Forced Air furnace sizing
I did an in depth heat load calc. It said that without wall insulation that I need a 100k btu furnace for my house. But once I add insulation I’d only need a 70k Btu furnace. I plan on adding insulation next year to the walls. Which size furnace would be worth getting?
Comments
-
is the house built? If so, use the fuel usage.0 -
-
I’d only need a 70k Btu furnace.
This is not a difficult question.
0 -
Total heat load seems high. Also, a 30K BTU load just for uninsulated walls seems unbelievably high.
If 70K BTU is the actual load at design then consider an 80K BTU modulating furnace.
My bet is that the load after insulating the walls (with attention to detail) is low enough where a 60K BTU modulating furnace will get the job done without issue.
Existing ductwork is usually too restrictive for larger equipment, so “downsizing” of equipment is super helpful in this respect (and others).Swinging hammers and fitting pipe…bringing the dream to life
1 -
Yes it's built. Here's the info I gathered based on that article:
Dec 21st to Jan 22nd usage: 600CCF = 623 Therms based on an online calculator
Boiler Efficiency: 82.2%
65F Heating degree days: 1,308.2
60F Heating degree days: 1,143.2
Math:
623 * 82.2% * 100,000 = 51,210,600 BTU
60F:
51,210,600 BTU / 1,143.2 degree days = 44,796 BTU per degree-day
44,796 BTU per degree-day / 24 hours * 45F = 83,991 BTU/HR
ASHRAE sizing factor 1.4 x 83,991 BTU/HR = 117,587 BTU/HR
65F:
51,210,600 BTU / 1,308.2 degree days = 39,145 BTU per degree-day
39,145 BTU per degree-day / 24 hours * 45F = 73,397 BTU/HR
ASHRAE sizing factor 1.4 x 73,397 BTU/HR = 102,756 BTU/HR
Is my math correct? So you think I should get something around 100,000 BTU's still? Even though I am insulating walls soon?
0 -
Northeast PA and 2,500 SQFT
0 -
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 106 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 104 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 952 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements