Radiant Snowmelt Tubing Size and Placement- Under Eaves

Options
davidm2232
davidm2232 Member Posts: 3

I am designing a snowmelt system for my garage. There are two sidewalks 4'x28' on each eave side and an apron that is 28x20 on the gable end. I also have 2 12' overhead doors and 2 3' man doors on the eave sides. I live in the Adirondacks of NY so it is not uncommon to get 3' of snow along with wind and zero degree temps.

For the apron, I am probably not ever going to heat it, I may on occasion but the pex will be in there for heating the slab if I ever add on the garage.

The sidewalks will probably just be heated occasionally after I plow off the main snow just to keep them ice free.

The big issue are the man doors. I want those to stay clear all/most times. But they are right under the eaves and the snow slides off the garage roof. What tubing size and spacing do I need to make sure all the snow gets melted quickly? I was thinking 5/8 tubing at 4" spacing. Is that overkill? Also, do I have to worry about cracking the sidewalks if I am only heating a 4x4 section and leaving the rest cold? I am doing my design in LoopCad and have an estimated 115K BTU load if I was to run the entire system but only 6k for the man doors which is totally doable off my current boiler (85K).

Comments

  • hot_rod
    hot_rod Member Posts: 25,263

    Here are the classifications of snowmelt design. Bottom line…how much snow and how quickly do you want to melt?

    Of course the faster the desired melt, the more boiler power you need. I would guess 200 btu/ sq ft or more for a system like that.

    What will it be powered by, it will not be a cheap date to run.

    Screenshot 2025-05-16 at 8.25.47 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mad Dog_2
  • Big Ed_4
    Big Ed_4 Member Posts: 3,232

    Food for thought in your design .. Drainage

    There was an error rendering this rich post.

    Mad Dog_2GGrossSuperTechKaos
  • davidm2232
    davidm2232 Member Posts: 3

    I have drainage thought out. My dad who pours concrete for a living thinks I am going overboard on the drainage, but he has no experience with snowmelt systems

    As far as the ASHRAE, that seems to not cover anything about snow falling off roofs. I will be running off an oil boiler to start. I may add a wood or coal boiler if I determine I like the way the system performs.

  • hot_rod
    hot_rod Member Posts: 25,263

    I don’t think it really matters where the snow comes from, just the amount of snow and the time required to melt to water.

    Chicago O Hare has or had some hydronic melt pads or pits they dumped snow onto with loaders.

    I see more of the metal dumpster looking devices being used now to melt snow as it is dumped in, at Chicago

    Regardless, it takes a lot of energy to melt snow.
    I would run a section of 3/4” pex in that area, get the tube spacing as tight as possible, if you want to try this. Insulate below with 2” foam

    With large diameter tube you “light bulb” the loop ends. A 10 or 12” diameter loop, then back to 6” spacing for the straight runs

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Jamie Hall
    Jamie Hall Member Posts: 26,121

    The snow that slides off the roof over the main doors… um, no. What you will get if that happens is a pile of snow — essentially the entire roof above where it hits — in a dense heap. Much denser than fallen snow. To look at it another way — the equivalent of perhaps 8 to 10 feet of snow in a nice dense pile two or three feet high.

    Seen that.

    There is a very good reason why barns in snow country are designed to keep snow from sliding off the roof over a door (a door in a side wall). Now there are several ways to do that. A covered area like a low dormer to deflect that roof snow off to the sides is sometimes the simplest. Assuming, of course, that the door has to be in a side wall for some reason (and there are good reasons). Alternatively, brakes of various types and styles (there are a lot — homemade and commercial) to keep the snow on the roof in the first place. They work pretty well — though of course the roof has to be designed and built to take the snow load…

    But don't think you are going to melt that heap of snow with a snow melt system. Not in the Adirondacks. Not going to happen. At least not in any reasonable time frame.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    PC7060
  • hot_rod
    hot_rod Member Posts: 25,263

    if you are just heating a 4’ wide path at the man door, that is more workable than the entire overhead door area.

    Plow or shovel first, then melt for ice protection, maybe?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Big Ed_4
    Big Ed_4 Member Posts: 3,232

    Just thinking you living up in Gods country and all , if it were me , I would have the system humming for those night storms that could hit up there :). I would guess you have a plow…

    There was an error rendering this rich post.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,117

    @Jamie Hall Idea would be a lot cheaper and may cut down on the amount of snow that needs melting

  • davidm2232
    davidm2232 Member Posts: 3

    After looking at PEX and foam costs, I am not going to heat the whole apron/sidewalks. Just the areas in front of the doors. This will cut down the BTU load significantly. I can then focus on putting the max amount of heat into where I really want it while still making the system somewhat economical to run.

    The plan is to run just a 4' section in front of each of the man doors pretty much all the time. I don't plow the driveway unless we get over 6" or so. I just need to keep it clear in front of the doors so I can walk to my car in the morning without getting snow on my boots. If we get a 2' storm, I can plow away the majority then let the snowmelt run in front of the doors for the smaller piles the plow can't get to. The overhead doors on the gable ends will just need to keep it warm enough so that when I plow, the snow right next to the doors will melt so that they will close all the way.

    I like the idea of 3/4 pex closely spaced in front of the doors to give maximum heating.

  • Jamie Hall
    Jamie Hall Member Posts: 26,121

    Good luck. Your two foot snowfall will put eight to ten feet of snow dense packed into a three foot mound in front of those doors when it slides off the roof. I've watched it happen to folks. Then came over with the front end loader on the tractor and shoveled them out…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Kaos
    Kaos Member Posts: 668

    This!

    There are a number of snow melts around me that do an excellent job of turning some easy to shovel snow into an iceberg at the end of the driveway where the heat stops that needs to be chipped away.

  • hot_rod
    hot_rod Member Posts: 25,263

    define the space. .4x20’ work for you?

    A grate at the end running yo a pit or gravity drain in some cases we would run a pex loop along the drain. Until it could drain away without re-freezing

    Actually wet heavy snow melts best. Light powder snow would “bridge”. The light fluffy snow would not push down against the warm slab. An air space would form between the snow and slab.

    So you have that going in your favor, with dense snow.

    As you know, the more snow you can move manually the less work the slab has to do

    At the ski areas were I worked, lodges with metal roofs always had snow hooks to keep snow on the roof, and off the tourists

    Obviously those roofs were designed for heavy loads.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream