Question about B-vent termination and CO

We have a three story duplex right outside Philadelphia thats heated by a gas boiler and convectors. Separate gas water heater and gas boiler (Williamson GWA 140N-S, 140K BTU) exhaust into the same flue in the basement laundry room, which is run outside through the basement wall and up the back of the house through 6” B-vent before terminating roughly 6 feet from the third floor bedroom window. The bedroom window in question is in a shed dormer on the back of the house.

I’ve attached a photo of the vent running up the exterior wall, and a link to a video from the 3rd floor bedroom window showing the vent in action.

I’ve never liked this setup as I suspect the system is exhausting too close to the window and/or not high enough above the shed dormer roof/main roof ridge. Depending on the wind, exhaust gets blown against the window and/or the shed dormer. I occasionally get low level CO readings up in that room using a low-level detector. I’ve taken readings in the boiler room and no CO is detected.

This setup, while ugly and probably not ideal for other reasons, is very common in this area, as when these homes were built in the 20s and 30s they all featured central plant steam heat piped into the house directly. They were all laid out to reflect that they supposedly would never need boilers or furnaces. Thus the chimney is on the other end of the basement from the laundry room where the boiler is located. These homes all had to be retrofitted with exterior metal flues in the 70s when the steam plant company abandoned operations.

What can we do about this? Extend the b-vent higher with roof brackets? Power venting?

Thanks in advance.

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,118
    edited February 19

    First of all, that B-vent does not meet code requirements. it is obvious that there was no municipal permit issued for this install, or the local inspector is clueless.

    Secong big No No is that B vent should not be exposed to the outdoor temperature for the entire vertical distance. And there are several other things that are wrong. I will make a diagram of what might be a better design.

    BRB

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    FrankMaraschinotcassano87Mad Dog_2SuperTech
  • FrankMaraschino
    FrankMaraschino Member Posts: 3

    Yeah, my understanding from talking with local building and code people is that when the old steam plant abruptly ended operations in the early 70s suddenly tens of thousands of people in this area were without heat and the local utility company and the state utility commission had to scramble. So they slapped these things up fast and they’ve basically been grandfathered in/ignored even though no one likes them.

    Anyway, thank you very much for your time and feedback. Let me know if I can provide any additional information, photos, etc.

    Mad Dog_2
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,118
    edited February 19

    Here is the lowest cost fix

    Here is an instruction guide for one manufacturer of B-vent. all the others are about the same. The diagram on page 5 figure 11 shows you basically what I have drawn for you. H&C B-Vent. the reason this has worked for so many years is the higher exhaust of a steam boiler, But when you get extreme cold or if the wind is in a certain direction, you can have down drafts that can put Carbon Monoxide inside your home, even if the windows are closed. The top of the vent MUST be at least 2 ft above any obstruction within 10 feet. The peak of your roof might be too close so you need to at least 2 ft higher than that. Just that pipe may not have enough support above the roof line to get a pipe up that high so the enclosure should be affixed to the building in such a way that it will support that long vent pipe above the roof line.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    FrankMaraschino
  • FrankMaraschino
    FrankMaraschino Member Posts: 3
    edited February 20

    I appreciate you taking the time to diagram that out. You’re proposing we build another chimney — albeit an insulated one — on the back of the house, basically, which makes sense. 

    I’m visualizing how that might be done. Unfortunately the house has shallow eaves; the overhang is shallower than the 6” B-vent is wide, so running the whole thing through the roof isn’t feasible. Seems like we’d have to bump the new “chimney” out to clear the gutters entirely and make it tall enough to terminate above the main roof ridge. 

    Ugh.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,118
    edited February 20

    Same vent pipe with a plywood enclosure (like T111 siding) that has 1.5" foam sheathing glued inside it to form an insulated enclosure for the B-vent.  A decent carpenter can notch out the eaves so that you do not need to have so many 90° turns. Then make a chimney covering out of plywood to support and insulate some of the B vent above the roof line until you get high enough to top the B vent chimney above the peak of your roof. 

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • hot_rod
    hot_rod Member Posts: 24,423

    building a chase and sealing it to a brick building will be a bit of a task

    A power vent out the side might be an option if you can get clearances from openings and windows

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Long Beach Ed