Bryant furnace

creger.robert
creger.robert Member Posts: 58

Model 350mav048100adka

natural gas-tripping on roll out switch on burner box

condensate leaking around bottom of inducer assembly area inside furnace

gas pressure is normal-flames look ok no rolling or anything

Comments

  • mattmia2
    mattmia2 Member Posts: 11,860

    bad heat exchanger?

  • pecmsg
    pecmsg Member Posts: 5,742

    gas pressure

    Combustion analysis numbers

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,198
    edited February 4

    When a rollout switch trips it is an indication that you have a blockage somewhere between the burner flame and the end of the exhaust pipe. That could be the combustion fan is not turning as fast as it should, or there could be a bird's nest in the vent pipe (intake or exhaust) the secondary heat exchanger may be blocked with carbon or calcium carbonate buildup. There may also be a blockage in one of the main burner heat exchanger primary pipes. Look for the blockage and clear it, to get the rollout switches to stop doing their job.

    The condensate leak may mean that there is water in the secondary heat exchanger that is not draining. Check the condensate trap for a blockage.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • delcrossv
    delcrossv Member Posts: 1,946
    edited February 4

    Bryant had a class action suit where their HX's would rust closed. Tripping rollout is indicative.

    You may get a HX for free.

    https://forum.heatinghelp.com/discussion/127381/bryant-90-lawsuit