supply line

Bob_115
Bob_115 Member Posts: 40

will a 3/8 copper line supply enough gas for a 120000 btu tankless water heater?

Comments

  • pecmsg
    pecmsg Member Posts: 5,670

    what gas?

    What pressure?

    How many bends?

    mattmia2
  • mattmia2
    mattmia2 Member Posts: 11,601
    edited February 7

    Propane maybe depending on the answers to @pecmsg 's questions , methane, no.

  • yellowdog
    yellowdog Member Posts: 242

    Absolutely not at 11" for propane. 1/2" copper wouldn't even do it at any length.