • mattmia2
    mattmia2 Posts: 18,399

    There's the trying to guess if things are going to fall apart in your hand aspect to working on live things. Sometimes you guess wrong. Some of those people are the 3 fingered electrician that set a number of surge suppressors on fire when they disconnected the neutral of a multiwire circuit.

  • Some people have no sense of adventure! And many of my customers were shocked when they found out I was not a licensed electrician.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    @GW

    he's just messn with ya

    EdTheHeaterMan
  • JUGHNE
    JUGHNE Posts: 11,653

    Are there many of the WM Gold GV boilers still around?

    I have a complete one sitting in my basement, changed just to go Mod Con. Power disconnect switch included……☺️

    Parts for sale…….CI will probably go to scrap.

  • GW
    GW Posts: 5,259

    we see the Golds here and there. Still tons of GB142s too

    Gary Wilson