Bit the bullet: bought an HTP UFT-100W on ebay

RickT
RickT Member Posts: 67

Actually I bought TWO of these UFT-100Ws, for $1,000 each. Our 50 yr old boiler went kaput in March and I am going to try to DIY my way into a heated home over the next few weeks.

They haven't arrived yet but the seller said they were manufactured in 2020 or later, so I am assuming they won't have the control board problems I have read about on here. I will check the info when they arrive to confirm. I know I probably won't qualify for any warranty for these discontinued units purchased on ebay, but $2k for TWO boilers was hard to beat. They are advertised as brand new, unopened. Pictures look like this is true and I will confirm of course.

I am planning to install them in a cascade setup so the heating load is shared between the two, and so that if I have to service one, I can bypass it and still have heat. My calculated heat load is about 93k BTU (DIY manual J and HDD methods both agree), so the pair of these will provide more than enough for the coldest days. The EDRs of all our rads can't even put out more than 130k at 180 degrees, so I am certain these two 100k boilers will be much more than enough, haha. But with the modulation, cascade mode, outdoor reset, etc etc they should do a good job of keeping everything efficient.

On a scale of 1 to 10, how dumb was this purchase?

Comments

  • mattmia2
    mattmia2 Member Posts: 13,756

    If you want fancy control i'd go with a viessman or lochinvar of the appropriate size. the control on the uft can do some stuff but it is fairly limited.

  • hot_rod
    hot_rod Member Posts: 25,443

    Doesn’t sound like often, maybe ever, both boilers will need to fire?

    So you got a good deal for the $$

    Does the the onboard control have boiler staging?

    If you want a feature rich staging control, take a look at tekmar

    Essay here

    https://www.watts.com/dfsmedia/0533dbba17714b1ab581ab07a4cbb521/81898-source/e005-06.pdf

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Member Posts: 13,756

    it does cascading with the right interconnect cable.

  • hot_rod
    hot_rod Member Posts: 25,443

    one as a spare of connect two and flip flop for equal run time

    Or lead lag

    If one carries the load, just store the second as a spare, eliminate the issues @GGross mentioned

    You have a few options

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • PC7060
    PC7060 Member Posts: 1,707
    edited August 12

    I have UFT-80 installed in my home and picked up a second one cheap as spare. Pretty simple install, just follow the manual. I'd install the single unit and keep second for hot spare. Use the time and $ you save to improve the air sealing and insulation of the home envelope. Will pay off all year long.

    Be sure to install a DirtMag prior to the boiler.

    IMG_7034.JPG
  • GroundUp
    GroundUp Member Posts: 2,388

    Fair price IMO. I was paying about $1800 for a 100W in 2019 when I stopped using them but as long as you don't have all low temp radiant or need any tech support, they're a pretty good boiler. As was mentioned above, I'd probably just install one with unions and keep the second for parts/spare rather than a cascaded system but you're welcome to do as you please.

    PC7060Rich_49
  • GGross
    GGross Member Posts: 1,582
  • mattmia2
    mattmia2 Member Posts: 13,756

    They have a 10:1 turndown ratio, they should do low temp as well as anything else out there.

  • PC7060
    PC7060 Member Posts: 1,707

    mine runs temps of 90-115f

    mattmia2
  • GroundUp
    GroundUp Member Posts: 2,388

    The Kiturami HX has some weird aluminum diverter plates in the SS fire tubes that tend to plug up with scale when running low temp and are just about impossible to clean. I installed a crap load of UFT and Laars Mascot FT from about 2016 to 2020 (hated HTP customer service and switched to Laars, then started seeing these issues come up) and have been kicking my own butt for it on a regular basis. High temp systems and low temp w/ indirect seem to be doing okay, but low temp only have been a nightmare. @Ironman and I have talked about this, I believe he's replaced a few HX as well that were not salvageable

    PC7060
  • PC7060
    PC7060 Member Posts: 1,707