I would want protect a prototype water filter design from exposure to "water hammer".
The filters are exposed to many quick closing solenoid valves throughout the commercial building.
Instead of using a standard "hammer arrester" , my question is, if I had an existing
conventional "water expansion tank" in the system already, wouldn't that serve just as well an arrester as well?
….. thoughts on this?
Thanks!
Comments
-
-
-
Think of the water hammer as a shock wave that travels at the speed of sound from the closing valve upstream through the piping system. Depending on where the valve is, the shock wave could reach your water filter before it reaches the expansion tank. It's like saying you have a bulletproof vest, but it's back in the car. If you're not wearing the vest when someone shoots you, it's not much help.
That's why the small water hammer arrestors are helpful, because you can put them right at the point where the shock wave is being created, and that dampens the shock right there instead of letting it propagate through your pipes until it finds a weak point to damage. Or, if there are multiple sources of shock that you can't control, you put the arrestor upstream of the thing you're trying to protect.
2 -
Hello Rick,
What you are saying is your hot and cold water feeders do not have copper risers that hold an air slug at the end of your triple loaders to act as an accumulator to accept the system pressure surges when a solenoid valve closes on one of your washing machines is that correct?
You do not need a pipeline hammer arrestor.
A much simpler solution for you is to just reduce the system inlet pressure after the water meter to 30 P.S.I.G. and be done with it, your washing machine solenoid valves and piping will appreciate it as they do not require 80 P.S.I.G. to operate and you will continue to have adequate flow.
Reducing the system inlet pressure to 30 P.S.I.G. will also eliminate the filter cartridges from collapsing as well.
1 -
" I would want protect a prototype water filter design from exposure to "water hammer". "
"Prototype" is this to be eventually to be sold to the public ?
I would venture to say if the prototype can't handle "Water Hammer" it is already a failure.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Well …….. the schedule 80 PVC (pressure) I built the prototype with was rated for 320 PSI working pressure. I'm sure that would be fine to use (cold water application).
I was thinking of using a schedule 40 PVC (pressure) instead as its rated 220 PSI at 73 degrees F.
My concern was of not max working pressure, but the peak pressure spikes.
I think LEON had a good suggestion, regulate down to 40 PSI to quell down the large spikes.
0 -
What Jesmed says. Snubbers at valves. They have to be periodically recharged. Returning to OP's queries. Expansion tanks do help. Especially multiple ones along line. Supposedly a no no? Motorized valves are gentler than solenoid.
0 -
-
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 424 Carbon Monoxide Awareness
- 108 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 954 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements