Hi,

I have a Rheem "Guardian" 50-gallon natural gas water heater manufactured in June of 2010. This is the original water heater to the house. We bought the house in November of 2024, and my guess is that it's never been flushed. The water heater is in the garage, and we live in south metro-Atlanta. I'd like to be proactive and replace it with another 50-gallon natural gas water heater as I think its time is nearly up. No issues so far, however. I am not interested in tankless, standard electric or heat pump options.

I want to purchase the most reliable brand on the market. My past experience suggests that is Bradford-White, but I am not an expert by any means. Few plumbers in my area, however, install this brand. Many seem to favor Rheem and Ruud. My impression is that these are mid-tier as far as reliability is concerned. I really want a brand that, as far as reliability is concerned, is pretty much bullet proof. If that is indeed Bradford-White, I'll find a plumber that installs them and pay a premium if I have to.

Does anyone have a suggestion as to which brands are worthy of consideration for bullet-proof reliability? Understood that nothing it truly bullet proof, but I would like to stack the deck in my favor.

Many thanks!

«1

Comments

  • Hi, After turning off the water and relieving pressure, I'd check the condition of the anode rod in the tank. It's your best indicator of actual tank condition. I'd also look around the tank for evidence of new or old leaks. I'd look into the combustion chamber also. If things looked okay and if there was something left of the anode, I'd just replace the anode and then check it periodically… that time period will depend on anode condition and water quality. 😉

    Yours, Larry

    bburdRobert_H
  • wcweaver3
    wcweaver3 Posts: 56

    Hi Larry,

    Thanks for the guidance. I regret that I don't have the skill set to engage your suggestions. To get a plumber to do it is $200+ so I'd rather just replace the whole thing and be done with it. Given that scenario, do you have a recommendation as to a more or less bullet proof brand I should consider?

  • B-W, Rheem, A.O. Smith. They're kinda' all the same these days although I've had issues with B-W in the past - had to replace a burner. From what I remember, most are made in the USA, assembled in Mexico.

    Standard was a 5 year warranty and you could get one that had a 10 year warranty that had a second anode rod, but don't know if that is still how they structure their products.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    wcweaver3
  • Mad Dog_2
    Mad Dog_2 Posts: 8,755

    I have exclusively installed Bradford White over the last 30 years after the others didn't hold up like they promised..Mad Dog

    rick in Alaskawcweaver3
  • MikeL_2
    MikeL_2 Posts: 561

    You can add life to most atmospheric fired water heaters by including a powered anode & thermal expansion tank as a part of the install. Draining & flushing yearly will extend life, too.

    wcweaver3Boilerengineer
  • Intplm.
    Intplm. Posts: 3,162

    I have been installing Bradford White water heaters for years. Very reliable, installed with confidence.

    If the plumbers in your area do not install them/recommend them, BW might not be readily available in your area. Check to see if they are offered at plumbing supply houses near you.

    wcweaver3rick in Alaska
  • STEAM DOCTOR
    STEAM DOCTOR Posts: 2,680

    The issue with the BW's, it that it's a pain to replace the anode rod. Need to do some un-piping and maneuver around the existing piping.

    wcweaver3
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    BW seems to hold up the best.

    Intplm.wcweaver3
  • hot_rod
    hot_rod Posts: 28,708

    A lot of the residential tanks are manufactured in the same plants, different jackets and labels.

    When you buy a 7 or 10 year tank, you may get two anode rods, same tank. The extra $$ is more like an insurance policy than a better tank.

    I'd like to see electric anodes offered on the 7 and 10 year tanks, then the extra $$ would have more value.

    BW has a good reputation, it used to be a trade channel product?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    wcweaver3
  • mattmia2
    mattmia2 Posts: 18,399

    I believe BW used to have their plant in rural michigan somewhat near me, I know others are in the south somewhere. There are a couple manufacturers but nowhere near as many manufacturers as brands.

    I would go with the powered anode and change the crappy factory drain out for a good full port ball valve with hose thread and a cap so you can do a good job of flushing it.

    Mad Dog_2wcweaver3
  • wcweaver3
    wcweaver3 Posts: 56

    Thank you @Larry Weingarten @Alan (California Radiant) Forbes @Mad Dog_2 @MikeL_2 @Intplm. @EBEBRATT-Ed @STEAM DOCTOR @hot_rod @mattmia2 I really appreciate the great responses and strong guidance!

  • hot_rod
    hot_rod Posts: 28,708

    Bock is another tank built in the US. Their tanks used to be thicker steel cylinder and heads, thicker glass coating, even thicker sheetmetal jackets. You could tell by the weight listing compared to others.

    Screenshot 2025-06-30 at 8.05.25 PM.png Screenshot 2025-06-30 at 8.06.18 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mad Dog_2
  • mattmia2
    mattmia2 Posts: 18,399

    then there is the htp that is stainless.

  • Ahoy
    Ahoy Posts: 3

    I went with HTP 11 years ago. I had had an AO Smith Sureshot Direct Vent (DV) since 2000 and it cracked in 2014 despite replacing the anode rod regularly and flushing once or twice a year.

