Boiler harmonics/piping fix
I have an rbi boiler that’s been installed for roughly 5 years. Apparently it’s been having harmonics issues since the beginning. I added pictures of the existing piping where they tried to do closely spaced tees with a building loop. After speaking with tech support they suggested changing the pump speeds and that should help. It didn’t. I have a feeling my common piping or building loop is way to small and clearly doesn’t run through the entire building. I have a 10 degree delta T at the boiler and I think that’s part of the problem. The harmonics only happen when the boiler temp gets up to 170 degrees and stops when the boiler/boiler pump turn off. It seems like a flow issue. I want to redo the piping with the drawing I added. The first zone is my largest “sanctuary” and my other 2 zones are just small classrooms with 3/4 fin tube. With my suggested piping should my largest zone be first and last back to evenly distribute heat? Has anyone seen harmonics like this? If so is there a quick fix with the existing piping or should we just rip it out and start over? We did
remove piping and flush heat exchanger, no signs of annealing at this time and the copper fin tube wasn’t plugged up internally or externally. Tech support is saying the ups26 should be the right size pump for this size boiler, so it brings me back to the lack of common piping. Any advice is appreciated
I'm not quite sure what you mean by "harmonics". That's a term I would usually use for an acoustic problem…
Your diagram shows three zone pumps, as well as the primary pump. Is that correct? If so, does the problem occur regardless of which zone pump or pumps are operating?
I also note a big compression tank overhead. That is not shown on your diagram; how does it connect to the rest of the system?
And last, to get back to the harmonics problem — I see a lot of somewhat poorly supported, though elegantly assembled, piping. That can cause vibration or harmonic problems.
More information, I think.
Yea for some reason it isn’t letting me upload the video. You can hear it through the building like a ghostly wail. The old compression tank has been abandonded and it’s using that bladder style tank. The drawing is how I would like to change the existing piping if needed. Yes it’s a 3 pump system, one for each zone, one for the boiler and one for the secondary “building loop”. Yes it happens when any zone calls and when they’re all calling, and only stops when the boiler turns off. If the pumps are still running for the heating demands and the boiler isn’t the house is gone. I can email you the video if you don’t mind.
You can do some simple experiments to see if the noise is related to flow velocity. You said you already turned the boiler circulator to low speed, but that could still be over-pumped. Try throttling the flow through the boiler loop by partially closing one of the ball valves near the boiler supply or return. Ball valves aren't the best choice for flow control, but this is just an experiment. If that eliminates the noise, we might reasonably conclude the noise was from the boiler loop water velocity being too high.
You also have a manual bypass valve. Does the valve position make any difference?
I'm still confused. You say "three pump system" and then you reference four pumps: one for each zone (3), one for the boiler (in the boiler?) and one for the secondary "building loop".
From the above, however, may I suppose that you only hear the noise when the boiler (internal) pump is running, but always hear it when that one pump is running? Is there any way you can run that one pump without the boiler firing? And are there any valves on that particular circuit?
And how does that pump relate to the secondary "building loop" pump.?
From what I can see from the picture you have many pipes that are either not supported or supported metal to metal or concrete to hanger etc. This can cause the noise that you are describing. The hydro-sorb type -b-line strut hangers seem to have that rubber cushion on some hangers but not all of them. This can make the whine, hum or harmonic problem you describe.
Go to the boiler while it is running and place your hand on different pipes. Push and pull on them a bit to see if or how the music changes.
This boiler is piped into a corner and will take some doing to add and reinforce your current supports as many pipes are in the way.
I would add and fix current supports to soften and even eliminate the noise before repiping everything.
Here are some pictures of different types of what can be called hydro-sorb supports.
1 -
Yes there are 5 pumps total. One for the boiler a grundfos ups26 multi speed one for the primary loop also a ups26 multi speed (we’ve tested it every speed combination) then each of the 3 zones has a taco pump installed. The noise only happens when the boiler water is heated up at 170-180, we’ve tried moving and resupporting pipes but the noise still occurs at higher temperatures only. When the boiler turns off and all of the other pumps run the noise is gone and it is as silent as it’s supposed to be. While the boiler is heating up the water from 60-170 the acoustics aren’t happening, it almost seems like the water is flashing and not being pumped properly at certain temperatures. The balance valve has been in every position trying to alleviate the noise but it doesn’t seem to matter where it’s located the noise still happens. I’m wondering if that secondary loop/building loop doesn’t have enough runway of pipe and is causing my delta T to only be a 10 degree split. And since the boiler is getting basically the same the return temp as supply temp that it’s flashing off through the boiler pump?
