New vaporstat

2»

Comments

  • mattmia2
    mattmia2 Member Posts: 12,280

    ideally but it is a product there isn't a lot of demand for so i don't think it quite got redesigned correctly when they stopped making them with mercury switches

  • KJB
    KJB Member Posts: 83

    I still stand by my previous statement. So since I got the boiler back up and running, now I can't build any pressure on the boiler. Been running for about 25 minutes and not 1 oz of pressure

  • KJB
    KJB Member Posts: 83

    So it finally built up pressure and cut out right where it is set…about 4 oz. I have the diff set at 2, but the boiler will not restart until all the pressure is off the system and then a little time beyond that before I get a restart. Is there a way to adjust only the diff?

  • mattmia2
    mattmia2 Member Posts: 12,280

    if the radiation is matched to the boiler it will never build pressure that is the ideal situation. since you were getting steam in the returns, maybe from a cold start there is no steam in the returns yet and some stuff is getting a chance to vent and heat that doesn't on an already warm system.

  • KJB
    KJB Member Posts: 83

    I think I'm having venting issues. I can hear it vent sometimes when theres pressure on the system. I've got 2 new gorton #2 vents ready to go on, but didn't want to risk ruining them till I get the blow by of the 2 water seals fixed.

  • 109A_5
    109A_5 Member Posts: 2,306

    Well I can't say I have been following you whole saga, but if it makes you feel any better my boiler pressure never exceeds:

    2" Water Column

    1.156 Oz

    0.072 PSI

    No pressure limiting controls needed.

    If you truly expect to build pressure (the Boiler size exceeds the EDR) you may now have a leak somewhere.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • neilc
    neilc Member Posts: 3,017
    edited March 3

    " Is there a way to adjust only the diff? "

    well yeah, dial the left scale(differential) down to 1, (I think) picture?

    and push the cut out up to 5, an oz or 2 doesn't matter

    known to beat dead horses
  • neilc
    neilc Member Posts: 3,017

    just up enough so you're off the floor

    known to beat dead horses
  • KJB
    KJB Member Posts: 83

    I meant fine tuning. Like the screw in the back for fine tuning the main pressure

  • 109A_5
    109A_5 Member Posts: 2,306

    Steam won't bother the Gortons they are made to close with the presents of steam.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • KJB
    KJB Member Posts: 83

    I adjusted the main to 6 oz and the diff to 2 oz, and it still won't restart until the pressure is off the boiler

  • KJB
    KJB Member Posts: 83

    So it would take approx 22 minutes to go from a hot start, to cutout, to cut in and then to cut out again. Does that sound like the right amount of time?

  • KJB
    KJB Member Posts: 83

    Even with 2 water seals leaking through? But I guess there is one on the main steam lineal, and that's around 160°

  • 109A_5
    109A_5 Member Posts: 2,306

    You may need a more stable setup to calibrate and and verify adjustment and functionality of the vaporstat, like in the video.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • neilc
    neilc Member Posts: 3,017

    but it restarts, correct?

    what gage scale are you trying to track this on?

    oz's are hard to see

    known to beat dead horses
  • KJB
    KJB Member Posts: 83

    It initiates a restart approx 30 seconds after the gauge reads 0. The gauge is a 0-3 psi gauge. Only 2 days old

  • KJB
    KJB Member Posts: 83

    Just set the main to 6 oz and the diff to 1 oz and it still will not initiate a restart until there is no pressure on the boiler and about 30 seconds after that

  • mattmia2
    mattmia2 Member Posts: 12,280
    edited March 3

    the return trap on your radiator may be hot from steam getting in to the return somewhere else and flowing back to that radiator

    the steam in the return will close the vent and stop all venting at that point. anything that hasn't vented when that happens won't heat.

    (i didn't read your other thread with 100 comments)

  • KJB
    KJB Member Posts: 83

    There are 2 radiators that are the only ones that the water seals are 130° ish. Every other one is ambient temp

  • mattmia2
    mattmia2 Member Posts: 12,280

    it could be a crossover trap if that system has them or a drip that isn't below the water line too

  • 109A_5
    109A_5 Member Posts: 2,306

    In the short term the inserting an orifice plate that mattmia2 mentioned may be the quickest way the get those radiators under control by limiting the amount of steam entering them.

    You may find this interesting

    https://youtu.be/8KisKrAaywQ

    Mouat water seal movie

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • KJB
    KJB Member Posts: 83

    I watched that video. Pretty cool learning about this stuff. Thanks.

  • 109A_5
    109A_5 Member Posts: 2,306

    You may want to have a conversation with PMJ, or at least read some of his posts about his Mouat system. I believe he does not use a vaporstat to limit the pressure cycle to cycle. Ultimately you may choose not to use his techniques but you should know the options.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System