    I needed DV because we had eliminated the chimney. In 2014 the tank DV options from AOSmith and BW would have been a lot of extra work due to the the strict requirements for the height of the vent penetration.

    After figuring that out the day after failure, I bought the cheapest electric water heater I could find at the big box and set it up temporarily powered via the nearby dryer receptacle.

    I ruled out tankless because of 1) the complexity of integrating my recirc system 2) the need to upsize the gas line & meter or regulator based on calculation 3) fill time required for a spa tub.

    THE HTP Phoenix 76-50 caught my eye because it was stainless, easily modified to work with recirc, was 76,000 BTU, Just under my load limit for existing piping, and the draft inducer - condensing venting requirements were flexible enough to use the existing penetration.

    What I really appreciate with this is that, with almost twice the burner capacity of my old 50-gallon DV, it can run an endless shower and recover very quickly in all our usage circumstances. It is challenged by my wife filling the spa tub at full bore mid-winter, but she is aware of her options and it is her choice to fill fast and have slightly cooler water.

    The only maintenance I've had to do besides flushing is rehabbing the condensate rock box which clogged after 10 years.

    They sold this unit under the Westinghouse brand for a while in the big boxes, too, but I think they have scaled back. Have not checked lately.

    Very happy with it!

    oldgit
  • SKYPAINTER
    SKYPAINTER Posts: 12

    WC - The commentor known as "Hot Rod" is very, very knowledgeable and highly respected in the hydronics industry, I would definitely listen to what he said. Bock and Bradford are both excellent products, I would go with a power-vent model if you can vent it properly and use a power anode rod, forget those outdated sacrificial style anode rods, they are a thing of the past. Good luck!

  • ChrisJ
    ChrisJ Posts: 17,763

    I didn't think a powdered anode was possible with a Bradford White heater?

    All anode rods are "sacrificial style", no?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ethicalpaul
    ethicalpaul Posts: 9,076
    edited July 2025

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • mattmia2
    mattmia2 Posts: 18,399

    Someone has a page on how to put a powered anode on different styles of water heater. If it doesn't have a tapping for the anode you can put it through a tee on the outlet.

    Anodes that produce the current through an electrochemical reaction are sacrificial. Powered anodes are not sacrificial, they are not consumed to produce the current that favors deposition of iron, it is produced by an external power supply.

    Larry Weingarten
  • ChrisJ
    ChrisJ Posts: 17,763

    Different doesn't necessarily mean goofy.

    Unless it's a mouse with 1 button when everyone else has 3. Then it's goofy. 😉

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    mattmia2PC7060Robert_H
  • ethicalpaul
    ethicalpaul Posts: 9,076
    edited July 2025

    sorry but using the same port for the water output and the anode is goofy!

    Our mice have trackpads on the top, try it

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • ChrisJ
    ChrisJ Posts: 17,763
    edited July 2025

    Less ports means less places to leak, no? Id also bet each tapping is another damaged place in the glass lining.

    Also means cheaper to manufacturer.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ethicalpaul
    ethicalpaul Posts: 9,076

    …marginally less expensive to manufacture and more expensive for everyone to work on and buy parts for, great plan. Anyway, yes you can get an electric anode for it

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • ChrisJ
    ChrisJ Posts: 17,763

    You kinda just skipped over my point…

    The point being, cheaper, with less failure points and less damage to the glass lining.

    As far as more to buy parts for…… 99% of people never touch their anode.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    PeteA
  • ethicalpaul
    ethicalpaul Posts: 9,076

    I don't know about less damage to the glass "lining". My understanding is that it's just spray paint that's baked on to provide a sort of glassy coating. But regardless we all know they fail in 10 years or less typically so whatever.

    But yes you can put an electric anode on a Bradford White

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • A.O. Smith owns the vast majority of the market branding under different names.

    The Federal regulations have made all heaters have a shorter life in the name of effeciency.

    you can extend the life of any heater by draining a little off the bottom to keep the sediment out and changing the anode rods every three to five years. Which heater to buy really depends on whether your distributor carries the parts in stock. Home depot does not and you ca only go to the manufacturer on line.

  • ChrisJ
    ChrisJ Posts: 17,763

    I don't believe the general life of a tank water heater has changed at all over the past 60 years.

    Neither has the efficiency aside from dampers on natural draft heaters, insulation thickness and other designs like power vent and direct vent.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Hi, Being the hot water nerd, I can comment. If anything, hot water lifespan for unmaintained tanks has decreased. Tanks are made of thinner steel. Glass lining used to be available as a doubled coating, and also sometimes done on the fireside of the tank. I've seen commercial style anodes used in residential tanks, putting a lot more magnesium in the tank. Efficiency has gone up, primarily due to better flue baffles being developed and used. Better insulation and heat traps add some also.

    A gripe of mine is they we forgot about the "U" tube heater, where the flue forms a heat trap by going up then back down before exiting the heater, low on the side. That heater must have "leaked" a lot less heat all of the time, compared to the standard straight flue.

    Yours, Larry the Nerd 😜

    PC7060
  • ChrisJ
    ChrisJ Posts: 17,763

    Larry,

    For some reason it seems like 10 years was the number everyone always says even 40 years ago? I have zero problems being corrected by you, you know far more about water heaters than anyone I know. I'm only going by memory and my own experiences which is a very tiny sample.

    Curious, do you feel more tappings in a tank means more possible damage to the glass lining, and therefore more chance of failure? For example, Braford White tanks which have the anode built into the hot water outlet vs other brands where the anode has it's own tapping?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Larry Weingarten
    Larry Weingarten Posts: 4,210
    edited August 2025

    Hi and yes, more tappings means more failure points, both inside and out. I like a tank with more tappings as it gives more opportunity for adding a second anode. As most people don't maintain tanks, the added tapping probably doesn't matter much. Way back when, we had copper and Monel tanks, and over 150 manufacturers, so some tanks were made to last far longer. 😇

    Yours, Larry

    ps. About the ten year thing, it's sort of a standing joke that if a plumber thinks the tank is ten years old, he says "Time for a new heater. This one could leak anytime." I've seen this happen with copper tanks too 🤔

    PC7060ChrisJethicalpaul
  • pioneersprings
    pioneersprings Posts: 1
    edited December 2025

    Great thread! As someone who installs water heaters in hard water regions,

    I can confirm Larry's points about anode rod management.

    One thing I've noticed: most homeowners don't realize the anode rod is the actual limiting factor, not the brand. We've installed Bradford White, Rheem, and HTP units longevity depends entirely on water chemistry and maintenance.

    **From our experience:**

    1. Anode rod replacement at year 2-3 extends ANY tank 5-7 years

    2. Water quality testing before installation prevents expensive failures

    3. Drain valve upgrade (plastic to brass) makes flushing actually effective

    4. 40-60 PSI pressure maintenance matters more than warranty length

    The Atlanta homeowner asking: Get your water tested first (hardness, iron content, pH). That determines lifespan more than any brand choice.

    HTP's stainless option is worth considering if available in your area, but honestly proper maintenance beats premium brands every time.

    Thanks for the discussion. This helps homeowners avoid brand chasing when

    water chemistry is the real answer.

    NAME: Henry Cooper

    Larry Weingartenbjohnhy
  • hot_rod
    hot_rod Posts: 28,708

    Temperature of the water has a lot to do with mineral precipitation. Hotter water = more minerals coming out of solution.

    Second factor is the amount of water that the tank sees. The more water, the more minerals, the shorter the lifespan of the tank.

    Currently manufactured glass lined tanks seem to have about a 7 year life expectancy.

    You can buy longer warranty tanks, but you get the same tank, the manufacturer is playing the odds on the life expectancy.

    If you go with a stainless tank, check the chloride levels of you water.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • ethicalpaul
    ethicalpaul Posts: 9,076

    seven years, @hot_rod ???

    Then why is everybody going around saying heat pump water heaters aren’t to be trusted???

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • hot_rod
    hot_rod Posts: 28,708

    I think 7 years comes from some of the wholesalers on this list, actual experience. This is for gas or LP fired tanks.

    HPWH have no burner, no flue, low thermal shock potential and the HX wraps around the outside of the tank, so no additional penetrations, which is where glass tanks generally fail, the welds.

    Early indications are the controls or the refrigeration components are the common failure with HPWH. Same as mini splits :)

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • ethicalpaul
    ethicalpaul Posts: 9,076

    OK so gas water heaters that rot out in 7 years are good and heat pump water heaters that everyone thinks fail too early (with no data to back it up) are bad, got it!

    Sorry to be flippant, but it's hard to understand things here sometimes!

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • ChrisJ
    ChrisJ Posts: 17,763

    I never said they couldn't be trusted,I said they do not have nearly enough output for my family of 6.

    Not even close. Id be running on resistance heating constantly.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Hi, The number I've been going with for tank longevity, for unmaintained tanks is 9-12 years. That was from someplace like Lawrence Berkeley Labs. More recently I've been hearing of HP units lasting for 15 years until something expensive kills it, like a compressor failure or tank leak. Too many HPs were designed with poor access to the anode rod, so are unlikely to get that maintenance. Those tanks would probably be happy to have a powered rod. 🤩

    Yours, Larry

  • ChrisJ
    ChrisJ Posts: 17,763

    And yet I changed mine at 5 years or so it still looked plenty thick and my tank still failed at 9 years. Hopefully me dropping my pressure from 90 to 60 will make a difference.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    ethicalpaul
  • ethicalpaul
    ethicalpaul Posts: 9,076
    edited December 2025

    I put a powered rod on mine. the Anode rod was a little harder to get to, but honestly, how many rods are getting checked/replaced on gas models? 😅

    More recently I've been hearing of HP units lasting for 15 years until something expensive kills it, like a compressor failure or tank leak.

    In that much time, the HP unit would have paid for itself at least two times over compared to the cost to run a natural gas unit

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el