Do you have enough radiation to heat the building with 165 degree water? If so, you could just turn the high limit down on the aquastat. But obviously that's more of a temporary band-aid than a fix.
If you think the pump is cavitating at higher temps, you could raise the system pressure, but obviously you don't want to get to close to the relief valve opening pressure, so you may not have much room for an increase.
160-degree water will boil at 5 psia, so in theory a low-pressure condition could cause problems, but 5 psia is negative 10 psi gauge pressure, and if your system pressure is, say 15 psi gauge (30 psia), you'd need a 25 psi reduction on the suction side of the pump to get down to 5 psia, which seems unlikely. But it may be worth experimenting with the pressure to see if adding a few psi helps.
Videos have to be hosted elsewhere and the link posted here.
One Pipe System0 -
One minor caution in all this troubleshooting — keep in mind that with metal piping, a noise created in one part of the system will travel all over the house. It can take real patience — and if it's a motor or pump, turning it on and off — to track down the source.
I haven't posted lately because I felt insulted. My nature is to be helpful & hopeful rather than hurtful. Kinda like Ed. But, I felt compelled to address this post.
Eric, I have, in any installation, rules that I always try to follow. The supply piping into any pump, 10 to 12 pipe diameters of straight pipe and 5 pipe diameters of straight pipe on the output of the pump before any directional change in flow. Common Manifold piping should be generously sized. ( I don't know whether yours is 1" or 1 1/4". You have 3 zones of 3/4" pipe at 4 GPM for 12 GPM when all zones are operating. The Common Manifold piping should be sized for that.) The Extank should be on the imput to the pump(s). Yours appears to be. I always pump into the highest pressure loss in a circuit. The Air Eliminator should be on the hottest water from the boiler. Yours is kinda iffy. There are more rules, but let me say that I like an install to be as aesthetically pleasing and symmetrical and minimal as possible. Yours, Eric, is not. Let's address the Delta T.
The Delta T is not sacrosanct, but it does indicate how a system is functioning. A 10 deg Delta T can lead to short cycling of the boiler and a 50 deg Delta T can indicated an undersized boiler, excessively long heat emitters, an excessively high heat exchange rate to the environment, etc. This is my thinking on your sys as to the Delta T. (The reason for a bypass valve is to prevent or minimize boiler condensation. All boilers condense at some point in the heating cycle. The idea is to prevent sustained condensation which is destructive to the flue and boiler heat exchanger.) The boiler bypass valve between the input and the output of the boiler is a ball valve. It appears to me to be 1" piping and valve. This means that the valve would have to be 97% closed to provide any real regulation. Aside that, a ball valve is a poor choice for bypass valve. You would have been better off with a 1/2" pipe and 1/2" ball valve as it would have given you better regulation. I prefer a Caleffi boiler bypass valve and I have used with great success a Taco I- Series modulating valve with sensor set at 135 degs.
Mixing the hot water from the boiler output to the boiler input will lower the Delta T. What is helping lower the Delta T, also, I think that the Grundfos pump in the common manifold piping. I DO NOT think that that pump is necessary and I would remove it as your diagram shows. I have used your diagram many times and would only change the location of the pump. Per my rules, I would pump into the boiler not away. I do not know the BTU rating of your boiler, but for every 10,000 BTUs you need 1 GPM thru the boiler. So, size the boiler pump on the flow you need to over come the pressure loss of the boiler circuit, which I would think is pretty minimal. Look at the Grundfos UPS26-99FC 3 speed flow chart and select the GPM you need at the pressure loss and select the proper speed or maybe a different pump. One last thing before I close this comment.
As the boiler reaches 170 deg when the harmonics start, close the bypass valve and see if that makes a difference and measure the Delta T. Also, I would put balancing valves on the output zone piping to the Common Manifold and set them to about 4GPM. This would balance out your 3 circuits so that the greatest flow wouldn't be going thru the shortest circuit. I like Caleffi Quick Setter balancing valves.
https://www.supplyhouse.com/Caleffi-132552A-3-4-NPT-QuickSetter-Balancing-Valve-w-Flow-Meter
1 -
I have use a mechanic's stethoscope you can get at Harbor Freight or any auto parts store and checked the sys. It is helpful in pinpointing noisy components. Or, Amazon's
allsun Auto ultrasonic Car Noise Finder Diagnostic Listening Device Stethoscope 100Hz-10kHz Black. Or,
Chassis Ear Automotive Engine Noise Finder Tool, 6 Channel Chassis Ears Sound Detector Identify the Troubling Engine Noises (Over-Ear Headphones)
Noise is not necessarily a harmonic. Harmonic has a specific definition.
1 -
@HomerJSmith I agree with everything you’re saying, not my install but has since become my problem. I like the simplicity of as well and that drawing I sketched up is how I would like to pipe to keep it as minimal as possible. Even with the bypass completely closed this is still an issue. Do you think it would be better to just lengthen the runway of pipes in this application or just try to do the straight common piping without the closely spaced tees? When I disconnect the wiring from the pump on the common piping the heat doesn’t travel through the common piping causing the boiler to over heat and not work at all so I’m not sure removing that pump in this current set up will help. The main thing I’m not understanding is why the loud harmonics are only happening at high temperatures and not all the time.
What is the model of the 3 Taco zone pumps. Are the Taco pumps multi speed? The 2 Grundfos UPS 26 are UPS26-99FC , I guess. What is the size of pipe in the common manifold piping? I find it difficult to understand why a properly sized Taco zone pump can not circulate water thru the zones and the common piping. Perhaps, the common piping Grundfos UPS 26 is adding a pressure increase to the Taco pumps, increasing the flow thru the heat emitters giving a lower return temp to the boiler. When you say, "When I disconnect the wiring from the pump on the common piping the heat doesn’t travel through the common piping causing the boiler to over heat and not work at all" What do you mean by 'over heat' and 'not work at all'? I assume that the boiler pump is working and that the boiler water temp has reached the set temp of the boiler (not high limit) and stops firing for a length of time allowing the boiler water to cool down to the re-ignition temp. This can be because there isn't flow or insufficient flow thru the heat emitters which would release the heat energy into the environment returning cooler water to the boiler. Are all your gate valves on the supply/return fully open?
Are you getting sufficient heat from your zones? How many thermostats do you have?
I'm not enamored with the B&G flow control valves. You might try this—Flo-Control Valves are designed with a handle on top that when turned fully counterclock-wise will permit gravity circulation (open up).
Try the stethoscope thing and try and pinpoint the noise.
Look Eric, I'm looking at your piping again (much closer) the piping's a mess. It is all done wrong. I started diagramming it out and there is so many mistakes. It is no wonder that you had no flow thru the zone pumps closely spaced tees when you disconnected the common pump. The flow to the zone pumps was greatly reduced. All the boiler flow went thru the boiler circuit closely spaced tees back to the boiler. 180 deg water out and 180 deg water pumped back into the boiler. The boiler shut down until the boiler differential was reached, when it turned back on. The closely spaced tees for the zone pumps, one after the other, creates a lower supply temp for the following pump because the return water is cooler and mixes with the supply for the next pump, lowering that supply temp. The pumps appear to me to be on the returns of the zone circuit instead of pumping into the zones (the highest pressure loss).
I would re-pipe the boiler bypass and the common manifold. I would do as your diagram shows except move the boiler pump to the input to the boiler (where it is now). I would add balancing valves to the return, too. The only closely spaced tee would be the boiler circuit connection to the distribution circuit. Keep us posted.
thank you @HomerJSmith that’s what our plan is going to be moving forward. Last question if I repipe it how I tried drawing, should I increase that common pipe to 2 inch? (It’s currently 1 1/2). And if done that way would the common piping even need a pump?
The harmonics could be from the burner also. Is it a single stage firing?
Easy enough to turn off the gas when it is firing and see if the noise stops.What size boiler?
The small zones may cause the boiler to short cycle.
