DIRECTION OF STEAM TRAVEL

My recently installed steam boiler has been piped with the steam feed from the boiler to the header feeding away from the equalizer then to the mains. Should the steam direction go toward the equalizer to avoid blocking condensate from returning? I am having alot of steam hammer! Thanks; JB
Comments
-
The manufacture's instructions is pretty specific on the near boiler piping. Post a photo of the piping from far enough back so we can see the pipes from floor to ceiling. at least 3 different sides
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
3 -
Ed's advice above is best, of course.
In good piping practice, the steam risers come off the boiler and enter the header. After a 12 inch nipple, the takeoffs for each main are connected to the header, with all or all but the last preferably at 45-degrees to the floor. Then the equalizer departs from the header with no horizontal reduction or with an eccentric fitting.
…unless otherwise specified by the manufacturer or a qualified fitter.
When we deviate from recommended or good practice, we may encounter problems. We may not. Compromises may be required and they have to be made with knowledge and experience and with a complete understanding of the entire system.
If you post a few pictures, someone here will diagnose your hammering problem I'm sure.
0 -
An example.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Here are some pics of the boiler piping.
The steam from the riser is not 6" away from the equalizer, and I think that some water from it is making the steam wet.
0 -
This is the piping for a Weil McLain PEG 45 steam boiler; 2nd attempt by the contractor, and still making a lot of noise, and not heating right! Any ideas?
0 -
-
WoW, how is this stuff that tough ??? The boiler's riser needs to go to where the cap is on that end of the header, the opposite end from the equalizer. How is the header pitched ?
Steam, condensate and any carryover need to be going in the same direction so when they separate out in the header they don't have to reverse directions, the steam goes up into the system and carryover / condensate goes into the equalizer.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
WoW, how is this stuff that tough ???
Apparently, you need a college degree to avail yourself of the installation manual that is packaged WITH THE BOILER.
And, the diagram doesn't cut it for larger boilers.
0 -
-
-
THANK YOU ONE AND ALL FOR PUTTING MY MIND AT EASE! I paid good money for a heat/plumbing contractor to do this piping job! By reading the manual that came with the boiler, I KNEW that it did not look right! No wonder I have hammering each time the boiler fires up, as I believe water is being drawn up into the mains from the equalizer. Now I have to TRY to get these same guys come back for the THIRD time to do this the right way! So, the steam flow should go toward the equalizer, not away from it. Should BOTH risers be used for dryer steam( mine has 2 plugs in the boiler top)? They used only one( prob to save cost)!
0 -
-
Should BOTH risers be used for dryer steam( mine has 2 plugs in the boiler top)? They used only one( prob to save cost)!
The manual for the EG-45 shows that it is acceptable with a single 2" riser. No contractor would use two unless the customer demanded it. It is small enough to work acceptably well with a single 2" riser.
0 -
All else being equal and, given a large enough header, one may be sufficient, but two is better. IMHO.
Give us your BTUs and we can give a definite answer.
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
" Weil McLain PEG 45 steam boiler "
Minimum piping.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Interesting.
I found this for the EG:
Only a single 2" riser………………………
0 -
There is a difference between the series 4 and series 5
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Apparently, somebody wised up!!
0 -
One 2 1/2" riser is sufficient, 2 2" is better (19ft/s double vs 27ft/s single). The 27ft/s is not bad so wouldn't worry about that too much compared to just getting the configuration right. I'm not good at identifying the pipe sizes from the photos like many are here. What size did they use for the riser and header? If the OD is 2.375" it is 2", if 2.875" it is 2 1/2" and if 3.5" it is 3". I can't see the mains in the photos but I do see reducers on the rise to the mains. Unless the mains are smaller than the riser and header I would get rid of the reducers.
1 -
After spending a bit of time with the photos, I'm guessing that the riser and the header are both 3". He reduces both of the mains down to 2" with reducing couplings or bushings.
If correct, he has a fairly simple solution:
Remove the cap on the right end of the header and pipe the riser directly to that point. Eliminate the current horizontal piping from the riser to the left side of the header and plug the tee in the header.
All problems go away.
0 -
The riser and header are all 2-1/2", and it is reduced on the vertical takeoffs to 1-1/2". The mains are both 1-1/2". He reduced both to match the size of the mains. So you agree that with this current piping, water is being drawn up into the steam flow from equalizer, and condensate, which cannot return due to the steam direction being reversed?
0 -
You can get away with the 2.5 piping. Just run the 2.5" riser as high as possible (36" or more), do a U turn near the ceiling, and come down to the header and enter the header where the cap is currently located.
That's it.
0 -
Will do! Just making the steam go in the opposite direction from the way it goes currently! Thanks for the advice; you have all been very helpful!
0 -
-
I can't follow this piping from such close shots. I took the time to put the pieces together so I could see how bad this is. Here is what I have come up with. Compare it to the Weil McLain illustration 18 that i modified for 2 main risers.
When compared to the instructions, (with modification for 2 main risers) there are too many extra fittings and pipes, along with possible incorrect pitch that can cause the header to hold condensate from returning to the equalizer back the the boiler return, and even pushing water back up into the main. Now that will bang like crazy
I think @109A_5 illustrates the easiest fix for your contractor. Just as long as the Header is properly pitched towards the Equalizer, and the Hartford loop is properly constructed. that 24" dimension can be more than 24" to get dryer steam. The higher the better.
Let your contractor look at this set of diagrams so it is more better clearer. Picture being worth a thousand words … and all.
The close nipple on the Hartford loop is important. The longer that pipe is the more noise it can make.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
-
Tell the contractor that you want 36" above the waterline instead of the 24" shown in the diagram. Higher is better. 24" is bare minimum.
0 -
No,they neglected to put in a Hartford ĺoop; along with the glaring other mistakes! Amazing that any steam is reaching any rads!
0 -
Thanks for the drawings and solutions! Should I also have him add two 45 degree fittings at the base of the takeoffs also?
0 -
Considering the piping, I would not be surprised if your pressuretrol is set to 5 psi or more. It should be set to cut out at 1.5 psi and back in at .5 psi
0 -
The main takeoffs are fine as they are. No need to do anything to them.
0 -
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 107 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 954 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements