Oil Boiler Small Water Streaks on Cast Iron
Had my yearly tuneup and when the tec removed the side paneling on the boiler he noticed small, fine, water marks on the cast iron. The tec last year also mentioned these to me. They didn't look any different to me from year to year. Last year's guy didn't seem to think much of it in terms of an emergency. Does anyone have any opinions on this situation? Cast Iron oil boiler is about 22 years old.
  • Grallert
    Grallert Posts: 1,237
    It could be a few things. Are you losing water? You can tell if you are by shutting the water supply to the boiler off. If you have steam the level in the gauge glass remain at a set or marked point. If you have circulating hot water the pressure should never drop below 10 or 12 psi or so.
  • Thanks for responding. No, I am not losing water.
    ethicalpaul Posts: 9,076
    Try to get a picture next year 🙂
  • Grallert
    I'd venture to say, unless there's been some big changes to the system, after 22 years there nothing to worry about. But yes if you could get some pictures we would be more sure.
  • Steam or water? Would highly doubt it's something to be concerned about
  • I can take the side off myself, will try for a pic tonight. it's water
  • mikedo
    mikedo Posts: 302
    is it a burnham cast iron boiler ?
    Check your return water temp. It should get above 130 within 15-20 min from a cold start.
    Sounds like condensation running down the boiler maybe from the clean out covers,
  • yes, It is a Burnham cast iron boiler.
  • attaching a zoomed in picture. it's between the 3rd and 4th sections.