You cannot use a compression tank and a Spiro vent., unless you vent the air from the Spiro up to the compression tank,
Living the hydronic dream0 -
Yes, I have dealt with harmonics on the copper heat exchangers. all on horizontal flow models and it has been that the heat exchanger has been internally scaled inside. It does become more pronounced has the loop temperature starts to rise. I would question how you descaled the unit. Did you make sure that the descaling solution is going thru the heat exchanger, not thru the system. You will need roughly 1-2 hours to properly descale. its a hard thing to troubleshoot because if you shut the gas valve off it tends to go away and you cant just shut the boiler pump off as you will flash to steam. I know you said you flushed it, but did you use descaling solution or vinegar? I would do it again.
the only other thing I have found causing harmonics at high decibal level is bad combustion. I normally find those on mod/cons as the air/ratio is out of wack from high fire to low fire. have checked the combustion?
You have enough isolation valves so you could run a descaler in just the boiler and near boiler piping, easily.
I use Hercules Sizzle in copper boilers. Mix it properly, it is safe, even in DHW use.
Tankless water heater descalers are another, out of the bottle citrus acid descaler.
The piping as is is mostly fine. The system is set up as primary/secondary with injection and bypass for boiler condensation protection. This means that bypass valve by the boiler should be somewhat open not fully closed. You want to adjust that so that when the zones are running the return water to the boiler stays above 130F. The closed space Ts (boiler and zones) and such are fine as long as the flow directions are all correct, hard to see that form the picture but you sketch the actual setup including pump directions you can see if it is right.
If you want to re-pipe, your diagram is meant for modcons and won't work* as you'll lose the boiler bypass.
As for the noise, I would vote for cavitation from low system pressure. This would only show up when the boiler is hot.
*you can make it work but you have to watch secondary primary flow rates. Secondoary flow rate has to be well bellow primary. A better option is Fig21 here:
It would be good to know how the heat emitters match up with the boiler output? With low mass emitters like fin tube, return protection is not as much as an issue. And if the boiler is oversized to the radiation, even less so.
Crank up all the zones and see how long it takes to return above 130F. 10 minutes or less is fine.
If you have low temperature heat emitters, RBI shows a thermostatic protection valve as the correct piping.
Regardless of the emitters, If you want absolute boiler protection, adding a thermostatic valve where that ball vale is, is not too involved, as RBI shows. I believe they offer that valve as a kit.
Over sized boilers with low mass and multi small zones tend to lead to short cycling. With just the smallest zone running, how long does the boiler fire?
If the harmonics was from day one, I less suspect scaling.
How hot does the boiler run? Unless you are running above 200F, 10 psi or more should be adequate to prevent cavitation, here is the Grundfos spec for all UP series circs.
I see the new expansion tank, ignore my above concern about the compression tank, it looks to be just decoration at this point.
I think the piping is fine, assuming the boiler circ is sized per RBI recommendation?
@hot_rod the boiler is an rbi 350,000 btu input 2 stage boiler. We tried a lot to get the noise to stop even running it in just single stage. The building uses fin tube, the sanctuary is ran in 1 inch all the way around and the smaller 2 zones are ran in 3/4. The UPS-26 is what rbi’s tech support recommended on this model. As for the descaling I’m not sure what was used I was just told a tech had taken apart the heat exchanger and flushed it. And you are correct the old compression tank was abandonded and they are currently using the bladder style extrol tank. The boiler is set to 180. I think at this point the company has decided to repipe like the above sketch I provided. And the way we are thinking will be the same as the link that @Kaos provided. When I do this work my plan is going to be to turn the boiler so that they have the proper clearances on both sides because currently it does not meet manufacturer specs. I’m slightly concerned the boiler is too large for the application but at this point it would cause some type of short cycling, but it is a church and at this point don’t want to replace the boiler they just want us to make the noise go away.
with the current set up the supply’s and returns are piped correctly but as someone said earlier it’s a better idea to have the pump pumping away and the boiler pump pumping into the boiler like the manual shows. I’m wondering if the common piping is too small at this point and should be upgraded to 2 inch pipe. We’re set up to go back this week and redo the piping set up. I think this current set up could have worked if the common piping loop was longer and potentially run through the entire building.
