I have never seen a DHW recirc system with the expansion tank on the suction side of the pump. Even in the Caleffi Tankmixer documentation they have it on the pump outlet.

Why, in this scenario do we not want to pump away? Even if the pump has a check valve the expansion tank is not isolated from the system because water is unrestricted from the other direction, right?

Comments

  • GGross
    GGross Posts: 2,104

    I'm sure many better educated than me can go into better detail. With a recirc on an open DHW system, we don't have a fill valve located at the expansion tank, and since the system is open we aren't going to be eliminating entrained air from the system. For my knowledge these are two primary advantages to establishing a proper PONPC in a closed loop hydronic system, purging air and maintaining proper fill pressure when a fill valve is present. neither of these are relevant really in an open DHW piping system

    On your tank mixer documents you would see your choices for tank location are either on the outlet hot port, or the inlet cold port, both on the tank side of the piping, you can't locate it past the mix valve because the valve can become isolated from the burner, and you have to locate the recirc in the location shown. Of the two available locations to pipe the expansion tank, the cold side is preferred because the tank should have a longer life being subjected to lower water temperatures, and prevents the tank lining from being damaged in the event the water heater overtemps on the hot side.

    I'd love for someone maybe a bit better educated on the subject than me to chime in, this is all from my understanding of the PONPC I typically don't dabble in the DHW side of things and usually stick to closed loop so there may be things I don't fully understand at work here also.

    Mad Dog_2
  • ChrisJ
    ChrisJ Posts: 17,763

    I suspect the chances of a pump pulling air in are mighty slim when the system is somewhere between 40-90 PSIG. The inlet of the pump is never going below atmosphere.

    And even if it does, no one cares with domestic hot water.

    That's my thoughts, but, I have very little knowledge on hot water systems.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    SnowmeltMad Dog_2
  • Jamie Hall
    Jamie Hall Posts: 27,975

    Probably the simplest reason is that as many have implied there is very little if any chance of the pump cavitating, never mind pulling air. It would be a very rare domestic water setup which had a static pressure less than around 20 psig; 30 psig would be more normal. With that much static pressure you would need 60 feet of head loss or more between the expansion tank and the pump inlet to get in trouble. Not going to happen…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    MatthewPKMad Dog_2
  • hot_rod
    hot_rod Posts: 28,708

    Pumping away allows the pump pressure differential to be "seen" or added to the circuit. Really no need for that in a recirc loop. The recirc pump just needs to move enough gpm to over-come the temperature loss in the loop

    Rare but possible on a very low static pressure and very high temperature that the pump would lower pressure below vapor pressure allowing it to flash. Typical recirc pumps are not adding but a few psi ∆P

    Maybe massive amounts of air/ gasses in the water could cavitate a pump, but it takes a lot to cavitate those small output recirc pumps. Even choking down a balance valve on the discharge side rarely cavitates them.

    Screenshot 2025-08-29 at 2.21.46 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mad Dog_2
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,952

    It's an open system. The PONPC concept does not apply. the pressure is always changing as you open and close faucets. The reason for the ThermXTrol is to allow for expansion of the cold water in the water heater to have a place to go when it heats up after all the faucets are closed. in the past that expanded water would just back up into the cold side and force the pressure back into the city water main. Today, however, many systems have a check valve or backflow preventer at the water meter location so that expanded water can't get back into the city water main. With no place to go, it expands and builds up pressure until the relief valve releases the pressure and who wants all that hot water spilling all over the laundry room floor?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • hot_rod
    hot_rod Posts: 28,708

    the dhw recirc systems morph between an open and closed system

    Probably more accurately described as a potable water hydronic heating loop

    Especially in resort and second homes where nobody lives or opens a hot water tap

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream