Is my pump too big. Circulator velocity noise.

Hello all. Spring is almost upon us……
I have a tenant apartment that has roughly about 50 feet of Baseboard (supply and return are in 1/2 inch copper) that has a Taco 007E. The tenants are complaining of velocity noise and keeping them up at night. I do faintly hear it. I believe the apartment needs about 30K btu's. There are no complaints about heat just the noise.
Would it beneficial to change the Taco 007E it out for a smaller pump? I don't understand pump curves and would appreciate any guidance.
Comments
-
The velocity in 1/2" is only about 4 ft/sec with the 007e so it is unlikely they are listening to "velocity noise". When is the last time the zone was purged?
0 -
Are there multiple zone valves on the system?
Once you get to 5fps feet per second velocity you can start to hear some noise from the flow'
In 1/2" copper M that would be 4 gpm or more.
Is there a way to adjust the speed on that model?
It looks like it is designed for multi zone valves and adjusts on a delta P condition?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
It's highly unlikely that the noise is velocity related, unless there is some sort of orifice or valve further reducing the diameter and therefore raising the velocity… Is it all 1/2" element as well or just the supply and return piping to the element?
0 -
I would first attempt to purge it as it takes only 10 minutes. The tenants might be listening to air in the line.
Also, if you have a ball valve anywhere along the flowpath, close it down to about 30 degrees (90 being fully open). This will absolutely slow the flow rate and allow you to determine if they are listening to velocity noise.
0 -
He cannot get to 4 GPM on 1/2" copper (estimated 75 ft EL) with a 10ft limit of the pump.
Almost impossible to be velocity noise at 3.5 GPM……….which is the maximum possible flow rate.
0 -
80' fin tube at 500 btu/ft = 40,000 btu/hr. If in fact that is what the load is, 4 gpm at a 20∆, not realistic with all 1/2" tube?
1/2" copper recommended max. flow in most hydronic design guides is 1.5 gpm
If you have 80' of fin tube plus piping and ells, call it 120' EL
If you are only flowing 1.5 gpm, at 20∆ then you are moving 15,000 btu/hr.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Is the IFC installed? 007E comes with one in the box. If it has a Flowvalve, you don't need an IFC.
0 -
You cannot flow 3 GPM through 1/2"M with a 007e at 120 EL. Not even close.
The load is irrelevant to the discussion. A higher flow rate (possibly 2.5) simply results in a smaller DT.
Clearly, he does not have 80' of element. That's ridiculous.
0 -
regardless if it is 80 or 120’ EL the pump is not causing excessive velocity
A valve that is partially opened can cause a hissing noise, any tight restriction in the piping actually. Maybe an isolation valve that didn’t open fully?
If the home maintains temperature on the coldest days, you have enough fin tube, regardless of the actual gpm
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
here is a recording of the noise. The other pump is silent.
0 -
Sure doesn't sound like a velocity noise, but I'll ask for a third time if there are any orifices or valves that may be partially restricting the flow? This could potentially cause a high velocity area and therefore some noise. The noise in the clip sounds more like a bearing than anything, but it's hard to say without being there to listen exactly where the noise is originating from.
0 -
pumps are cheap
Change it and see if the noise goes away0 -
So, to quickly answer your question about a smaller circ, the 007e is a variable speed delta P circ, so it is running slower based upon the system that is connected to it such as yours with 1/2".
There are times I hear harmonics in the pipes in a house and sometimes the quickest and easiest fix is adding a pipe clamp on a long run that you can see and rteach
Dave Holdorf
Technical Training Manager - East
Taco, Inc
1
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 106 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 104 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 952 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements