supply line
![Bob_115](https://secure.gravatar.com/avatar/60f8600465fb250c66ee79c1c80bbc32/?default=https%3A%2F%2Fvanillicon.com%2Fd4628f9b3384946711c3ee7fb1b09199_200.png&rating=g&size=200)
Bob_115
Member Posts: 40
will a 3/8 copper line supply enough gas for a 120000 btu tankless water heater?
0
Comments
-
-
Absolutely not at 11" for propane. 1/2" copper wouldn't even do it at any length.