Steam traps - do not touch?

Sawboss41
Sawboss41 Member Posts: 3

ASSISTANCE WITH IDENTIFYING THESE PLEASE.

Dan's video from 2024 appears to provide much needed insight. I am the estimator for hydronic and ac systems. Steam is not my usual subject. I am learning but this one is something i haven't seen. Assistance with positive id of these components is what i seek.

Comments

  • Sawboss41
    Sawboss41 Member Posts: 3
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,893

    Oh boy...You need to purchase The Lost art of Steam Heating & We got steam Heat…Mad Dog

    mattmia2
  • delcrossv
    delcrossv Member Posts: 2,050
    edited March 20

    Looks like an intact Hoffman vapor system. The black thing is a boiler return trap, the blue thing with the vent on it is a vent trap.

    If the system is working, leave them be.

    Ditto on @Mad Dog_2 's suggestion.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,893

    If you don't know The Steam, you'll take a terrible beating on this job. Where are you located? Mad Dog

    delcrossvLong Beach Ed
  • Steamhead
    Steamhead Member Posts: 17,678

    I think that's a Webster Type R system. And the green vent on the vent trap is too small- change it to a Gorton #2.

    These are not "steam traps" in the usual sense. Get the book- it's in chapter 15.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    delcrossvLong Beach EdMad Dog_2
  • delcrossv
    delcrossv Member Posts: 2,050
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    Mad Dog_2
  • delcrossv
    delcrossv Member Posts: 2,050
    edited March 20

    Choose between 2 pick the wrong one. Story of my life.

    In any event, they're not "traps " in the conventional sense.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    mattmia2Mad Dog_2
  • Jamie Hall
    Jamie Hall Member Posts: 25,826

    Not Hoffman. Webster. As noted, it's in The Lost Art — which you very definitely need.

    In the meantime until it comes, check the system operating pressure. The cutout on whatever pressure control you have must not be more than 8 ounces per square inch — half a pound. Cutin should be half that — 4 ounces.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 12,191

    It is a vapor system, it needs to operate at very low pressures to work properly. That is much easier if you are very carful about not oversizing the boiler. You will have a bad time if you don't size it based on the connected radiation. I would reduce the baked in pickup factor and think about even figuring the EDR at filling maybe 80%-90% of the emitter because if it has the correct vapor valves on the radiator that is what they should be set to.

    You should really find someone that knows steam to help learn on this.

    delcrossvMad Dog_2
  • delcrossv
    delcrossv Member Posts: 2,050

    Or measured EDR with no pickup.

    And a vaporstat.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    Mad Dog_2
  • mattmia2
    mattmia2 Member Posts: 12,191

    It does look like it has a vaporstat but i can't tell if that is indeed a vaporstat or just a pressuretrol or modulating control in the same case from the picture.

    delcrossv
  • delcrossv
    delcrossv Member Posts: 2,050
    edited March 20

    Looks like a mercury vaporstat to me. Seems like there's a p-trol below as a safety.

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • Jamie Hall
    Jamie Hall Member Posts: 25,826

    Ah ha! Yes it does look like a mercury switch vapourstat! Hooray! I can't tell from the picture what it's set to, though.

    Whatever else you do, don't lose that vapoustat. They last forever and are much more reliable than the newer ones. They do need to be level, though…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2delcrossvLong Beach EdMad Dog_2
  • WilliamGwiazdowski
    WilliamGwiazdowski Member Posts: 24

    I have essentially the same equipment in my basement. 1934 colonial. I also have Webster radiator valves as well as Webster radiator traps

    delcrossvLong Beach EdMad Dog_2Intplm.
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,893

    The Ol' cast iron Ham....Mad Dog

    mattmia2
  • Sawboss41
    Sawboss41 Member Posts: 3

    Thank you all for your input.

    Turns out my WM vendor knows Dan from his days w BG and we reviewed Dan's video post from fall of 2024.

    WM still makes all the parts for the EGH85. Will be a pull and replace and leave the dead men's design completely in tact.

    Another problem solved thanks to DH and heatinghelp.com

    Intplm.Long Beach EddelcrossvHeatingHelp.com
  • mattmia2
    mattmia2 Member Posts: 12,191
    edited March 22

    Still need to do the edr calculations to make sure the last person did it right. The fact that people with a lot of experience with these specific systems are telling you the vent is too small are at best brining that in to question.

    Long Beach Ed
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,719

    Why are you replacing this boiler?

    mattmia2Mad Dog_2delcrossv