  • ChrisJ
    ChrisJ Member Posts: 17,565

    When the compressor stops, you stop pulling gas from the evaporator, so it's going to essentially be full the next time it starts, if not overfull.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,684

    @mattmia2

    • Non-Bleed (Hard Shut-Off) TXVs: Most modern air conditioning and refrigeration TXVs are non-bleed. When the system shuts down, the superheat drops to zero, and the valve's spring forces it to close tightly. These valves do not allow pressures to equalize during the off-cycle, meaning the compressor must start against a significant pressure difference. [1, 2, 3, 4, 5]
    • Bleed-Port TXVs: Some valves feature a small bleed port (or a notched seat) that allows refrigerant to slowly bypass the valve. This gradual leak equalizes the system's high and low side pressures during the off-cycle, reducing the load on the compressor at startup. [1, 2]

    Systems utilizing a non-bleed TXV and a standard PSC motor often require a Hard Start Kit to help the compressor overcome the un-equalized pressure difference at startup. [1, 2]

    image-5891419751dae8-2b3c.png image-265400619b38b-cf93.png image-ad5a057cacb9e-85fb.png

    7 sites

    Show all

    This is an AI thing but true. Prevents liquid migration to help keep the compressor from slugging on start-up. Of course there are also accumulators and solenoid valves to help prevent this.

  • Harvey Ramer
    Harvey Ramer Member Posts: 2,292

    @EdTheHeaterMan

    Can you check the locked rotor voltage?

    Screenshot 2026-07-17 232751.png
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,594
    edited July 18

    We are way past this topic. this was resolved last summer. The reason for the renewed interest is because @mojones469's comment from this morning

    Since this was the first post from this new member, there may be something suspect about it. perhaps it is AI bots posting and seeing if there is any response. We have asked the @HeatingHelp.com admins to look into this.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Harvey Ramer
    Harvey Ramer Member Posts: 2,292

    Gotcha

  • HeatingHelp.com
    HeatingHelp.com Member, Moderator, Administrator Posts: 261

    Since @EdTheHeaterMan said his original issue was resolved, I'm going to close the thread. -Andrew