Triangle Tube Solo 110 not igniting...Error E-02 and or E-04
Hello,
I'm trying to get my Solo 110 back up and running. We came home from vacation to no hot water or radiant floor heat. Saw a large puddle under the unit and the E-04 error code. I discovered that the LWCO was faulty and leaking water. I replaced the LWCO, but when I attempted to power the unit back on, the LED screen was blank, and it was just running the blower. It would not run through the ignition process. I replaced the main system board. After the board replacement, it would start and run through the ignition process, but would not ignite. I noticed that the ground cable to the ignitor was corroded, so I also replaced the bad section of ground cable as well as the ignitor and the ignitor cable. Still no ignition. It runs through the process 5 times and either ends with the E-02 or E-04 code. There is no visible flame in the sight glass during the ignition process. Desperately looking for some recommendations as I am unable to locate a contractor.
Rob
  • Ironman
    Ironman Posts: 7,975
    You need to determine if you’re actually getting a spark at the igniter.
    There’s a recall on some model and year Triangle Tubes. You should check to see if yours is one.
    Bob Boan
  • tim smith
    tim smith Posts: 2,935
    is that a PS110 or PT110. What p/n was the board and the igniter? When is the last time it was pulled apart and cleaned?
  • tim smith
    Did someone re enter the parameters for your system? All info here will hopefullly shed light on whats happening.
    109A_5 Posts: 4,759
    edited April 2025
