Steam bath in the boiler room

JohnMansolf
JohnMansolf Member Posts: 8

I'm troubleshooting a Weil McLain 380 steam boiler. The boiler room has been filling up with steam from the condensate tank vents and water bubbling out of the main air valves. The piping is a two-pipe gravity system with a wet return. There are no traps, only air valves. When I started the boiler, I noticed that the condensate pump filled the boiler to the top of the sight glass. I replaced the 15-year-old pump control and low water cut-off. (The head replacement is recommended every 5 years.) When I started the boiler, the pump control and low water cut-off filled the boiler halfway up the sight glass and stopped. This morning, the boiler is up to temperature. My concern is that the water level is almost to the top of the sight glass. Am I overreacting, or should I be looking at other symptoms? The wet return has a 6-foot-high loop before going into the condensate tank. The water level in the condensate tank is normal and gets flushed every year. Should I install a drain to flush the wet return before the loop?

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,162

    Pictures please..Mad Dog

    ScottSecor
  • Pumpguy
    Pumpguy Member Posts: 751

    Ordinarily I would say you have leaking trap(s), but you say no traps.

    We need more information to identify what type of system you have.

    Based on the limited information supplied, I'm guessing you're operating with too much steam pressure.

    What is the operating steam pressure?

    Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
    Website: www.nashjenningspumps.com

    The first step in solving any problem is TO IDENTIFY THE PROBLEM.
    mattmia2ScottSecor
  • JohnMansolf
    JohnMansolf Member Posts: 8

    1.5 PSI Pictures shortly

  • Steamhead
    Steamhead Member Posts: 17,789

    Why do you even need that condensate pump?

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    mattmia2Mad Dog_2
  • JohnMansolf
    JohnMansolf Member Posts: 8

    The condensate is part of the existing system. Here are some pictures to see what I am looking at. Thanks in advance

    1000014522.jpg
  • ScottSecor
    ScottSecor Member Posts: 980

    Based on the right low water cutoff (MM #150) and the gray tank in you photo above. I think your tank is actually a boiler feed tank. I tried to read the scale on your pressure controls, I cannot make out the numbers.

    Boiler feed tanks have a feedwater pipe that allows city water to automatically fill the tank when needed. In you case I suspect there are two possibilities, you may be able to simply lower the pressure setting to prevent steam from blowing back to your boiler feed tank. On the other hand, your boiler feed tank may be overflowing due to a faulty feed valve/ballcock.

  • JohnMansolf
    JohnMansolf Member Posts: 8
    edited April 17

    The pressure controller is set to 1.5 PSI, and the diff is set to 4 kPa. The reset controller is set to 3 PSI. I have # 35 air valves in the returns which are rated for a 3 PSI. The condensate tank has about 8 inches of water in it. We have not had a steam bath since replacing the McDonnell & Miller 150s. Then again, it has not been very cold😏

    Seems pretty normal except for the higher than normal water level in the sight glass (1st picture).

  • Steamhead
    Steamhead Member Posts: 17,789

    Unless you've got a really short "A" or "B" dimension, you likely don't need that condensate pump. If you get rid of it you can get rid of some moving parts and servicing issues. Where are you located?

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    ethicalpaul
  • JohnMansolf
    JohnMansolf Member Posts: 8

    Connecticut, I know what you mean.

  • Steamhead
    Steamhead Member Posts: 17,789
    edited April 17
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,414

    The issue that will come up when the tank is removed is that there is no venting. You'll also need to double check the fire rate of the boiler against the connected EDR. I'm not saying to check the rating on the boiler but to actually clock the meter.

    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating