Pin Valves

I'm starting to see more and more manifold pin valves seize up; the ones with manifold actuators that open and close the valves millions of times. These came off a Rehau manifold we installed 23 years ago. As you can see, some were still working, but I replaced them all; cheap insurance.

8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab

Comments

  • hot_rod
    hot_rod Member Posts: 24,332

    Fluid it too dirty, see the black build up on the pin stems. Running a hydronic cleaner would bring them back to a clean brass and stainless look.

    Once they get hard to push, you can blow the top off the actuators.

    Loosen that small nut on top and drop the pin out. Soak it all in a good cleaner, or run them through the dishwasher, they could be re-usable. Lube the pin with some silicone grease.

    Here is my system fluid after running a cleaner, adding DI water, and some Adey MC-1 inhibitor. I'm hoping it stays like this for years.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,131

    Does glycol cause that or is it a water only system?