Condensation line is cleared but water stops 3 inches in

Options
alexr94
alexr94 Member Posts: 12

my split unit started leaking a few days ago. I took it apart cleaned the drain pan, used a shop vac on the outside drain line and the one inside multiple times, ran a thick cable thru 3 feet of the condensation drain hose and flushed 15 times with hot soapy water and vinegar. Only to pour water into the condensation drain hose attached to the unit inside. And the water just sits there. Even if I hold the hose up it doesn’t drain down. Is there a mechanism in the beginning of the hose that can allow a cable to pass thru but not water? And does the msz-gl09na have a condensation pump? Please help.

Comments

  • neilc
    neilc Member Posts: 3,201

    post a picture of the trap, or drain coming from the pan,

    known to beat dead horses
  • alexr94
    alexr94 Member Posts: 12
    IMG_0658.jpeg

    I removed the drain pan. This is the hose that goes into the back of it. I poured water in it and hold the hose up and it just sits there. Doesn’t drain at all.

  • alexr94
    alexr94 Member Posts: 12

    I did test it with it running and off. No difference.

  • 109A_5
    109A_5 Member Posts: 4,346

    " ran a thick cable thru 3 feet of the condensation drain hose and flushed 15 times with hot soapy water and vinegar. "

    Often spiders and critters get in from the outside and the debris in the drain pan washes down.

    Was the thick cable you used longer than the drain hose ?

    When you flushed it with the hot soapy water and vinegar, did it drain then ?

    I would say you need a thick cable (or the like) that is longer than the whole drain hose and work out the blockage from both ends. Spinning the 'Snake' may also help dislodge the blockage so it can be flushed out.

    Once you get it running flush it good.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • HVACNUT
    HVACNUT Member Posts: 7,613

    When you lift the hose, its kinking? Have you tried putting it back together and testing? Pour water on the coil.

  • alexr94
    alexr94 Member Posts: 12

    no the cable did not make it all the way thru. It was an instrument cable. lol all I had. And no, water only came out when I used the air compressor from the inside. But without that, nothing. And yes I assumed I might be kinking the hose so I did put everything back together and let it run. Made no difference. Started leaking after an hour of running. If it’s a clog I’m assuming it’s closer to inside than out due to how fast it takes to fill up.

  • HVACNUT
    HVACNUT Member Posts: 7,613

    I had one yesterday where the vinyl hose used to extend the drain came disconnected from the drain hose. The vinyl hose was clear, but the factory hose was clogged. Some stable genius thought a hose clamp on soft tubing is a good idea.

  • alexr94
    alexr94 Member Posts: 12

    what’s the difference between the two hoses? Does that sound like what I’m expecting? Like which is the one sticking out that connects to the drain pan? Also water and air go thru the hose when I use the air gun inside and vacuum outside. But not without.

  • alexr94
    alexr94 Member Posts: 12

    is there a mechanism in the unit that acts as a vacuum or something to pull water from the drain pan into the hose? Or is it based on gravity?

  • 109A_5
    109A_5 Member Posts: 4,346

    The ones I have worked on it is just gravity drain and you have to get the junk out of the hose, which may take some agitation of the junk to dislodge it. Just poking through the junk (if that even happened), it may re-seal. Also if you don't completely drain the hose it will fill up quickly even if the blockage is close to the far (exit) end.

    Did you poke the "instrument cable" from the outside too. Curious is the "instrument cable" a thin guitar string or a low E string from a Bass or the cable going to an Amp ?

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • alexr94
    alexr94 Member Posts: 12

    ok got it. I’m thinking the clog is closer to the indoor unit itself because when I pour water into the condensation hose it just sits there. And I love that you know that! lol. It’s the cable that goes into the amp

  • alexr94
    alexr94 Member Posts: 12

    and yes I did from both sides. The out side drain is pretty close to the indoor unit itself. The cable was maybe 2 feet. I definitely didn’t get all the way through though.

  • mattmia2
    mattmia2 Member Posts: 17,906

    Some bleach in the hose might help break down the mold, just be careful not to spray bleach on yourself.

  • alexr94
    alexr94 Member Posts: 12

    nothing will go in the condensation hose. It just sits there hold the hose up all different ways and it still doesn’t drain

  • 109A_5
    109A_5 Member Posts: 4,346

    You need something like 1/4" wire rope or the outer sheathing of a bicycle hand brake cable that is longer than the drain hose for a sanity check that it will pass all the way through. Can the drain hose be easily removed from the building to force water through it with a garden hose ?

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • mattmia2
    mattmia2 Member Posts: 17,906

    or put a barb fitting and valve of some sort on a garden hose and flush it through with the hose.

  • neilc
    neilc Member Posts: 3,201

    did we try the wet vac on the hose?

    use a rag to "seal" between the vac hose and the con hose,

    known to beat dead horses
  • alexr94
    alexr94 Member Posts: 12

    I did that multiple times on both ends.

  • HVACNUT
    HVACNUT Member Posts: 7,613

    The factory drain hose jist stubs outside. They're sometimes extended with field supplied drain hose. If there is and extension, have you checked to see if the connection came apart?

  • neilc
    neilc Member Posts: 3,201

    how bout a more distant picture, the unit with wall surrounding it,

    It's level, correct?

    known to beat dead horses
  • alexr94
    alexr94 Member Posts: 12

    I gave in a just called Bolton. Thanks for everyone’s help and suggestions!!

  • pedmec
    pedmec Member Posts: 1,478

    Make sure the unit is pitching the correct way

  • mattmia2
    mattmia2 Member Posts: 17,906

    or actually level in both directions. if there is a built in trap too much pitch could cause it to get airbound depending on how it is arranged

  • pecmsg
    pecmsg Member Posts: 7,442

    minis do not get traps.

  • alexr94
    alexr94 Member Posts: 12

    so in case anyone runs into this anomaly. There was negative pressure in the hose within the first 2 feet. Cut it there and spliced pvc pipe for the remainder

  • 109A_5
    109A_5 Member Posts: 4,346

    So it would suck stuff in from either end ? What was the source of the negative pressure ?