Bryant furnace
Model 350mav048100adka
natural gas-tripping on roll out switch on burner box
condensate leaking around bottom of inducer assembly area inside furnace
gas pressure is normal-flames look ok no rolling or anything
    mattmia2 Posts: 18,231
    bad heat exchanger?
    pecmsg Posts: 7,612
    gas pressure
    Combustion analysis numbers
    EdTheHeaterMan Posts: 12,857
    edited February 2025
    When a rollout switch trips it is an indication that you have a blockage somewhere between the burner flame and the end of the exhaust pipe. That could be the combustion fan is not turning as fast as it should, or there could be a bird's nest in the vent pipe (intake or exhaust) the secondary heat exchanger may be blocked with carbon or calcium carbonate buildup. There may also be a blockage in one of the main burner heat exchanger primary pipes. Look for the blockage and clear it, to get the rollout switches to stop doing their job.
    The condensate leak may mean that there is water in the secondary heat exchanger that is not draining. Check the condensate trap for a blockage.
  • delcrossv
    delcrossv Posts: 2,204
    Bryant had a class action suit where their HX's would rust closed. Tripping rollout is indicative.
    You may get a HX for free.
    https://forum.heatinghelp.com/discussion/127381/bryant-90-lawsuit
    More on google