Hi Everyone,

I’ve recently finished our new home build and have been experiencing issues with water pressure. I’m wondering if there’s more for me to do before calling in outside help.

Boiler: LAARS Combi Boiler 140

Propane

Heat set to 125*F

Issues: Low water pressure when showering. Water seems hot enough, just feels like more of a heavy rainfall than a shower.

I’ve adjusted the mixing valve already but I’m wondering if there’s more balancing to be done. Cold water pressure is fine, and sinks have decent hot water pressure.

It is a 3/4” supply to 1/2” branches. Upstairs shower is the one in question. Also, upstairs sink hot water takes very long to get hot.


Any help is greatly appreciated!


-Evan

IMG_3620.jpeg IMG_3621.jpeg

Comments

  • Mad Dog_2
    Mad Dog_2 Posts: 8,724

    The intake screen could be clogged on the unit. Check that next. Mad Dog

    Ironman
  • Ironman
    Ironman Posts: 7,942

    The screen on the water inlet may be clogged or the internal plate heat exchanger may be fouled from hard water.

    I can’t tell for certain from your pictures, but it doesn’t appear that there are any valves provided for de-scaling the heat exchanger.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    Mad Dog_2
  • hot_rod
    hot_rod Posts: 28,204

    If it is brand new, I doubt you have scaling issues. Yet!

    I don't know if that model mix valve has screens on H &C the union versions do. Check the installation manual. That is another common "choke" point, at the mix valve.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • kcopp
    kcopp Posts: 4,714

    On another note why didnt they run a combustion air intake? That would be best practice especially where the boiler is located in the laundry room…

    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Posts: 8,724

    Kcopp..

    C'mon..thats extra...ha ha... Mad Dog

    kcopp
  • psb75
    psb75 Posts: 1,162

    Check any screens that may be in the anti-scald/mixing valve.