Help: What's an affordable way to get a smaller, one pipe steam radiator?
I am interested in replacing a one pipe radiator in my living room (NY, pre-war building). It works perfectly fine, but it's the original radiator and takes up a decent amount of space in my small apartment.
I've put pictures of the unit and some details for heat loss calculations below. The current radiator is 76 cm wide x 65 cm high x 24 cm deep.
I've looked at Castrads (very expensive), Governale (not great style) and Runtal. I would have loved the Runtal for the space savings, but I couldn't fit a unit large enough for sufficient heat.
Any ideas?
Yes, I own the apartment. I’ll see if any shops have something relevant.
Junkyard/salvage shops have all but disappeared in the 5 Boros. One that comes to mind that still has some used radiators is The Bronx, Mike's I recall. Tje Burnham Classic Victorian is an option as well. Mad Dog
That rad is rated 45 square feet EDR. You need something with similar rating. Governale's 4-tube, 25", 22-section rad would work since it won't stick out so far from the wall.
2 -
There are tons on Facebook Marketplace as well. For the size you are looking for you probably muscle it into your trunk.
@OnePipeProblem If you are planning a trip up I95 in the future, look at a few salvage yards in Ct. They still should have a few cast iron rads around.
I would leave it as is and put a radiator enclosure over it. No reason to disturb it or cause an issue.
Buy or have a carpenter build you one. You can control the heat by how much air enters the bottom of the enclosure
So are you trying to match the output of your current radiator in a more workable shape/configuration or are you looking to reduce the edr? How tall is the 2 column radiator you have now?
Based on the OP'S comment, the former. (physical size)
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
What is happening with the stool on that window?
Based on his listed options it looks he may be looking for less depth but maybe the length is more his concern?? If the latter a shorter 3 or 4 column would work. If the output is good for the room right now and want to stay the same then that is needed input. He said the window sill height is 26" so I figure the radiator there now isn't any taller than that so figure 2.6sqft/section x12 = 31.2sqft. Could go with an 8 section 3 column or 6 section 4 column or many other configuration around 30sqft. @Steamhead
I see you came up with 45sqft so maybe you have a better identification on that radiator?0 -
@dabrakeman , OP gave dimensions in centimeters, and I converted them to inches. 9" deep is 3-column, and it's 26" high- 3.75 square feet per section.
1 -
Thanks for so many helpful comments! Really appreciate all of the knowledge and generosity of the group.
Correct, my goal is to maintain the heat level while decreasing the size of the radiator. The goal is to gain a bit more space in the living and improve the look.
I'm familiar with the requirements for changes in my building, which will be the step after I figure out the best solution / model for the situation.
Runtal makes steam radiators ? Double check …
Can you get away with a smaller radiator , How is that size working out ?
For the same comfort,you probably realize that you'll need a cast iron radiator with similar mass and the same square footage "EDR". The type you are replacing is a two column steam radiator from the 1900 - 1925 era.
The smaller cast iron radiator with the same EDR would be a "compact tube" model with multiple tubes from later era.
A steel or aluminum modern replacement will not do the job. It will not retain sufficient heat, allowing the space to cool excessively between cycles.
A properly designed system utilizes a similar type radiator in each conditioned space.
1 -
Pictures can be deceiving... You must be right.
