Which valve do I turn off auto feed

Options
Ghynes440
Ghynes440 Member Posts: 45

I’m trying to drain my boiler which is getting replaced in a few months, which valve do I turn to stop it from auto filling? I’m trying to pull a radiator

IMG_2206.jpeg

Comments

  • pecmsg
    pecmsg Member Posts: 6,236

    red handle on the left side upstream of the auto fill b

  • Ghynes440
    Ghynes440 Member Posts: 45

    thank you!

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,652
    edited June 19

    It appears that your boiler also does your hot water. How soon is the replacement boiler coming? Is there water heater already in place? If you are still using the boiler for DHW, you may want to keep the pressure valve operational until you have made arrangements for an alternative DHW source. if you let the water level in the existing boiler get too low, then you may have a cracked boiler on your hands. If that happens, you will be without DHW until you get your new system in place.

    EDIT:

    If you need to remove a radiator, you can cap off the both sides of the radiator feed pipes so you can re-pressurize the system for DHW usage.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • HVACNUT
    HVACNUT Member Posts: 6,815

    Come back "in a few months" and post pics of the beautiful new boiler. 👍

    EdTheHeaterMan
  • hot_rod
    hot_rod Member Posts: 25,231

    either the red or blue valve will turn off the fill. Hopefully the pressure in the boiler, on the square gauge, does not drop with the fill valve off. If so you want to find and repair leaks before adding a new boiler.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Ghynes440
    Ghynes440 Member Posts: 45

    there is a water tank already installed to the right of the boiler

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,652

    @Ghynes440 said "there is a water tank already installed to the right of the boiler"

    Then you are good to go. shut off the water feed (Red Valve) and drain the boiler you can then remove the radiator in question.

    After you install the new boiler, you will need to put the old radiator back or cap off both pipes (supply and return) so you can put water back in the system.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?