The installation manual answers most of your questions. 1-1/2" piping at the boiler is adequate up to the 400K unit
You could run that boiler out to a 30∆ which would require 19 gpm. Well within that circulators capacity. Very low pressure drop thru that boiler even at a 20∆, 28 gpm flow
Regardless if you pump into or out of the boiler the gpm will be the same. With the short piping loop I suspect you are flowing over 20 gpm on speed 3. I'd adjust the boiler pump speed based on the delta across the boiler. Probably end up between 20 and 30 ∆
Looks to me like you are pumping into the boiler, unless this pump is backwards?
The boiler pump is referencing the PONPC, the expansion tank connection, via the closely spaced tees (hydraulic separation).
You could move the tank right at the boiler pump, then all that pumps ∆P shows up in the boiler. With caution as high head circs can sometimes cause the relief to seep if the dynamic pressure approaches 30 psi. Currently the boiler circ "sees" the expansion tank through the close tees. I doubt the change would change the boilers operating pressure much.
The advice above to boost the static fill to say 20 psi, does the noise stop? Then high temperature low pressure could be inducing some cavitation. Although pumps don't last long under that condition. Could be the impeller has been chewed away in the boiler circ. Easy enough to pull and check the boiler circ impeller.
180F at 10- 12 psi is not a cavitation risk at all. Again, a gauge on the boiler will confirm the dynamic (flowing) pressure.
Confirm that you have an accurate pressure gauge. A gauge in the boiler will show you static fill and what the pressure increases to when the boiler circ runs. Easy enough to remove the relief, put in a tee and add a 30 psi gauge to confirm. Or on a boiler drain.
Do some more troubleshooting before you breakout the sawzall and spend $$ and not arrive at a fix.
Add up the fin tube lengths to arrive at the btu that can actually be delivered, regardless of how large the boiler is. I'd be curious what the smallest zone come up at.
I don't think the boiler could have been flushed properly without low point drains on the boiler. You need to add a low point drain on the supply and return after the isolation valves. They should have been installed at installation anyway. Then you can descale the heat exchanger the correct way.
Copper fin tube boilers are basically a flat copper fin coil, not unlike an AC coil. Two headers with 5/8" finned copper tube going across.
There really isn't a low point. Here is the RBI he has. Generally with the correct pump, as he has, the flow velocity keeps them pretty clean. 20- 25 gpm flowing thru 8 or so short 5/8" copper tubes.
DHW copper tube boilers tend to scale as they see fresh water constantly. Unless this system has a leak or gets flushed often, the water hasn't changed too much.
Odd is it made the noise from day one?
They don't usually ship from the factory with scaled coils :)
i agree but i'm only going by experience. Certain RBI boilers do come with low point drains installed at the lower header on vertical copper vertical heat exchangers. The Futera line of boilers do have them for just this purpose. i say install tee's instead of 90's before tying into the header. it's either that or you have to get creative and remove wells and install drawoffs.
I also must have missed that he said out of the box this has been happening. it is normally the domestic hot water boilers that scale and lime but my last two were on a closed loop water source heat pump system. those air handlers don't last long so the system is constantly being opened up for repairs introducing fresh water.
Any possibility you are low on water?? We had a situation with this exact type of boiler earlier this winter that whenever the burners where on there was a very strange high pitch noise that could be heard throughout the home. The gauge showed 15psi which we found was stuck when we drained the system.
1 -
No we changed the boiler T&P gauge because it was leaking when we got there. Also above the boiler pump there is a ball valve with a drain to force bleed and have had separate 30 psi gauges on there to make sure pressure weren’t off. I’m going back Friday and I’m going to try moving the expansion tank first to see if helps and they still doesn’t work we’re going to repipe how I had in my sketch at the beginning.
Repiping might not fix the problem. I would root cause the issue and fix from there, throwing more pipe at the problem won't help.
While there, fire the boiler so it gets up to temp where it starts to sing. Turn off all pumps and turn each pump on one at a time to see which loop is creating the noise. If you isolate to a single pump, try adjusting the flow on the pump, either by changing its speed or by throttling the outlet, to see if it effects the noise.
Once you know the problem, it might be a simple fix.
1